Register communication
Register access via process data exchange
Control byte in register mode (REG=1)
MSB
REG=1
W/R
A5
A4
A3
A2
A1
A0
REG = 0bin: Process data exchange
REG = 1bin: Access to register structure
W/R = 0bin: Read register
W/R = 1bin: Write register
A5..A0 = register address
Addresses A5...A0 can be used to address a total of 64 registers.
Register communication 1:
Register mode control byte
The control or status byte occupies the lowest address of a logical channel. The corresponding register values are located in the following 2 data bytes. (The BK2000 is an exception: here, an unused data byte is inserted after the control or status byte, and the register value is therefore placed on a word boundary).
Sample 1:
Reading of register 8 in the BK2000 with a KL4002 and the end terminal:
If the following bytes are transferred from the controller to the terminal,
Byte
Byte 3
Byte 2
Byte 1
Byte 0
DataOUT 1
DataOUT 0
Not used
Control byte
Value
0xXX
0xXX
0xXX
0x88
The terminal returns the following type identifier (0x0FA2 corresponds to unsigned integer 4002).
Byte
Byte 3
Byte 2
Byte 1
Byte 0
DataIN 1
DataIN 0
Not used
Status byte
Value
0x0F
0xA2
0x00
0x88
Sample 2:
Writing of register 31 in the BK2000 with an intelligent terminal and the end terminal:
If the following bytes (code word) are transferred from the controller to the terminal,
Byte
Byte 3
Byte 2
Byte 1
Byte 0
DataOUT 1
DataOUT 0
Not used
Control byte
Value
0x12
0x35
0xXX
0xDF
The code word is set, and the terminal returns the register address with bit 7 for register access as acknowledgment.
Byte
Byte 3
Byte 2
Byte 1
Byte 0
DataIN 1
DataIN 0
Not used
Status byte
Value
0x00
0x00
0x00
0x9F