Basic function principles
The analog input terminals process signals in the range of:
KL3102: -10 V ... +10 V
KL3112: 0 mA ... 20 mA
KL3122: 4 mA ... 20 mA
with a resolution of up to 16 bits (65535 steps). The terminal inputs are differential inputs with common ground. Due to the differential inputs, the terminals are particularly suitable for floating measuring of voltage drops. In the standard version, a filter with a stop frequency (64.5 dB) of 50 Hz is active. The filter constant and the associated conversion time are configurable in a wide range.
The green Run LEDs indicate the operating state of the associated terminal channel.
- On: Normal operation
- Off: Watchdog-timer overflow has occurred. If no process data are transmitted by the Bus Coupler for 100 ms, the green LEDs go out.
The red ERROR LEDs indicate an overflow.
- On: Measured current outside the measuring range (> 20 mA)
- Off: Current in valid range
KL3102 - Output format of the process data
In the delivery state the process data are shown in two's complement form (integer -1 corresponds to 0xFFFF). Other presentation types can be selected via the feature register (R32) (e.g. signed amount representation, Siemens output format).
Measured value | Output | |
KL3102 | dec | hex |
-10 V | -32768 | 0x8000 |
-5 V | -16383 | 0xC001 |
0 V | 0 | 0x0000 |
5 V | 16383 | 0x3FFF |
10 V | 32767 | 0x7FFF |
KL3112, KL3122 - Output format of the process data
Measured value | Output | ||
KL3112 | KL3122 | dec | hex |
0 mA | 4 mA | 0 | 0x0000 |
10 mA | 12 mA | 16383 | 0x3FFF |
20 mA | 20 mA | 32767 | 0x7FFF |
Calculation of process data
The terminal continuously records measured values and stores the raw values of its A/D converter in register R0 (RAM ). The calculation of the correction with the calibration values takes place after each sampling of the analog signal. This is followed by manufacturer and user scaling:
The process data that are transferred to the Bus Coupler are calculated using the following equations:
Y_a = (B_a + X_adc) * A_a | (1.0) | Neither user nor manufacturer scaling is active. |
Y_1 = B_h + A_h * Y_a | (1.1) | Manufacturer scaling active: (Default setting) |
Y_2 = B_w + A_w * Y_a | (1.2) | User scaling active |
Y_1 = B_h + A_h * Y_a | (1.3) | Manufacturer and user scaling active |
Key
Name | Designation | Register |
X_adc | Output value of the A/D converter | - |
Y_aus | Process data for controller | - |
B_a | Vendor calibration: Offset | |
A_a | Vendor calibration: Gain | |
B_h | Manufacturer scaling: Offset | |
A_h | Manufacturer scaling: Gain | |
B_w | User scaling: Offset | |
A_w | User scaling: Gain |
The equations of the straight line are enabled via register R32