Cyclic diagnostics
The variables PnIoBoxState and PnIoBoxDiag are available for cyclic diagnostics.
Cyclic diagnostics 1:
Diagnostic variables PnIoBoxState and PnIoBoxDiag in the TwinCAT tree view.
These variables are cyclically exchanged with the process image between the PROFINET driver and the System Manager.
PnIoBoxState
PnIoBoxState variable, description of the states.
Number
Text
Remedial action / reason
0
No error
No error
No error
1
PROFINET Device state machine is in boot mode
PROFINET Device State Machine is still in the start-up phase
Not an error, wait
2
Device not found
Device does not reply to the Identify Request
Check connection, device connected, was the device called by its correct name?
3
The stationname is not unique
The station name is not unique
There are two or more devices in the network with the same PROFINET name. A correct identification cannot take place.
4
IP could not set
IP address could not be set.
The PROFINET device has rejected the IP settings for some reason. Check whether the IP settings are correct.
5
IP conflict
An IP conflict has occurred in the network.
A possible cause is that several devices have the same IP address.
6
DCP set was not successful
There was no reply or an erroneous reply to a DCP Set.
7
Watchdog error
The connection was broken off with a Watchdog error.
Check the cycle time, check the connection, if necessary increase the Watchdog factor.
8
Datahold error
The connection was broken off with a Datahold error.
Frame Data status was invalid for the length of the DataHoldTimer. Restart the device if necessary.
9
RTC3: Sync signal could not be started
For IRT only: the Sync signal could not be started.
Is EtherCAT Sync signal correct or has Sync0 started?
10
PROFINET Controller has a link error
The PROFINET controller has no link.
Check cable and connection.
11
The aliasname is not unique
The alias name is not unique
There are two or more devices in the network with the same alias name. This is made up of the neighborhood information (PortId.ChassisId). A correct identification cannot take place.
12
The automatic name assignement isn't possible - wrong device type
The automatic name assignment is not possible.
The expected PROFINET device is not in the projected position (VendorId or DeviceId does not correspond). Hence, no automatic naming and thus no device start is possible.
31
only for EtherCAT gateways: WC-State of cyclic EtherCAT frame is 1
For EL6631 only: EtherCAT WC State is 1
Check the mode on the EtherCAT master & slave (OP?).
PnIoBoxDiag
In contrast to the State variable, the variable PnIoBoxDiag can be used to display more than one state at the same time, i.e. the information is bit-coded and up to 16 parameters can be displayed. The following statuses are currently displayed.
PnIoBoxDiag variable, description of the states.
Number
0x0000
No diagnosis
0xXXX1
IOC-AR is not established
0xXXX2
IOC-AR is established
0xXXX4
IOC-AR is established but no ApplReady
0xXXX8
IOC-AR is established but module difference
0xXX1X
At least one AlarmCR get diagnosis alarm
0xX1XX
At least one InputCR is invalid
0xX2XX
At least one InputCR provider is in stop
0xX4XX
At least one InputCR problem indicator is set
0x1XXX
At least one OutputCR is invalid
0x2XXX
At least one OutputCR provider is in stop
0x4XXX
At least one OutputCR problem indicator is set
On the one hand information about the status of the IO Controller Single AR is displayed here. In addition, collective statuses are formed from the Frame Data statuses of the individual CRs. The whole thing happens for the input and the output CRs (currently only one is possible; in future the controller will support several CRs). In addition a PROFINET alarm is also displayed in the “PnIoBoxDiag”