Diagnostic LEDs for PROFIBUS
These are described by the upper two LEDs.
LED green
LED red
I/O RUN
Remedy
on
on
No significance
Module waiting for communication
A baud rate has been found, start communication, incorrect identification number
off
on
No significance
Module is in Baud rate search mode
Start PROFIBUS, connect/check bus cable
off
off
No significance
Module waiting for cyclic communication
Start the cyclic PROFIBUS communication (start task)
on
flashing
No significance
Baud rate found, start up error
Parameter or configuration error, see blink code
on
off
off
DP start up OK, but still no Data_Exchange telegram received
on
off
on
Module in data exchange
no error
Parameter data error
Error code 1
The reserved, fixed UserPrm data has an incorrect value. The error code argument indicates an incorrect byte (byte 0 starts with error code argument 1).
Error code 3
The combination of certain functions, using UserPrmData, is not allowed. The error code argument gives more precise information
Error code argument
In synchronous mode it is not allowed to set the reaction to Profibus errors to "Outputs unchanged". The watchdog of the subsidiary bus system triggers more quickly than the PROFIBUS watchdog.
2-7
Reserved
8
Synchronous mode is not allowed when there are no outputs.
9-11
Reserved
12
The fast free-run mode is not allowed when synchronous mode is switched on
Error code 9
Error code 9 describes start-up errors
Error code argument
Length of the DP input data too great
2
Length of the DP output data too great
3
Length of the DP CfgData too great
4
IP Box type not recognized
5
Configuration data of DP-interface are not OK
Configuration data (CfgData) error
Error code 2
Error when comparing the configuration data. The error code argument indicates the first incorrect byte (beginning with "1")
Error code 5
Error in the length of the digital output data. The error code argument indicates the expected number of bytes.
Error code 6
Error in the length of the digital input data. The error code argument indicates the expected number of bytes.
Error code 7
Error code 7 describes CfgData errors
Error code argument
Length of the CfgData is not correct
2
Syntax of the CfgData is not correct
3
Length of the configuration data's calculated input data is too great
4
Length of the configuration data's calculated output data is too great