KL3064
The KL3064 is mapped in the Bus Coupler according to the set parameters. If the terminal is completely evaluated, it occupies memory space in the process image of the inputs and outputs.
Default mapping for CANopen, CANCAL, DeviceNet, ControlNet, Modbus, RS232 and RS485 coupler
Conditions | Word offset | High byte | Low byte |
Complete evaluation: no | 0 | Ch1 D1 | Ch1 D0 |
1 | Ch2 D1 | Ch2 D0 | |
2 | Ch3 D1 | Ch3 D0 | |
3 | Ch4 D1 | Ch4 D0 |
Default mapping for: Profibus and Interbus Coupler
Complete evaluation: no | 0 | Ch1 D0 | Ch1 D1 |
1 | Ch2 D0 | Ch2 D1 | |
2 | Ch3 D0 | Ch3 D1 | |
3 | Ch4 D0 | Ch4 D1 |
Complete evaluation: yes | 0 | Ch1 D0 | Ch1 CB/SB |
1 | Ch2 CB/SB | Ch1 D1 | |
2 | Ch2 D1 | Ch2 D0 | |
3 | Ch3 D0 | Ch3 CB/SB | |
4 | Ch4 CB/SB | Ch3 D1 | |
5 | Ch4 D1 | Ch4 D0 |
Complete evaluation: yes | 0 | Ch1 D1 | Ch1 CB/SB |
1 | Ch2 CB/SB | Ch1 D0 | |
2 | Ch2 D0 | Ch2 D1 | |
3 | Ch3 D1 | Ch3 CB/SB | |
4 | Ch4 CB/SB | Ch3 D0 | |
5 | Ch4 D0 | Ch4 D1 |
Default mapping for: Lightbus, EtherCAT and Ethernet coupler and Bus Terminal Controller (BCxxxx, BXxxxx)
Complete evaluation: yes | 0 | Res. | Ch1 CB/SB |
1 | Ch1 D1 | Ch1 D0 | |
2 | Res. | Ch2 CB/SB | |
3 | Ch2 D1 | Ch2 D0 | |
4 | Res. | Ch3 CB/SB | |
5 | Ch3 D1 | Ch3 D0 | |
6 | Res. | Ch4 CB/SB | |
7 | Ch4 D1 | Ch4 D0 |
1 | Ch1 D0 | Ch1 D1 | |
3 | Ch2 D0 | Ch2 D1 | |
5 | Ch3 D0 | Ch3 D1 | |
7 | Ch4 D0 | Ch4 D1 |
Key
Complete evaluation | The terminal is mapped with control and status byte. |
Motorola format | Motorola or Intel format can be set. |
Word alignment | The terminal is positioned on a word boundary in the Bus Coupler. |
Ch n CB | Control byte for channel n (appears in the process image of the outputs). |
Ch n SB | Status byte for channel n (appears in the process image of the inputs). |
Ch n D0 | Channel n, data byte 0 (byte with the lowest value) |
Ch n D1 | Channel n, data byte 1 (byte with the highest value) |
Res. | Reserved: This byte is assigned to the process data memory, although it has no function. |