Technical data
Technical data | KL2751-0000, KS2751-0000, | KL2761-0000, KS2761-0000, |
Mains voltage | 230 VAC | 230 VAC |
Power rating** | 300 VA (W), max. 1.35 A | 600 VA (W), max. 2.7 A |
Permissible load types | Inductive (transformers only, no ballasts for fluorescent tubes), | |
Cable length | max. 100 m between dimmer terminal and lamp | |
Types of control | Leading edge phase control, trailing edge phase control, rectifier mode (positive or negative half-wave in leading edge phase control) | |
Resolution | max. 7 bit | |
Leakage current (OFF state) | < 2 mA | |
Electrical isolation | 500 V (K-bus / field voltage), 3750 VAC (1 min.) | |
Power supply for the electronics | via the K-bus | |
Current consumption from K-bus | typically 95 mA | |
Bit width in the input process image | 1 x 16 bit data, 1 x 8 bit status | |
Bit width in the output process image | 1 x 16 bit data, 1 x 8 bit control | |
Configuration | via the Bus Coupler or the controller | |
Weight | approx. 60 g | |
Permissible ambient temperature range during operation | 0 °C to + 55 °C (refer to the chapter Installation positions!) | |
Permissible ambient temperature range during storage | -25 °C ... + 85 °C | |
Permissible relative air humidity | 95 %, no condensation | |
Dimensions (W x H x D) | approx. 15 mm x 100 mm x 70 mm (width aligned: 12 mm) | |
on 35 mm mounting rail conforming to EN 60715 | ||
Vibration / shock resistance | conforms to EN 60068-2-6 / EN 60068-2-27 | |
EMC immunity/emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |
Protection class | IP20 | |
Installation position | load-dependent (refer to the chapter Installation positions!) | |
Pluggable wiring | for all KSxxxx terminals | |
Approvals/markings | CE, UKCA, EAC |
**) Rated output = lamp power + ballast losses
The ballast losses are typically equivalent to:
- 5 % of the rated output of the ballast in the case of electronic ballasts
- 20 % of the rated output of the transformer in the case of inductive ballasts