KL5051 - Bidirectional SSI encoder interface
Data exchange, function
Communication with the servo drive takes place via the process data (A0-A5, E0-E5). With
A0/E0 is the control/status byte for the operating data communication and
A3/E3 is the control/status byte for the parameter and server status communication with the device.
Operating data status byte E0
The operating data status byte issues potential servo drive error messages in process data exchange.
MSB
REG=0
ERROR
ALARM
KOM_ERR
CRC_ERR
Bit
ERROR
This is set when ALARM or KOM_ERR is set.
ALARM
The alarm bit of the servo drive is displayed here.
KOM_ERR
There has been a communication problem. No valid data is exchanged.
Possible causes:
The servo interface is de-energized or not ready for operation.
An open circuit is present, or the connection lines of the terminal are reversed.
CRC_ERR
Faulty telegrams occur during data transmission (possibly EMC issue).
Parameter control byte A3 when the servo control is set (bit 7 = 0)
Various actions are performed in the servo drive with this control byte.
MSB
REG=0
RD_PARH
RD_PARL
RS_ANS
RF
/NSTOP
/PSTOP
Bit
REG
This bit switches between servo parameter and servo control/status communication.
RD_PARH
Read parameter High Word (parameter address in A4)
RD_PARL
Read parameter Low Word (parameter address in A4)
RS_ANS
Reset of communication monitoring or lag error.
If the servo reports a fault, e.g. communication monitoring has been triggered, the fault can be reset by setting this bit.
If the error message in status byte E3 (SERV_ERR) is not reset (e.g. internal temperature too high), the servo drive must be de-energized (this is the only way to reset the other error messages).
RF
Controller enable. The output stage is enabled and the brake (if available) is enabled at the same time.
/NSTOP (active low)
Negative set values are set to zero.
/PSTOP (active low)
Positive set values are set to zero.
Parameter status byte E3 during acquisition of the servo status
Once enabled, the servo status word is continuously read and updated by the servo.
MSB
REG=0
KOM_ERR
RD_PARH_Q
RD_PARL_Q
SERV_ERR
RF_Q
/NSTOP_Q
/PSTOP_Q
Bit
REG
0: The channel consisting of A3, A4, A5, E3, E4, E5 is in the operation mode with which the servo control/status is operated.
KOM_ERR
An error has occurred during data transfer.
RD_PARH_Q
E4, E5 contains the high word of the requested parameter value.
RD_PARL_Q
E4, E5 contains the low word of the requested parameter value.
SERV_ERR
The power section of the servo reports an error.
RF_Q
The output stage and any existing brake are enabled.
/NSTOP_Q (active low)
1: Negative set values are possible.
0: Negative set values are set to zero.
/PSTOP (active low)
1: Positive set values are possible.
0: Positive set values are set to zero.
Parameter control byte A3 in parameter operation mode (bit 7 = 1)
The parameter data is written to a buffer with the parameter address and transferred to the servo on request. This request can be made with the last buffer entry. The data frame is formed by the terminal, and the checksum is checked and evaluated. The parameter data form a maximum of one double word, but shorter parameter data can also be sent.
MSB
REG=1
RD_PARH
RD_PARL
PUT_HW
PUT_LW
TRS_BUF
Bit
REG
RD_PARH
RD_PARL
PUT_HW
Write high word of the parameter to the buffer (A4, A5 parameter High Word).
PUT_LW
Write low word of the parameter to the buffer (A4, A5 parameter Hight Word).
TRS_BUF
Write data from the buffer to the parameter address set by A4.
Parameter status byte E3 in Parameter operation mode
During parameter communication (REG = 1) with the servo, various acknowledgements are output in the status byte.
MSB
REG=1
KOM_ERR
RD_PARH_Q
RD_PARL_Q
SERV_ERR
PUT_HW_Q
PUT_LW_Q
TRS_BUF_Q
Bit
REG
1: The channel consisting of A3, A4, A5, E3, E4, E5 is in the operation mode with which the parameter communication takes place.
KOM_ERR
RD_PARH_Q
RD_PARL_Q
SERV_ERR
PUT_HW_Q
The High Word was written to the buffer.
PUT_LW_Q
The Low Word was written to the buffer.
TRS_BUF_Q
Data was successfully transferred.