Example for Register Communication
Control Byte
The Control Byte is located in the output image, and can be read or written.
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
REG |
R/W |
register number | |||||
Bit |
Name |
Description | |
7 |
REG |
1bin |
Register Communication switched on: The first two Data Bytes are not used for process data exchange, but are written to the register set of the Fieldbus Box or are read from there. |
6 |
R/W |
0bin |
Read: the register should be read without changing it. |
1bin |
Write: the register should be written. | ||
5-0 |
register number |
Number of the Registers, that should be read or written. 64 Registers are addressable. | |
Status Byte
The Status-Byte is located in the output image und can only be read.
Bit |
7 |
6 |
5 |
4 |
3 |
2 |
1 |
0 |
Name |
REG |
R |
Bit |
Name |
Description | |
7 |
REG |
1bin |
receipt register number |
6 |
R |
0bin |
Read |
5-0 |
register number |
Number of the Registers, that was read or written. | |
Example 1
Byte 0 (control byte) |
Byte 1 (data out, high byte) |
Byte 2 (data out, low byte) |
0x88 (1000 1000bin) |
0xXX |
0xXX |
Bit 0.7 set indicates register
communication active
Bit 0.6 not set indicates reading the register.
Bit 0.5 to Bit 0.0 indicates with 001000bin the register
number 8.
The output data word (Byte 1 and Byte 2) has no function
at the reading access. If you want to change a register, you have
to write the desired value into the output data word.
Byte 0 (status byte) |
Byte 1 (data in, high byte) |
Byte 2 (data in, low byte) |
0x88 |
0x0C |
0x84 |
The terminal/box returns the type name 0x0C84 (equivalent unsigned integer 3204) in the input data word (Byte 1 and Byte 2).
Special feature in the naming of
Fieldbus Boxes:
The last figure of the delivered unsigned Integer (3204)
is not the same like the last character of
the Fieldbus Box name (3202),
witch stands for the connector type (0 for S8, 1 for M8 and 2 for
M12). It returns instead of that the number of channels (IE3204
owns 4 channels).
![]() | User code word In order to write into registers, you have to write the user code word (0x1235) into register 31, so that write protection is deactivated. It is activated again by writing any value other than 0x1235. Note that some of the settings that can be made in registers only become active after the next power restart (power-off/power-on) of the module. |
Example 2
Process of register communication for writing into register.
0xDF |
0x12 |
0x35 |
Answer of the module/terminal
0x9F |
0xXX |
0xXX |
0x9F |
0xXX |
0xXX |
0x9F |
0x12 |
0x35 |
CAUTIONThe given value 0x0002 is only an example! The bits of the feature register change the properties of the module und and have different meanings, depending on the module type. Please check the description of the feature register of your module (chapter register description) about the meanings of the bits in detail, before changing the values!
0xE0 |
0x00 |
0x02 |
0xA0 |
0xXX |
0xXX |
0xA0 |
0xXX |
0xXX |
0xA0 |
0x00 |
0x02 |
0xDF |
0x00 |
0x00 |
0x9F |
0xXX |
0xXX |