Control and status bytes
Register communication
Control byte 1 (for register communication)
Control byte 1 (CB1) is located in the output image, and is transmitted from the controller to the terminal.
Bit
CB1.7
CB1.6
CB1.5
CB1.4
CB1.3
CB1.2
CB1.1
CB1.0
RegAccess
R/W
Reg. no.
Key
Bit
CB1.7
RegAccess
1bin
Register communication switched on
CB1.6
R/W
0bin
Read access
1bin
Write access
CB1.5 to CB1.0
Reg. no.
Register number:
Enter the number of the register that you
- want to read with input data word DataIN1 or
- want to write with output data word DataOUT1.
Status byte 1 (for register communication)
The status byte 1 (SB1) is located in the input image and is transmitted from terminal to the controller.
Bit
SB1.7
SB1.6
SB1.5
SB1.4
SB1.3
SB1.2
SB1.1
SB1.0
RegAccess
R/W
Reg. no.
Using control and status bytes
In contrast to other types of terminal, the process data provided when using a KL3356 is valid even during register communication!
The KL3356 uses
  • control byte 0 and status byte 0 exclusively for register communication
  • control byte 1 and status byte 1 exclusively for process data mode
Key
Bit
SB1.7
RegAccess
1bin
Acknowledgment for register access
SB1.6
R
0bin
Read access
SB1.5 to SB1.0
Reg. no.
Number of the register that was read or written.
Process data mode
Control byte 2 (for process data mode)
Control byte 2 (CB2) is located in the output image, and is transmitted from the controller to the terminal.
Bit
CB2.7
CB2.6
CB2.5
CB2.4
CB2.3
CB2.2
CB2.1
CB2.0
Quit
Error
MapCaliCounter
RegLockReq
MapCaliData/
DisableSymm
CaliDisReq/
Channel
StartManCheck/
StartManCali
Key
Bit
CB2.7
0bin
reserved
CB2.6
QuitError
1bin
All errors are cleared
CB2.5
0bin
reserved
CB2.4
MapCaliCounter
0bin
The registers R2, R3 and R5 show the data selected with bit CB2.2.
1bin
Registers R2, R3 and R5 show the calibration counters (in addition, bit CB2.3 must be set to 0bin for this purpose). (see note below)
The calibration counters are evaluated by the KL3356
The calibration counters are a measure for the quality of the self-calibration. In standard applications, it is not necessary for the user to evaluate these counters, since the KL3356 evaluates the counters itself and uses bit 0.8 or bit 0.15 of the status word (R0) to report when permitted tolerances have been exceeded.
Bit
CB2.3
RegLockReq
0bin
Register lock not active:
  • The KL3356 can update the values in registers R1, R2, R3 and R5.
  • Registers R2, R3 and R5 can be shown by setting bit CB2.4 to 1bin.
1bin
Register lock active:
  • The KL3356 no longer updates the registers R1, R2, R3 and R5.
  • Bit CB2.4 is not evaluated!
normal operation
manual operation*
CB2.2
MapCaliData/
DisableSymm
0bin
The measured value registers contain the mapped raw data from the converters:
  • R1: the calculated weight
  • R2: the strain gauge measuring signal
  • R3: the strain gauge reference signal
  • R5: the last actual test value
Symmetrical measurement is switched on if it has been enabled by bit R32.7 of the feature register.
1bin
The measurement registers contain the mapped calibration data:
  • R1: reserved (register is empty)
  • R2: the offset error of the measuring signal
  • R3: the offset error of the reference signal
  • R5: the correction factor for the differential signal
Symmetrical measurement is switched off even if it has been enabled by bit R32.7 of the feature register.
CB2.1
CaliDisReq/
Channel
0bin
The ForcedCali status bit (SB2.4) is cleared
Selection of the measuring channel, UDiff
1bin
Blocking automatic calibration and cyclic reference measurement
Selection of the measuring channel, URef
CB2.0
StartManCheck/
StartManCali
1bin
Start test
Start calibration and test
*) Manual operation can be enabled via the command register (R7).
Status byte 2 (for process data mode)
The status byte 2 (SB2) is located in the input image and is transmitted from terminal to the controller.
Bit
SB2.7
SB2.6
SB2.5
SB2.4
SB2.3
SB2.2
SB2.1
SB2.0
Error
ForcedCali
RegLockAck
NoActualValue
CaliDisAck/Channel
NegWeight
Key
Bit
SB2.7
0bin
reserved
SB2.6
Error
1bin
internal error
SB2.5
0bin
reserved
SB2.4
ForcedCali
1bin
Forced calibration is being carried out.
SB2.3
RegLockAck
1bin
Acknowledgement for the write protection of all registers
SB2.2
NoActualValue
1bin
The process data indicated is not valid.
SB2.1
CaliDisAck/
Channel
normal operation
manual operation*
0bin
selected measuring channel: Udiff
1bin
Acknowledgement of calibration block
selected measuring channel: Uref
SB2.0
NegWeight
0bin
Process data is positive
1bin
Process data is negative