AC input
AC input | |||
AC input | Nom. | AC 100-240V | Suitable for TN, TT and IT networks with alternating voltage |
AC input range | Min. | 90-264Vac | Continuous operation |
Min. | 264-300Vac | For up to 500 ms max. | |
Permissible voltage L or N to earth | Max. | 300Vac | Continuous according to IEC 60664-1 |
Input frequency | Nom. | 50-60Hz | ±6% |
Turn-on voltage | typ. | 81Vac | Static, see Fig. Input voltage range, |
Shut-down voltage | typ. | 63Vac/71Vac | At zero load / nominal load, static value, see Fig. Input voltage range, |
External input protection | See recommendations in chapter Safety instructions and installation requirements |
AC input |
| AC100V | AC120V | AC230V |
Input current | typ. | 5.2A | 4.3A | 2.3A | At 24V, 20A, see Fig. Input current over output current |
Power factor 1) | typ. | 0.99 | 0.99 | 0.97 | At 24V, 20A, see Fig. Power factor over output current |
Crest factor 2) | typ. | 1.6 | 1.7 | 2.0 | At 24V, 20A |
Start-up delay | typ. | 420ms | 300ms | 230ms | See Fig. Switch-on behavior definitions |
Rise time | typ. | 100ms | 100ms | 100ms | At 24V, 20A constant current load, 0mF load capacity, see Fig. Switch-on behavior definitions |
typ. | 140ms | 140ms | 140ms | At 24V, 20A constant current load, 20mF load capacity, see Fig. Switch-on behavior definitions | |
Turn-on overshoot | Max. | 200 mV | 200 mV | 200 mV | See Fig. Switch-on behavior definitions |
1) The power factor is the ratio of real (or active) power to apparent power in an AC circuit. |
