RTD/resistance measurement
Comparative overview of Beckhoff R/RTD measuring devices (terminals, boxes, modules)
The following table is intended to provide a quick overview of the available Beckhoff I/O devices for the direct connection of RTD sensors for temperature and resistance measurement.
Notice
Device documentation is solely authoritative
The values may be shortened extracts from the respective documentation, which is decisive and recommended for detailed analysis.
For a possibly more up-to-date overview, please consult www.beckhoff.com.
Design
Number of RTD
channels
Connection
technology
Resolution
Conversion time/sampling rate 1)
KL3201
K-bus terminal IP20
1
Cage Clamp
0.1 °C/0.5 °C
~200…250 ms
KL3202
K-bus terminal IP20
2
Cage Clamp
0.1 °C/0.5 °C
~200…250 ms
KL3204
K-bus terminal IP20
4
Cage Clamp
0.1 °C/0.5 °C
~200…250 ms
KL3204-0030
K-bus terminal IP20
4
Cage Clamp
0.1 °C
~250 ms
KL3208-0010
K-bus terminal IP20
8
Cage Clamp
0.01 °C/0.1 °C
~250 ms
KL3228
K-bus terminal IP20
8
Cage Clamp
0.01 °C/0.1 °C
~250 ms
KL3222
K-bus terminal IP20
2
Cage Clamp
0.01 °C/0.1 °C
~50 ms
KL3214
K-bus terminal IP20
4
Cage Clamp
0.01 °C/0.1 °C
~170 ms
EL3201
EtherCAT Terminal IP20
1
Cage Clamp
0.01 °C/0.1 °C
4…500 ms
EL3201-0010
1
Cage Clamp
0.01 °C/0.1 °C
4…500 ms
EL3202
2
Cage Clamp
0.01 °C/0.1 °C
2…800 ms
EL3202-0010
2
Cage Clamp
0.01 °C/0.1 °C
4…500 ms
EL3204
4
Cage Clamp
0.01 °C/0.1 °C
2…800 ms
EL3204-0162
4
Cage Clamp
0.01 °C/0.1 °C
33…833 ms
EL3204-0200
4
Cage Clamp
0.01 °C/0.1 °C
4…500 ms
EL3208
8
Cage Clamp
0.01 °C/0.1 °C
4.5…1600 ms
EL3208-0010
8
Cage Clamp
0.01 °C/0.1 °C
12.8…7800 ms
EL3214
4
Cage Clamp
0.01 °C/0.1 °C
5…1600 ms
EL3214-0090
4
Cage Clamp
0.01 °C/0.1 °C
5…1600 ms
EL3218
8
Cage Clamp
0.01 °C/0.1 °C
20…1600 ms
EL3692
2
Cage Clamp
>= 12 µΩ
10 … 400 ms
EL3751
1
Cage Clamp
0.01 °C
>= 100 µs (10 kSps)
EL3751-0004
1
Cage Clamp
0.01 °C
>= 100 µs (10 kSps)
ELM3244, ELM3246
4/6
Push-in
0.1/0.01/0.001 °C
> 1 ms (1 kSps) per channel
ELM3502
2
Push-in
0.1/0.01/0.001 °C
>= 50 µs (20 kSps) per channel
ELM3504
4
Push-in
0.1/0.01/0.001 °C
>= 100 µs (10 kSps) per channel
ELM3702, ELM3704
2/4
Push-in
0.1/0.01/0.001 °C
ELM3702-0101
2
LEMO
0.1/0.01/0.001 °C
EP3204-0002,
EPP3204-0002
EtherCAT Box IP67,
EtherCAT P Box IP67
4
M12
0,1 °C
2 … 800 ms
EJ3202
EtherCAT plug-in module
2
On application-specific signal distribution boards
0,01 °C/0,1 °C
2 … 800 ms
EJ3214
4
0,01 °C/0,1 °C
5 … 1600 ms
1) depending on settings, e.g. active input channels and filters, for complete and authoritative information see respective documentation
Continuation:
Measurement uncertainty 2)
Oversampling
Distributed Clocks for timestamp operation
Electrically isolated channels
TwinSAFE SC
KL3201
< ±1 °C
KL3202
< ±1 °C
KL3204
< ±1 °C
KL3204-0030
< ±1 °C
KL3208-0010
< ±1.5 °C
KL3228
< ±1 °C
KL3222
< ±0.1 °C
KL3214
< ±0.5 °C
EL3201
< ±0.5 °C
EL3201-0010
< ±0.1 °C
EL3202
< ±0.5 °C
EL3202-0010
< ±0.1 °C
EL3204
< ±0.5 °C
EL3204-0162
< ±0.5 °C
EL3204-0200
< ±0.3 % 3)
EL3208
< ±0.5 °C
EL3208-0010
-20…+60 °C: ±0.25 °C
-50…+150 °C: ±1.5 °C
EL3214
< ±0.5 °C
EL3214-0090
< ±0.5 °C
x
EL3218
< ±0.5 °C
EL3692
< ±0.5 % 3)
EL3751
< ±0.5 °C for Pt100
< ±0.13 °C for Pt1000
x
x
EL3751-0004
< ±0.5 °C for Pt100
x
x
ELM3244, ELM3246
< ±0.1 °C for Pt100
x
x
ELM3502
< ±0.07 °C for Pt100
x
x
ELM3504
x
x
ELM3702, ELM3704
< ±0.05 °C for Pt100
x
x
ELM3702-0101
< ±0.1 °C for Pt100
x
x
x
EP3204-0002,
EPP3204-0002
< ±0.5 °C (Pt sensors in 4-wire connection)
EJ3202
< ±0,5 °C
EJ3214
< ±0,5 °C
2) If several specifications are shown for a device, the best value is given here; for complete and authoritative specifications, see the respective documentation
3) of the respective full scale value
Continuation:
Measured value filtering
Sampling type
Digital resolution
Special
features
KL3201
Various predefined
internal digital filters
simultaneous
16-bit
KL3202
Various predefined
multiplex
16-bit
KL3204
Various predefined
multiplex
16-bit
KL3204-0030
Various predefined
multiplex
16-bit
KL3208-0010
Various predefined
multiplex
16-bit
B parameters possible
KL3228
Various predefined
multiplex
16-bit
KL3222
Various predefined
multiplex
16-bit
for precise measurements; reduced measuring range Pt100: -200..+320 °C
KL3214
Various predefined
multiplex
16-bit
Siemens S5 data format
EL3201
Various predefined
simultaneous
16-bit
EL3201-0010
Various predefined
simultaneous
16-bit
for precise measurements; reduced measuring range Pt100 -200..+320 °C
EL3201-0020: with factory working standard calibration certificate
EL3201-0030: with external ISO17025/DAkkS calibration certificate
EL3202
Various predefined
multiplex
16-bit
EL3202-0010
Various predefined
multiplex
16-bit
EL3202-0020: with factory working standard calibration certificate
EL3202-0030: with external ISO17025/DAkkS calibration certificate
EL3204
Various predefined
multiplex
16-bit
EL3204-0162
Various predefined
multiplex
16-bit
additional 2 channels for 12 bit voltage measurement +/-10 V, < ±0.3 %
EL3204-0200
Various predefined
multiplex
16-bit
for sensor types up to 240 kΩ which otherwise cannot be measured; temperature calculation according to Steinhart-Hart, B-parameter, IEC 60751, free table
EL3208
Various predefined
multiplex
16-bit
EL3208-0010
Various predefined
multiplex
16-bit
Measuring range limited to -50...+150 °C, NTC possible
EL3214
Various predefined
multiplex
16-bit
EL3214-0090
Various predefined
multiplex
16-bit
EL3214-0090: TwinSAFE SC
EL3218
Various predefined
multiplex
16-bit
EL3692
Various predefined
multiplex
24-bit
Autorange
EL3692-0020: with factory working standard calibration certificate
EL3692-0030: with external ISO17025/DAkkS calibration certificate
EL3751
Various predefined
Freely parameterizable with
TwinCAT Filter Designer
simultaneous
24-bit
EL3751-0020: with factory calibration certificate
EL3751-0004
Various predefined
simultaneous
24-bit
EL3751-0024: with factory calibration certificate
ELM3244, ELM3246
Various predefined
multiplex
24-bit
Output in °C/ °F/K possible;
ELM3502
Various predefined
simultaneous
24-bit
ELM3502‑0030: with external ISO 17025/DAkkS calibration certificate
ELM3504
Various predefined
simultaneous
24-bit
ELM3504‑0030: with external ISO 17025/DAkkS calibration certificate
ELM3702, ELM3704
Various predefined
simultaneous
24-bit
ELM3702-0101
Various predefined
simultaneous
24-bit
EP3204-0002,
EPP3204-0002
Various predefined
multiplex
16-bit
EJ3202
Various predefined
multiplex
16-bit
EJ3214
Various predefined
multiplex
16-bit
Continuation:
RTD connection 4)
Resistance measuring range
RTD sensor types
KL3201
3-wire
0...1200 Ω, 0...5000 Ω
Pt100, Pt200, Pt500, Pt1000, Ni100, Ni120, Ni1000
KL3202
3-wire
KL3204
2-wire
KL3204-0030
2-wire
0…250 kΩ
NTC10k (Carel characteristic, 0 °C: 27280 Ω)
KL3208-0010
2-wire
0…650 kΩ
Pt1000, Ni1000, NTC
KL3228
1-wire (single-ended)
0…6500 Ω
Pt1000, Ni1000,
KL3222
4-wire
Pt100, Pt200, Pt500, Pt1000, Ni100, Ni120, Ni1000, KTY
KL3214
3-wire
0...1200 Ω, 0...4000 Ω
EL3201
3-, 4-wire
EL3201-0010
4-wire
EL3202
3-wire
EL3202-0010
4-wire
EL3204
2-wire
EL3204-0162
2-wire
EL3204-0200
2-wire
0 … 6.5/65.5/240 kΩ
various Ni/Pt characteristics, any RTD in the range 100 Ω...240 kΩ
EL3208
2-wire
EL3208-0010
2-wire
0...1 kΩ, 0...5 kΩ, 0...10 kΩ
0...1.3 MΩ
Pt1000, Ni1000, NTC 1.8 k/2.2 k/3 k/5 k/10 k/20 k/100 k
EL3214
2-, 3-wire
EL3214-0090
2-, 3-wire
EL3218
2-, 3-wire
EL3692
2-, 4-wire
0..0.1 Ω, 0..1 Ω, 0..10 Ω, 0..100 Ω, 0..1 kΩ, 0..10 kΩ, 0..100 kΩ, 0..1 MΩ, 0..10 MΩ
EL3751
2-, 3-, 4-wire
0...5 kΩ
Pt100, Pt200, Pt500, Pt1000, Ni100, Ni120, Ni1000, various KT/KTY
EL3751-0004
2-, 3-, 4-wire
0...5 kΩ
ELM3244, ELM3246
2-, 3-, 4-wire
0...50 Ω, 0...200 Ω, 0...500 Ω, 0...2 kΩ, 0...5 kΩ
ELM3502
2-, 3-, 4-wire
not usable
Pt1000
ELM3504
2-, 3-, 4-wire
not usable
Pt1000
ELM3702, ELM3704
2-, 3-, 4-wire
ELM3702-0101
2-, 3-, 4-wire
EP3204-0002,
EPP3204-0002
2-, 3-, 4-wire
0…4095 Ω
EJ3202
2-, 3-wire
EJ3214
2-, 3-wire
4) if a sensor with fewer lines is to be connected, jumpers must be set on the device