Register description
The registers can be read or written via the register communication. They are used for the parameterization of the terminal.
R0 to R7: Registers in the internal RAM of the terminal
The process variables can be used in addition to the actual process image. Their function is specific to the terminal.
- R0 ADC raw value (X_R)
This register contains the raw ADC value with gain and offset error
- R1 to R5: Reserved
- R6: Diagnostic register
- High byte: reserved
- Low byte: Status byte
- R7: Command register
High-Byte_Write = function parameter
Low-Byte_Write = function number
High-Byte_Read = function result
Low-Byte_Read = function number
R8 to R15: Registers in the internal ROM of the terminal
The type and system parameters are hard programmed by the manufacturer, and the user can read them but cannot change them.
- R8: Terminal type
The terminal type in register R8 is needed to identify the terminal.
- R9: Software version (X.y)
The software version can be read as a string of ASCII characters.
- R10: Data length
R10 contains the number of multiplexed shift registers and their length in bits.
The Bus Coupler sees this structure.
- R11: Signal channels
Related to R10, this contains the number of channels that are logically present. Thus for example a shift register that is physically present can perfectly well consist of several signal channels.
- R12: Minimum data length
The particular byte contains the minimum data length for a channel that is to be transferred. If the MSB is set, the control and status byte is not necessarily required for the terminal function and is not transferred to the control, if the Bus Coupler is configured accordingly.
- R13: Data type register
Data type register | Meaning |
0x00 | Terminal with no valid data type |
0x01 | Byte array |
0x02 | Structure 1 byte n bytes |
0x03 | Word array |
0x04 | Structure 1 byte n words |
0x05 | Double word array |
0x06 | Structure 1 byte n double words |
0x07 | Structure 1 byte 1 double word |
0x08 | Structure 1 byte 1 double word |
0x11 | Byte array with variable logical channel length |
0x12 | Structure 1 byte n bytes with variable logical channel length (e.g. 60xx) |
0x13 | Word array with variable logical channel length |
0x14 | Structure 1 byte n words with variable logical channel length |
0x15 | Double word array with variable logical channel length |
0x16 | Structure 1 byte n double words with variable logical channel length |
- R14: reserved
- R15: Alignment bits (RAM)
The alignment bits are used to place the analog terminal in the Bus Coupler on a byte boundary.
R16 to R30: Manufacturer parameter area (SEEROM)
The manufacturer parameters are specific for each type of terminal. They are programmed by the manufacturer, but can also be modified by the controller. The manufacturer parameters are stored in a serial EEPROM in the terminal, and are retained in the event of voltage drop-out.
These registers can only be altered after a code word has been set in R31.
- R17: Hardware compensation - offset (B_a)
16 bit signed integer
This register is used for offset compensation of the terminal (Eq. 1.1).
Register value approx. 0xFFXX
- R18: Hardware compensation - gain (A_a)
16 bit signed integer*2-12
This register is used for gain compensation of the terminal (Eq. 1.1).
Register value approx. 0x11XX
- R19: Manufacturer scaling - offset (B_h)
16 bit signed integer [0x0000]
This register contains the offset of the manufacturer straight-line equation (equation 1.3). The straight-line equation is activated via register R32.
- R20: Manufacturer scaling - gain (A_h)
16 bit signed integer*2-10 [0x2002]
This register contains the scale factor of the manufacturer's equation of the straight line (Eq. 1.3). The straight-line equation is activated via register R32.
1 corresponds to register value 0x0400.
- R21: Over range limit (OVRL)
16 bits signed integer in Y_a (Eq. 1.0) [0x0FFF]
This limit value limits the maximum measuring range of the input terminal. If it is exceeded, the associated status bit is set, and the maximum value is displayed.
- R22: Under range limit (UNRL)
16 bit signed integer in Y_a (equation 1.0) [0x0000]
If the actual value falls below this limit, the associated status bit is set, and the minimum value is displayed.
- R23: ADC hardware preset
[0x1000]
Initialization of the ADC offset register.
R31 to R47: User parameter area (SEEROM)
The user parameters are specific for each type of terminal. They can be modified by the programmer. The user parameters are stored in a serial EEPROM in the terminal, and are retained in the event of voltage drop-out. The user area is write-protected by a code word.
• R31: Code word register in RAM The code word 0x1235 must be entered here so that parameters in the user area can be modified. If any other value is entered into this register, the write-protection is active. When write protection is not active, the code word is returned when the register is read. If the write protection is active, the register contains a zero value. |
- R32: Feature register
[0x1106]
This register specifies the operation modes of the terminal. Thus, for instance, a user-specific scaling can be activated for the analog I/Os.
Feature bit no. |
| Description of the operation mode |
Bit 0 | 1 | User scaling (R33, R34) active [0] |
Bit 1 | 1 | Manufacturer scaling (R19, R20) active [1] |
Bit 2 | 1 | Watchdog timer active [1] |
Bit 3 | 1 | Sign / amount representation [0] |
Bit 4 | 1 | Siemens output format [0] |
Bits 5 to 7 | - | Reserved, don't change |
Bit 8 | 1 | Over range Protection [1] |
Bit 9 | 1 | Limit value 1 active [0] |
Bit 10 | 1 | Limit value 2 active [0] |
Bit 11 | 1 | Filter1 active [0] |
Bits 12 to 15 | - | Reserved, don't change |
If the Siemens output format is selected, the lowest three bits are used for status evaluation. The process data is represented in bits 15 to 3, with bit 15 representing the sign bit. Scaling of the measured value according to the Siemens standard has to be done via user scaling (R33, R34).
KL3061, KL3062 | ||||
Measured value | Bits 15 to 3 | Bit 2 | Bit1 | Bit 0 |
Measured value > 10 V |
| 0 | 0 | 1 |
Measured value <10 V | Process data | 0 | 0 | 0 |
KL3064 | ||||
| X | ERROR | Overflow |
| 0 | 0 | 1 |
- R35: Limit value 1 (Y_2)
If the process data are outside this threshold, the appropriate bits are set in the status byte.
- R36: Limit value 2 (Y_2)
- R37: Filter constant
[0x0000]
If the internal filter is activated via R32.11, you can choose between the following filter constants in R37 (not possible with KL3064). In the standard setting, the corresponding conversion time is 2.5 ms:
Applies to all terminals from firmware version 3x. This documentation applies to all terminals from firmware version 3x. The version information can be found on the right-hand side of the terminal in the serial number: xxxx3xxx. Example: 52983A2A => the firmware version is 3A. |
R37 | Explanation | |
0x0000 | 2nd order FIR filter | default value |
0x0100 | 1st order IIR filter, cut-off frequency Fg approx.1 kHz | The implemented IIR filters do not have any notch behavior, i.e., they do not explicitly suppress any frequency. |
0x0200 | 1st order IIR filter, cut-off frequency Fg approx. 100 Hz | |
0x0300 | 1st order IIR filter, cut-off frequency Fg approx. 50 Hz | |
0x0400 | 1st order IIR filter, cut-off frequency Fg approx. 20 Hz | |
0x0500 | 1st order IIR filter, cut-off frequency Fg approx. 10 Hz | |
0x0600 | 1st order IIR filter, cut-off frequency Fg approx. 5 Hz | |
0x0700 | 1st order IIR filter, cut-off frequency Fg approx. 1 Hz | |
0x1000 | 50 Hz FIR filter | In contrast to the IIR filters, FIR filter have notch behavior. The timer settings of the notch filter are made via channel 0 of the terminal. This means that the 50 Hz filter on channel 0 and the 60 Hz filter on channel 1 cannot be active simultaneously. |
0x2000 | 60 Hz FIR filter | |
Other values | No filter active |
