Output
Output voltage
Nom.
DC 24V
Adjustment range
Min.
24-28V
Guaranteed value
Max.
30V 2)
In end position of the potentiometer, clockwise.
Factory settings
typ.
24.1V
±0.2%, at full load (cold device)
Line regulation
Max.
5 mV
Between 90 and 264Vac
Load regulation
Max.
100 mV
Between 0 and 10A, static value, see Fig. Output voltage over output current, typ.
Residual ripple and ripple voltage
Max.
100mVpp
Bandwidth 20 Hz to 20 MHz, 50 Ohm
Output current
Nom.
10A
At 24V and an ambient temperature below 55°C, see Fig. Output current over ambient temperature
Nom.
6.25A
At 24V and an ambient temperature below 70°C, see Fig. Output voltage over output current, typ.
Nom.
8.6A
At 28V and an ambient temperature below 55°C, see Fig. Output current over ambient temperature
Nom.
5.4A
At 28V and an ambient temperature below 70°C, see Fig. Output voltage over output current, typ.
Output power
Nom.
240W
Ambient temperature below 55°C
Nom.
150W
Ambient temperature below 70°C
Overload characteristics
Continuous current
Output voltage > 13Vdc, see Fig. Output voltage over output current, typ.
Hiccup mode1)
Output voltage < 13Vdc, see Fig. Output voltage over output current, typ.
Short circuit current
Min.
11A
Load impedance 50mOhm, see Fig. Output voltage over output current, typ.
The discharge current of the output capacitors is not included.
Max.
15A
typ.
4.8A
Average current (rms), load impedance 50mOhm, see Fig. Output voltage over output current, typ.
Output capacity
typ.
2,850µF
Included in the power supply
1) Hiccup mode
In case of severe overload (when the output voltage drops below 13V) the power supply delivers a continuous output current for 2-5 seconds. The output is then switched off for approx. 1 second before a new start attempt is automatically made for 1 second. This cycle is repeated as long as the overload exists. The device starts operating normally again once the overload has been rectified.
2) This is the maximum output voltage that can occur in the end position of the potentiometer in clockwise direction due to tolerances. It is not a guaranteed value that can be achieved. A typical value is 28.5V.
Output 1:
Output voltage over output current, typ.; short circuit at output, hiccup mode