Slave
Diagnostic variables
The slave features various diagnostic variables, which describe the state of the slave and the Profibus and can be linked in the PLC:
Slave 1:
DpState:
Value
No Error:
Station is in data exchange.
1
Station deactivated:
The slave was deactivated.
2
Station not exists:
Slave does not respond. Check whether the slave is switched on, the cabling is OK and the station address is correct.
3
Master lock:
The slave is in data exchange with another master.
4
Invalid slave response:
Incorrect response from the slave. Occurs temporarily if the slave has terminated the data exchange due to a local event.
5
Parameter fault:
Indicates a paramétrisation error.
6
Not supported:
A DP function is not supported. Check whether the GSD file and the station address is correct.
7
Config fault:
Indicates a configuration error. Check whether the added terminals or modules are OK.
8
Station not ready:
The device is starting up. This is displayed temporarily during startup.
9
Static diagnosis:
The slave indicates a static diagnosis and is currently unable to provide valid data. Check the operating state at the slave.
10
Diagnosis overflow:
The slave indicates a diagnostics overflow. Read the diagnostic data with ADS Read and check the operating state of the slave.
11
Physical fault:
Indicates a physical error in the response from a slave. Check the cabling.
12
Data-Exchange left:
The data transfer was not completed.
13
Severe bus fault:
Indicates a serious bus error. Please check the cabling.
14
Telegram fault:
The slave responds with an invalid telegram.
15
Station has no resources:
The slave has insufficient resources for the telegram. Check whether the GSD file is correct.
16
Service not activated:
Occurs if the slave terminates the data exchange due to a local event. Check whether DP functionality is disabled for the slave.
17
Unexpected telegram:
Unexpected telegram; can occur temporarily, if two PROFIBUS networks are linked, or check whether bus times in the second master are set the identically
18
Station ready:
Occurs temporarily during startup, as long as the task has not yet started.
31
only for EtherCAT gateways:
WC state of the cyclic EtherCAT frame is 1.
128
Slave waiting for data transfer:
The slave was parameterized and configured, but has not yet received a data exchange telegram.
129
Slave waiting for configuration:
The slave was parameterized, but has not yet received a Chk_Cfg telegram.
130
Slave waiting for parameter:
The slave was not yet parameterized and is waiting for a Set_Prm (Lock) telegram.
131
Slave waiting for baud rate:
The baud rate was not set.
132
Slave waiting for station no. from PLC:
The Profibus address was not set.
ExtDiagFlag:
Value
Diagnostic data have not changed.
1
Diagnostic data have changed. Use ADS Read to read the data.