Identifier Allocation
Default identifier
CANopen provides default identifiers for the most important communication objects, and these are derived from the 7-bit node address (the node ID) and a 4-bit function code in accordance with the following scheme:
Identifier Allocation 1:
For broadcast objects the node ID is set to 0. This gives rise to the following default identifiers:
Broadcast objects
Object
Function
Function code
Resulting COB ID
Object for communication Parameter / mapping
hex
dec
NMT
Boot-Up
0
0x00
0
SYNC
Synchronization
1
0x80
128
0x1005
Peer-to-peer objects
Object
Function
Function code
Resulting COB ID
hex
dec
Emergency
Status / error
1
0x81 - 0xFF
129 - 255
PDO1 (tx)
dig. inputs
11
0x181 - 0x1FF
385 - 511
0x1800
PDO1 (rx)
digital outputs
100
0x201 - 0x27F
513 - 639
0x1400
PDO2 (tx)
analog inputs
101
0x281 - 0x2FF
641 - 767
0x1801
PDO2 (rx)
analog outputs
110
0x301 - 0x37F
769 - 895
0x1401
PDO3 (tx)
analog inputs*
111
0x381 - 0x3FF
897 - 1023
0x1802
PDO3 (rx)
analog outputs*
1000
0x401 - 0x47F
1025 - 1151
0x1402
PDO4 (tx)
analog inputs*
1001
0x481 - 0x4FF
1153 - 1279
0x1803
PDO4 (rx)
analog outputs*
1010
0x501 - 0x57F
1281 - 1407
0x1403
SDO (tx)
Parameters
1011
0x581 - 0x5FF
1409 - 1535
SDO (rx)
Parameters
1100
0x601 - 0x67F
1537 - 1663
Guarding
Life/node guarding,
Heartbeat,
Boot-up message
1110
0x701 - 0x77F
1793 - 1919
(0x100C
*) The Beckhoff Default Mapping applies to PDO 3 + 4. In most configurations, PDOs 3 and 4 contain data related to analog inputs and outputs, but there can also be "excess" data from digital I/Os, or data from special terminals. Details may be found in the section covering PDO Mapping.
Up until version 3 of the CANopen specification, default identifiers were assigned to 2 PDOs at a time. The BECKHOFF Bus Couplers up to firmware status BA correspond to this issue of the specification. After firmware status C0 (CANopen version 4), default identifiers are provided for up to 4 PDOs.
Manufacture-Specific Default Identifiers for Additional PDOs
Identifiers are not assigned to the additional PDOs that are filled by the Beckhoff Bus Couplers in accordance with the standard scheme. The user must enter an identifier for these PDOs in the object directory. It is easier to activate the occupied PDOs by means of object 0x5500.
This entry in the object directory extends the default identifier allocation up to 11 PDOs. This creates the following identifiers:
Object
Function code
Resulting COB ID (hex)
Resulting COB ID (dec)
PDO5 (tx)
1101
0x681 - 0x6BF
1665 - 1727
PDO5 (rx)
1111
0x781 - 0x7BF
1921- 1983
PDO6 (tx)
111
0x1C1 - 0x1FF
449 - 511
PDO6 (rx)
1001
0x241 - 0x27F
577 - 639
PDO7 (tx)
1011
0x2C1 - 0x2FF
705 - 767
PDO7 (rx)
1101
0x341 - 0x37F
833 - 895
PDO8 (tx)
1111
0x3C1- 0x3FF
961 - 1023
PDO8 (rx)
10001
0x441 - 0x47F
1089 - 1151
PDO9 (tx)
10011
0x4C1 - 0x4FF
1217 - 1279
PDO9 (rx)
10101
0x541 - 0x57F
1345 - 1407
PDO10 (tx)
10111
0x5C1 - 0x5FF
1473 - 1535
PDO10 (rx)
11001
0x641 - 0x67F
1601- 1663
PDO11 (tx)
11011
0x6C1 - 0x6FF
1729 - 1791
PDO11 (rx)
11101
0x741 - 0x77F
1857 - 1919
Note
Warning
Index 0x5500 must not be used if Bus Couplers with more than 5 PDOs are present in networks with node numbers greater than 64, otherwise identifier overlaps can occur.