FM33xx-B110-xxxx - Technical data
Technical data | FM3312-B110-0010 | FM3332-B110-1010 |
Power supply | 24 VDC, -15…+20% (20.4 .. 28.8 V) | |
typical operating current | 120 mA (24 V) | 150 mA (24 V) |
max. operating current | 150 mA (24 V) | 180 mA (24 V) |
Power supply input protection Reverse voltage Over voltage | min. –35 V max. 35 V | |
Potential separation Thermocouples / Fieldbus | 500 V | |
Potential separation Thermocouples / Supply Voltage | 500 V | |
Potential separation Supply Voltage / Fieldbus | 100 V | |
Operating temperature | 0 °C ... + 55 °C | |
Storage temperature | -25 °C ... + 85 °C | |
Type of protection | IP65 | |
Vibration | EN 60068-2-6 10 Hz <= f <= 57 Hz: 0,075 mm amplitude 57 Hz <= f <= 150 Hz: 1,0 g | |
Shock | EN 60068-2-27 35 g @ 6 ms | |
Vibration | conforms to EN 60068-2-6 / EN 60068-2-27 | |
EMC immunity / EMC emission | conforms to EN 61000-6-2 / EN 61000-6-4 | |
Approvals | CE, cULus | |
Fieldbus/Configuration | EtherCAT/ via TwinCAT System Manager | |
Number of inputs | 12 | 32 |
Type of Input | Differential Input, mV measurement, high impedance grounded no electrical separation | |
Connection | 2-wire, direct connection | |
Wiring length (max.) | 30 m | |
Thermocouple sensor type | Type K:-100...1370°C, Type J:-100...900°C | |
Common Mode input voltage range | -8 V...+8 V | |
Common mode rejection | typical 90 dB (independent from conversion time) typical 150 dB (at 50 Hz or 60 Hz Rejection | |
Normal mode rejection | typical 98 dB (at 50 Hz or 60 Hz Rejection) | |
Resolution | 0.1 °C per Digit | |
Total measuring error (temperature) | see chapter "TC plug measurement accuracy" | |
Cold junction compensation | Internal (temperature measurement in the plug) | |
Conversation time (per channel) | Adjustable 50 ms (60 Hz Common Mode Rejection) 60 ms (50 Hz Common Mode Rejection) | |
Data update time | 200 ms (60 Hz), 230 ms (50 Hz) | |
Wiring fail indication | Yes (Open Thermocouple) | |
Back Voltage Range | >10 V, < -10 V | |
Switch off time | 3 ms max. | |
Input resistance for current limitation | 2400 R, typ. | |
Input voltage | 100 VACbetween TC+ and TC- of each channel 240 VAC above Protective Earth 415 VAC to other TC | |
Input protection mechanism | Current limitation, Channel disconnect | |
Range of Input protection | 240 VAC/DC | |
Earth connection | The plug must be connected to protective earth with the earth-connector in the plug! | |
Dimensions (L x W x H) | approx. 120 mm x 52 mm x 129 mm | |
Connector hood | Han24B (Harting) | |
Connector to Thermocouples | Han24E | Han64D |
Contacts | Hard gold plated | |
Coding system | With coding pins in the connector | |
Connctor power supply | M8 | |
Connector fieldbus | M12 | |
Weight | approx. 500 g |