AC input
AC input | |||
AC input | Nom. | AC 100-120V / 220-240V | Auto select, |
AC input range | Min. | 90-132Vac / 180-264Vac | Continuous operation |
Min. | 264-300Vac | For up to 500 ms max. | |
Permissible voltage L or N to earth | Max. | 300Vac | Continuous, IEC 62103 |
Input frequency | Nom. | 50-60Hz | ±6% |
External input protection | See recommendations in chapter External input protection |
AC input |
| AC 100V | AC120V | AC230V |
Input current | Typ. | 2.0A | 1.72A | 1.05A | At 24V, 5A, see Fig. Input current over output current |
Power factor*)
| Typ. | 0.66 | 0.64 | 0.54 | At 24V, 5A, see Fig. Input current over output current; |
Peak factor**) | Typ. | 2.7 | 2.8 | 3.4 | At 24 V, 5 A |
Turn-on voltage | Typ. | 78Vac | 78Vac | 157Vac | Static, at 24V, 0A, see Fig. Input voltage range |
Shut-down voltage | Typ. | 68Vac | 68Vac | 68Vac | Static, at 24V, 5A, see Fig. Input voltage range |
Start-up delay | Typ. | 400ms | 400ms | 100ms | See Fig. Switch-on behavior definitions |
Rise time | Typ. | 30ms | 30ms | 30ms | At 24V, 5A constant current load, 0mF load capacitance, see Fig. Switch-on behavior definitions |
Typ. | 90ms | 90ms | 90ms | At 24V, 5A constant current load, 5mF load capacitance, see Fig. Switch-on behavior definitions | |
Turn-on overshoot | Max. | 200mV | 200mV | 200mV | See Fig. Switch-on behavior definitions |
*) The power factor is the ratio of real (or active) power to apparent power in an AC circuit.
**) The peak factor is the mathematical ratio of the peak value to the RMS value of the input current waveform.