Energy scan
Application
The energy scan enables the 16 IEEE 802.15.4 channels to be monitored in order to detect other radio systems. The energy in a frequency band is determined and displayed. Each channel is measured for approx. 5 seconds before moving to the next channel. Care must be taken that a channel does not communicate during these 5 seconds. It therefore makes sense to repeat the scanning of the channels a couple of times in order to obtain a more accurate statement as to whether or not a channel is occupied. The energy level is displayed through 0...0xF; "0" means no energy, "0xF" or 16dec stands for high energy level.
Set bit 1 in CB1 to TRUE. The KM6551-0000 confirms this in the status with bit 1, which is then also set to TRUE. The scan is finished when bit 1 of SB1 goes to FALSE. The result is then available in the input data byte 0 to 7. Each channel then corresponds to a nibble, i.e. half of a byte.
Example
Byte number
Value (hex)
Meaning
1
SB1
Status byte 1
2
SB2
Status byte 2
3
Data IN[0]
0x3F
3 - channel 1 low energy, F - channel 2 very high energy
4
Data IN[1]
0x01
0 - channel 3 no energy, 1 - channel 4 very low energy
5
Data IN[2]
0x7F
7 - channel 5 moderate energy, F - channel 5 very high energy
6...9
... (not considered in this example for reasons of simplicity)
10
Data IN[8]
0x10
1 - channel 15 low energy, 0 - channel 16 no energy
11...12
Data IN[8...9]
not required
The result is to be interpreted as follows. Channels 2 and 5 are to be avoided at all costs, but channels 3 and 16 look very good. No energy was measured here. Please note that these are instantaneous values. You can exclude channels with a high energy from further searches for free channels, but channels with no or only moderate energy may lead under certain circumstances to entirely different results.
Example: activation of the energy scan
Set bit 1 to TRUE in order to start data exchange.
CB1
Bit
CB1.7
CB1.6
CB1.5
CB1.4
CB1.3
CB1.2
CB1.1
CB1.0
RegAccess
reserve
Add3
Add2
Add1
Scan
EnergyScan
Start
Value
0
0
0
0
0
0
1
0
The terminal sets bit 1 of the status byte SB1 to TRUE as long as the scan is active.
SB1
Bit
SB1.7
SB1.6
SB1.5
SB1.4
SB1.3
SB1.2
SB1.1
SB1.0
RegAccess
Error
Add3
Add2
Add1
Scan
EnergyScan
Start
Value
0
0
0
0
0
0
1
0
The terminal resets bit 1 of the status byte SB1 to FALSE once the scan is finished. You can now evaluate the input data bytes 0...7 (bytes 8-9 have no meaning and should not be evaluated).
The scan takes approx. 80 seconds.
SB1
Bit
SB1.7
SB1.6
SB1.5
SB1.4
SB1.3
SB1.2
SB1.1
SB1.0
RegAccess
Error
Add3
Add2
Add1
Scan
EnergyScan
Start
Value
0
0
0
0
0
0
0
0