Mapping
The Bus Terminals occupy addresses within the process image of the controller. The assignment of process data (input and output data) and parameterization data (control and status bytes) to the control addresses is called mapping. The type of mapping depends on:
The Bus Couplers (BKxxxx, LCxxxx) and Bus Terminal Controllers (BCxxxx, BXxxxx) are supplied with certain default settings. The default setting can be changed with the KS2000 configuration software or with a master configuration software (e.g. TwinCAT System Manager or ComProfibus).
The following tables show the mapping depending on different conditions. For information about the contents of the individual bytes please refer to the pages Process image and Control and status byte.
Compact evaluation
For operation with compact process image, you must configure your Bus Coupler to compact mapping and bit R32.6 of the feature register of the KL5152-0000 (KL5151-0050) must be 1bin.
In this configuration the control bytes are suitable only for process data operation. Register communication is not possible!
Compact evaluation in Intel format
Default mapping for CANopen, CANCAL, DeviceNet, ControlNet, Modbus, RS232 and RS485 coupler
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Complete evaluation: no
Motorola format: no
Word alignment: n/a
0
DataIN1 D1
DataIN1 D0
reserved
CB1PD
1
DataIN1 D3
DataIN1 D2
reserved
CB2PD
2
DataIN2 D1
DataIN2 D0
DataOUT D1
DataOUT D0
3
DataIN2 D3
DataIN2 D2
DataOUT D3
DataOUT D2
Compact evaluation in Motorola format
Default mapping for PROFIBUS and Interbus coupler
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Motorola format: yes
Word alignment: n/a
0
DataIN1 D2
DataIN1 D3
CB2PD
reserved
1
DataIN1 D0
DataIN1 D1
CB1PD
reserved
2
DataIN2 D2
DataIN2 D3
DataOUT D2
DataOUT D3
3
DataIN2 D0
DataIN2 D1
DataOUT D0
DataOUT D1
Complete evaluation
For operation with complete process image, you must configure your Bus Coupler to complete mapping and bit R32.6 of the feature register of the KL5151-0050 must be 0bin.
In this configuration you can use the control and status bytes alternatively for register communication or process data operation.
Complete evaluation in Intel format
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Complete evaluation: yes
Motorola format: no
Word alignment: no
0
DataIN1 D0
SB1
DataOUT1 D0
CB1
1
DataIN1 D2
DataIN1 D1
DataOUT1 D2
DataOUT1 D1
2
SB2
DataIN1 D3
CB2
DataOUT1 D3
3
DataIN2 D1
DataIN2 D0
DataOUT2 D1
DataOUT2 D0
4
DataIN2 D3
DataIN2 D2
DataOUT2 D3
DataOUT2 D2
Complete evaluation in Motorola format
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Word alignment: no
0
DataIN1 D3
SB1
DataOUT1 D3
CB1
1
DataIN1 D1
DataIN1 D2
DataOUT1 D1
DataOUT1 D2
2
SB2
DataIN1 D0
CB2
DataOUT1 D0
3
DataIN2 D2
DataIN2 D3
DataOUT2 D2
DataOUT2 D3
4
DataIN2 D0
DataIN2 D1
DataOUT2 D0
DataOUT2 D1
Complete evaluation in Intel format with word alignment
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Motorola format: no
Word alignment: yes
0
reserved
SB1
reserved
CB1
1
DataIN1 D1
DataIN1 D0
DataOUT1 D1
DataOUT1 D0
2
DataIN1 D3
DataIN1 D2
DataOUT1 D3
DataOUT1 D2
3
reserved
SB2
reserved
CB2
4
DataIN2 D1
DataIN2 D0
DataOUT2 D1
DataOUT2 D0
5
DataIN2 D3
DataIN2 D2
DataOUT2 D3
DataOUT2 D2
Complete evaluation in Motorola format with word alignment
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Word alignment: yes
0
reserved
SB1
reserved
CB1
1
DataIN1 D2
DataIN1 D3
DataOUT1 D2
DataOUT1 D3
2
DataIN1 D0
DataIN1 D1
DataOUT1 D0
DataOUT1 D1
3
reserved
SB2
reserved
CB2
4
DataIN2 D2
DataIN2 D3
DataOUT2 D2
DataOUT2 D3
5
DataIN2 D0
DataIN2 D1
DataOUT2 D0
DataOUT2 D1
Compact process image on Bus Coupler that is set to complete process image
If the KL5152-0000 (KL5151-0050) is operated on a Bus Coupler that is set by default to complete process image (e.g. Lightbus), but bit R32.6 of the feature register is 1bin (default setting), the following process image results:
In this configuration you have different control and status bytes for register communication and process data operation. These are only suitable for the respectively specified purpose!
Intel format
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Motorola format: no
Word alignment: no
0
DataIN1 D0
SB1RC
CB1PD
CB1RC
1
DataIN1 D2
DataIN1 D1
CB2PD
reserved
2
SB2RC
DataIN1 D3
CB2RC
reserved
3
DataIN2 D1
DataIN2 D0
DataOUT D1
DataOUT D0
4
DataIN2 D3
DataIN2 D2
DataOUT D3
DataOUT D2
Motorola format
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Word alignment: no
0
DataIN1 D3
SB1RC
reserved
CB1RC
1
DataIN1 D1
DataIN1 D2
reserved
CB2PD
2
SB2RC
DataIN1 D0
CB2RC
CB1PD
3
DataIN2 D2
DataIN2 D3
DataOUT D2
DataOUT D3
4
DataIN2 D0
DataIN2 D1
DataOUT D0
DataOUT D1
Default mapping for Lightbus, EtherCAT and Ethernet coupler as well as Bus Terminal Controllers (BCxxxx, BXxxxx)
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Motorola format: no
Word alignment: yes
0
reserved
SB1RC
reserved
CB1RC
1
DataIN1 D1
DataIN1 D0
reserved
CB1PD
2
DataIN1 D3
DataIN1 D2
reserved
CB2PD
3
reserved
SB2RC
reserved
CB2RC
4
DataIN2 D1
DataIN2 D0
DataOUT D1
DataOUT D0
5
DataIN2 D3
DataIN2 D2
DataOUT D3
DataOUT D2
Parameterization
of the Bus Coupler
Address
Input data
Output data
Word offset
High byte
Low byte
High byte
Low byte
Word alignment: yes
0
reserved
SB1RC
reserved
CB1RC
1
DataIN1 D2
DataIN1 D3
CB2PD
reserved
2
DataIN1 D0
DataIN1 D1
CB1PD
reserved
3
reserved
SB2RC
reserved
CB2RC
4
DataIN2 D2
DataIN2 D3
DataOUT D2
DataOUT D3
5
DataIN2 D0
DataIN2 D1
DataOUT D0
DataOUT D1
Key
Complete evaluation: In addition to the process data, the control and status bytes are also mapped into the address space.
Motorola format: Motorola or Intel format can be set.
Word alignment: In order for the channel address range to commence at a word boundary, empty bytes are inserted into the process image as appropriate.
SB n: Status byte for channel n (appears in the input process image).
CB n: Control byte for channel n (appears in the output process image).
SB n PD: Status byte for channel n, to be used only for process data operation (appears in the input process image)
CB n PD: Control byte for channel n, to be used only for process data operation (appears in the output process image)
SB n RC: Status byte for channel n, to be used only for register communication (appears in the input process image)
CB n RC: Control byte for channel n, to be used only for register communication (appears in the output process image)
DataIN n D0: Channel n, input double word, lowest significant data byte
DataIN n D1: Channel n, input double word, ...
DataIN n D2: Channel n, input double word, ...
DataIN n D3: Channel n, input double word, highest significant data byte
DataOUT n D0: Channel n, output double word, lowest significant data byte
DataOUT n D1: Channel n, output double word, ...
DataOUT n D2: Channel n, output double word, ...
DataOUT n D3: Channel n, output double word, highest significant data byte
reserved: This byte occupies process data memory, although it has no function.