KL2692 - cycle monitoring terminal
Technical data
Technical data
KL2692
Number of outputs
2 potential-free relay outputs (make contacts)
Rated load voltage of the outputs
230 VAC / 30 VDC
Ohmic switching current
5 AAC / 5 ADC
Inductive switching current
2 AAC / 2 ADC
Minimum permitted load
10 mA at 5 VDC
Number of inputs
2 digital inputs (24 V)
Rated voltage of the inputs
24 VDC (-15% / +20%)
Signal voltage "0"
-3 V ... 5 V (EN 61131-3, type 1)
Signal voltage "1"
15 V ... 30V (EN 61131-3, Type 1)
Input filter
3.0 ms
Input current
typically 5 mA
Electrical isolation
500 V (K-bus/field voltage)
Power supply for the electronics
via the K-bus
Current consumption from K-bus
typically 165 mA
Bit width in the input process image
2 x 8 bit data, 1 x 8 bit status
Bit width in the output process image
2 x 8 bit data, 1 x 8 bit control
Mechanical switching cycles
minimum 2 x 107
Electrical switching cycles
minimum 1 x 105 (5 A / 30 VDC)
Configuration
via the Bus Coupler or the controller
Weight
approx. 60 g
Permissible ambient temperature range during operation
0 °C ... + 55 °C
Permissible ambient temperature range during storage
-25°C ... + 85 °C
Permissible relative air humidity
95%, no condensation
Dimensions (W x H x D)
approx. 15 mm x 100 mm x 70 mm
Mounting
on 35 mm mounting rail conforms to EN 60715
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP20
Installation position
variable
Approval
CE