Object description and parameterization
![]() | EtherCAT XML Device Description The display matches that of the CoE objects from the EtherCAT XML Device Description. We recommend downloading the latest XML file from the download area of the Beckhoff website and installing it according to installation instructions. |
![]() | Parameterization via the CoE list (CAN over EtherCAT) The EtherCAT device is parameterized via the CoE-Online tab (double-click on the respective object) or via the Process Data tab (allocation of PDOs). Please note the following general CoE notes when using/manipulating the CoE parameters:
Introduction
- Objects required for parameterization during commissioning
- Objects required for the selection of the interface type
- Objects intended for regular operation, e.g. through ADS access
- Objects for indicating internal settings (may be fixed)
- Further profile-specific objects indicating inputs, outputs and status information
The following section first describes the objects required for normal operation, followed by a complete overview of missing objects.
Objects to be parameterized during commissioning
Index 1011 Restore default parameters
1011:0 | Restore default parameters | Restore default settings | UINT8 | RO | 0x01 (1dec) |
1011:01 | SubIndex 001 | If this object is set to "0x64616F6C" in the set value dialog, all backup objects are reset to their delivery state. | UINT32 | RW | 0x00000000 (0dec) |
Index 8000 COM Settings Ch.1
Index (hex) | Name | Meaning | Data type | Flags | Default | |
8000:0 | COM Settings Ch.1 |
| UINT8 | RO | 0x1A (26dec) | |
8000:02 | Enable XON/XOFF supported tx data | Enable flow control for send data. | BOOLEAN | RW | 0x00 (0dec) | |
8000:03 | Enable XON/XOFF supported rx data | Enable flow control for receive data. | BOOLEAN | RW | 0x00 (0dec) | |
8000:04 | Enable send FIFO data continuous | Enable Continuous transmission of data. | BOOLEAN | RW | 0x00 (0dec) | |
8000:05 | Enable transfer rate optimization | BOOLEAN | RW | 0x01 (1dec) | ||
8000:06 | Enable half duplex | Half duplex for RS485 mode (this bit is not evaluated in RS232 and RS422 mode) | BOOLEAN | RW | 0x00 (0dec) | |
0 | Full duplex: The module monitors its transmitted data. | |||||
1 | Half duplex: The module does not monitor the data that it has transmitted itself. | |||||
8000:07 | Enable point to point connection (RS422) | 0 | The module is used in a bus structure in accordance with the RS485 standard. | BOOLEAN | RW | 0x00 (0dec) |
1 | The module is used as a point-to-point connection (RS422) | |||||
8000:11 | Baud rate | Baud Rate | BIT4 | RW | 0x06 (6dec) | |
0x01 | 300 baud | |||||
0x02 | 600 baud | |||||
0x03 | 1200 baud | |||||
0x04 | 2400 baud | |||||
0x05 | 4800 baud | |||||
0x06 | 9600 baud | |||||
0x07 | 19200 baud | |||||
0x08 | 38400 baud | |||||
0x09 | 57600 baud | |||||
0x0A | 115200 baud | |||||
8000:15 | Data frame | Data frame / Stop bits | BIT4 | RW | 0x03 (3dec) | |
0x01 | 7E1 | |||||
0x02 | 7O1 | |||||
0x03 | 8N1 | |||||
0x04 | 8E1 | |||||
0x05 | 8O1 | |||||
0x09 | 7E2 | |||||
0x0A | 7O2 | |||||
0x0B | 8N2 | |||||
0x0C | 8E2 | |||||
0x0D | 8O2 | |||||
8000:1A | Rx buffer full notification | The value specifies the number of data in the receive FIFO, from which the bit "buffer full" is set. | UINT16 | RW | 0x0360 (864dec) | |
8000:1D | Transfer Rate Optimization Delay Threshold | Minimum length of the pause between two data sets for the Automatic summarizing of receive data. | UINT16 | RW | 0x10 (16dec) | |
Index 8010 COM Settings Ch.2
8010:0 | COM Settings Ch.2 |
8010:02 | Enable XON/XOFF supported tx data | Enable flow control for send data. | BOOLEAN | RW | 0x00 (0dec) | |
8010:03 | Enable XON/XOFF supported rx data | Enable flow control for receive data. | BOOLEAN | RW | 0x00 (0dec) | |
8010:04 | Enable send FIFO data continuous | Enable Continuous transmission of data. | BOOLEAN | RW | 0x00 (0dec) | |
8010:05 | Enable transfer rate optimization | BOOLEAN | RW | 0x01 (1dec) | ||
8010:06 | Enable half duplex | Half duplex for RS485 mode (this bit is not evaluated in RS232 and RS422 mode) | BOOLEAN | RW | 0x00 (0dec) | |
8010:07 | Enable point to point connection (RS422) | 0 | The module is used in a bus structure in accordance with the RS485 standard. | BOOLEAN | RW | 0x00 (0dec) |
8010:11 | Baud rate | Baud Rate | BIT4 | RW | 0x06 (6dec) | |
8010:15 | Data frame | Data frame / Stop bits | BIT4 | RW | 0x03 (3dec) | |
0x01 | 7E1 | |||||
0x02 | 7O1 | |||||
0x03 | 8N1 | |||||
0x04 | 8E1 | |||||
0x05 | 8O1 | |||||
0x09 | 7E2 | |||||
0x0A | 7O2 | |||||
0x0B | 8N2 | |||||
0x0C | 8E2 | |||||
0x0D | 8O2 | |||||
8010:1A | Rx buffer full notification | The value specifies the number of data in the receive FIFO, from which the bit "buffer full" is set. | UINT16 | RW | 0x0360 (864dec) | |
8010:1D | Transfer Rate Optimization Delay Threshold | Minimum length of the pause between two data sets for the Automatic summarizing of receive data. | UINT16 | RW | 0x10 (16dec) | |
Index F800 COM Settings
F800:0 | COM Settings |
| UINT8 | RO | 0x03 (3dec) | |
F800:01 | Interface Type Ch 1 | 0x00 | RS232 | BIT1 | RW | 0x00 (0dec) |
0x01 | RS485/422 | |||||
F800:02 | Interface Type Ch 2 | 0x00 | RS232 | BIT1 | RW | 0x00 (0dec) |
Additional objects
Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
1000:0 | Device type | Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile. | UINT32 | RO | 0x02581389 (39326601dec) |
Index 1008 Device name
1008:0 | Device name | Device name of the EtherCAT slave | STRING | RO | EPP6002-0002 |
Index 1009 Hardware version
1009:0 | Hardware version | Hardware version of the EtherCAT slave | STRING | RO | 00 |
Index 100A Software Version
100A:0 | Software version | Firmware version of the EtherCAT slave | STRING | RO | 00 |
Index 1018 Identity
1018:0 | Identity | Information for identifying the slave | UINT8 | RO | 0x04 (4dec) |
1018:01 | Vendor ID | Vendor ID of the EtherCAT slave | UINT32 | RO | 0x00000002 (2dec) |
1018:02 | Product code | Product code of the EtherCAT slave | UINT32 | RO | 0x17724052 (393363538dec) |
1018:03 | Revision | Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description | UINT32 | RO | 0x00100002 (1048578dec) |
1018:04 | Serial number | Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0 | UINT32 | RO | 0x00000000 (0dec) |
10F0:0 | Backup parameter handling | Information for standardized loading and saving of backup entries | UINT8 | RO | 0x01 (1dec) |
10F0:01 | Checksum | Checksum across all backup entries of the EtherCAT slave | UINT32 | RO | 0x00000000 (0dec) |
Index 1400 COM RxPDO-Par Outputs Ch.1
1400:0 | COM RxPDO-Par Outputs Ch.1 | PDO Parameter RxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1400:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 1 | OCTET-STRING[2] | RO | 04 16 |
Index 1401 COM RxPDO-Par Outputs Ch.2
1401:0 | COM RxPDO-Par Outputs Ch.2 | PDO Parameter RxPDO 2 | UINT8 | RO | 0x06 (6dec) |
1401:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 2 | OCTET-STRING[2] | RO | 05 16 |
Index 1404 COM RxPDO-Par Outputs Ch.1
1404:0 | COM RxPDO-Par Outputs Ch.1 | PDO Parameter RxPDO 5 | UINT8 | RO | 0x06 (6dec) |
1404:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 5 | OCTET-STRING[2] | RO | 00 16 |
Index 1405 COM RxPDO-Par Outputs Ch.2
1405:0 | COM RxPDO-Par Outputs Ch.2 | PDO Parameter RxPDO 6 | UINT8 | RO | 0x06 (6dec) |
1405:06 | Exclude RxPDOs | Specifies the RxPDOs (index of RxPDO mapping objects) that must not be transferred together with RxPDO 6 | OCTET-STRING[2] | RO | 01 16 |
Index 1600 COM RxPDO-Map Outputs Ch.1
1600:0 | COM RxPDO-Map Outputs Ch.1 | PDO Mapping RxPDO 1 | UINT8 | RO | 0x1C (28dec) |
1600:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x01 (Transmit request)) | UINT32 | RO | 0x7000:01, 1 |
1600:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x02 (Receive accepted)) | UINT32 | RO | 0x7000:02, 1 |
1600:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x03 (Init request)) | UINT32 | RO | 0x7000:03, 1 |
1600:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x04 (Send continuous)) | UINT32 | RO | 0x7000:04, 1 |
1600:05 | SubIndex 005 | 5. PDO Mapping entry (4 bits align) | UINT32 | RO | 0x0000:00, 4 |
1600:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x09 (Output length)) | UINT32 | RO | 0x7000:09, 8 |
1600:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x11 (Data Out 0)) | UINT32 | RO | 0x7000:11, 8 |
1600:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x12 (Data Out 1)) | UINT32 | RO | 0x7000:12, 8 |
1600:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x13 (Data Out 2)) | UINT32 | RO | 0x7000:13, 8 |
1600:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x14 (Data Out 3)) | UINT32 | RO | 0x7000:14, 8 |
1600:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x15 (Data Out 4)) | UINT32 | RO | 0x7000:15, 8 |
1600:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x16 (Data Out 5)) | UINT32 | RO | 0x7000:16, 8 |
1600:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x17 (Data Out 6)) | UINT32 | RO | 0x7000:17, 8 |
1600:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x18 (Data Out 7)) | UINT32 | RO | 0x7000:18, 8 |
1600:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x19 (Data Out 8)) | UINT32 | RO | 0x7000:19, 8 |
1600:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1A (Data Out 9)) | UINT32 | RO | 0x7000:1A, 8 |
1600:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1B (Data Out 10)) | UINT32 | RO | 0x7000:1B, 8 |
1600:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1C (Data Out 11)) | UINT32 | RO | 0x7000:1C, 8 |
1600:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1D (Data Out 12)) | UINT32 | RO | 0x7000:1D, 8 |
1600:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1E (Data Out 13)) | UINT32 | RO | 0x7000:1E, 8 |
1600:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1F (Data Out 14)) | UINT32 | RO | 0x7000:1F, 8 |
1600:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x20 (Data Out 15)) | UINT32 | RO | 0x7000:20, 8 |
1600:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x21 (Data Out 16)) | UINT32 | RO | 0x7000:21, 8 |
1600:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x22 (Data Out 17)) | UINT32 | RO | 0x7000:22, 8 |
1600:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x23 (Data Out 18)) | UINT32 | RO | 0x7000:23, 8 |
1600:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x24 (Data Out 19)) | UINT32 | RO | 0x7000:24, 8 |
1600:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x25 (Data Out 20)) | UINT32 | RO | 0x7000:25, 8 |
1600:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x26 (Data Out 21)) | UINT32 | RO | 0x7000:26, 8 |
Index 1601 COM RxPDO-Map Outputs Ch.2
1601:0 | COM RxPDO-Map Outputs Ch.2 | PDO Mapping RxPDO 2 | UINT8 | RO | 0x1C (28dec) |
1601:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x01 (Transmit request)) | UINT32 | RO | 0x7010:01, 1 |
1601:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x02 (Receive accepted)) | UINT32 | RO | 0x7010:02, 1 |
1601:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x03 (Init request)) | UINT32 | RO | 0x7010:03, 1 |
1601:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x04 (Send continuous)) | UINT32 | RO | 0x7010:04, 1 |
1601:05 | SubIndex 005 | 5. PDO Mapping entry (4 bits align) | UINT32 | RO | 0x0000:00, 4 |
1601:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x09 (Output length)) | UINT32 | RO | 0x7010:09, 8 |
1601:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x11 (Data Out 0)) | UINT32 | RO | 0x7010:11, 8 |
1601:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x12 (Data Out 1)) | UINT32 | RO | 0x7010:12, 8 |
1601:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x13 (Data Out 2)) | UINT32 | RO | 0x7010:13, 8 |
1601:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x14 (Data Out 3)) | UINT32 | RO | 0x7010:14, 8 |
1601:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x15 (Data Out 4)) | UINT32 | RO | 0x7010:15, 8 |
1601:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x16 (Data Out 5)) | UINT32 | RO | 0x7010:16, 8 |
1601:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x17 (Data Out 6)) | UINT32 | RO | 0x7010:17, 8 |
1601:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x18 (Data Out 7)) | UINT32 | RO | 0x7010:18, 8 |
1601:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x19 (Data Out 8)) | UINT32 | RO | 0x7010:19, 8 |
1601:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1A (Data Out 9)) | UINT32 | RO | 0x7010:1A, 8 |
1601:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1B (Data Out 10)) | UINT32 | RO | 0x7010:1B, 8 |
1601:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1C (Data Out 11)) | UINT32 | RO | 0x7010:1C, 8 |
1601:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1D (Data Out 12)) | UINT32 | RO | 0x7010:1D, 8 |
1601:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1E (Data Out 13)) | UINT32 | RO | 0x7010:1E, 8 |
1601:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1F (Data Out 14)) | UINT32 | RO | 0x7010:1F, 8 |
1601:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x20 (Data Out 15)) | UINT32 | RO | 0x7010:20, 8 |
1601:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x21 (Data Out 16)) | UINT32 | RO | 0x7010:21, 8 |
1601:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x22 (Data Out 17)) | UINT32 | RO | 0x7010:22, 8 |
1601:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x23 (Data Out 18)) | UINT32 | RO | 0x7010:23, 8 |
1601:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x24 (Data Out 19)) | UINT32 | RO | 0x7010:24, 8 |
1601:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x25 (Data Out 20)) | UINT32 | RO | 0x7010:25, 8 |
1601:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x26 (Data Out 21)) | UINT32 | RO | 0x7010:26, 8 |
Index 1604 COM RxPDO-Map Outputs Ch.1
1604:0 | COM RxPDO-Map Outputs Ch.1 | PDO Mapping RxPDO 5 | UINT8 | RO | 0x17 (23dec) |
1604:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7001 (Ctrl Ch.1), entry 0x01 (Ctrl)) | UINT32 | RO | 0x7001:01, 16 |
1604:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x11 (Data Out 0)) | UINT32 | RO | 0x7000:11, 8 |
1604:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x12 (Data Out 1)) | UINT32 | RO | 0x7000:12, 8 |
1604:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x13 (Data Out 2)) | UINT32 | RO | 0x7000:13, 8 |
1604:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x14 (Data Out 3)) | UINT32 | RO | 0x7000:14, 8 |
1604:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x15 (Data Out 4)) | UINT32 | RO | 0x7000:15, 8 |
1604:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x16 (Data Out 5)) | UINT32 | RO | 0x7000:16, 8 |
1604:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x17 (Data Out 6)) | UINT32 | RO | 0x7000:17, 8 |
1604:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x18 (Data Out 7)) | UINT32 | RO | 0x7000:18, 8 |
1604:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x19 (Data Out 8)) | UINT32 | RO | 0x7000:19, 8 |
1604:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1A (Data Out 9)) | UINT32 | RO | 0x7000:1A, 8 |
1604:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1B (Data Out 10)) | UINT32 | RO | 0x7000:1B, 8 |
1604:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1C (Data Out 11)) | UINT32 | RO | 0x7000:1C, 8 |
1604:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1D (Data Out 12)) | UINT32 | RO | 0x7000:1D, 8 |
1604:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1E (Data Out 13)) | UINT32 | RO | 0x7000:1E, 8 |
1604:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x1F (Data Out 14)) | UINT32 | RO | 0x7000:1F, 8 |
1604:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x20 (Data Out 15)) | UINT32 | RO | 0x7000:20, 8 |
1604:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x21 (Data Out 16)) | UINT32 | RO | 0x7000:21, 8 |
1604:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x22 (Data Out 17)) | UINT32 | RO | 0x7000:22, 8 |
1604:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x23 (Data Out 18)) | UINT32 | RO | 0x7000:23, 8 |
1604:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x24 (Data Out 19)) | UINT32 | RO | 0x7000:24, 8 |
1604:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x25 (Data Out 20)) | UINT32 | RO | 0x7000:25, 8 |
1604:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x7000 (COM Outputs Ch.1), entry 0x26 (Data Out 21)) | UINT32 | RO | 0x7000:26, 8 |
Index 1605 COM RxPDO-Map Outputs Ch.2
1605:0 | COM RxPDO-Map Outputs Ch.2 | PDO Mapping RxPDO 6 | UINT8 | RO | 0x17 (23dec) |
1605:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x7011 (Ctrl Ch.2), entry 0x01 (Ctrl)) | UINT32 | RO | 0x7011:01, 16 |
1605:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x11 (Data Out 0)) | UINT32 | RO | 0x7010:11, 8 |
1605:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x12 (Data Out 1)) | UINT32 | RO | 0x7010:12, 8 |
1605:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x13 (Data Out 2)) | UINT32 | RO | 0x7010:13, 8 |
1605:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x14 (Data Out 3)) | UINT32 | RO | 0x7010:14, 8 |
1605:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x15 (Data Out 4)) | UINT32 | RO | 0x7010:15, 8 |
1605:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x16 (Data Out 5)) | UINT32 | RO | 0x7010:16, 8 |
1605:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x17 (Data Out 6)) | UINT32 | RO | 0x7010:17, 8 |
1605:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x18 (Data Out 7)) | UINT32 | RO | 0x7010:18, 8 |
1605:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x19 (Data Out 8)) | UINT32 | RO | 0x7010:19, 8 |
1605:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1A (Data Out 9)) | UINT32 | RO | 0x7010:1A, 8 |
1605:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1B (Data Out 10)) | UINT32 | RO | 0x7010:1B, 8 |
1605:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1C (Data Out 11)) | UINT32 | RO | 0x7010:1C, 8 |
1605:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1D (Data Out 12)) | UINT32 | RO | 0x7010:1D, 8 |
1605:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1E (Data Out 13)) | UINT32 | RO | 0x7010:1E, 8 |
1605:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x1F (Data Out 14)) | UINT32 | RO | 0x7010:1F, 8 |
1605:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x20 (Data Out 15)) | UINT32 | RO | 0x7010:20, 8 |
1605:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x21 (Data Out 16)) | UINT32 | RO | 0x7010:21, 8 |
1605:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x22 (Data Out 17)) | UINT32 | RO | 0x7010:22, 8 |
1605:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x23 (Data Out 18)) | UINT32 | RO | 0x7010:23, 8 |
1605:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x24 (Data Out 19)) | UINT32 | RO | 0x7010:24, 8 |
1605:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x25 (Data Out 20)) | UINT32 | RO | 0x7010:25, 8 |
1605:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x7010 (COM Outputs Ch.2), entry 0x26 (Data Out 21)) | UINT32 | RO | 0x7010:26, 8 |
Index 1800 COM TxPDO-Par Inputs Ch.1
1800:0 | COM TxPDO-Par Inputs Ch.1 | PDO parameter TxPDO 1 | UINT8 | RO | 0x06 (6dec) |
1800:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1 | OCTET-STRING[2] | RO | 04 1A |
Index 1801 COM TxPDO-Par Inputs Ch.2
1801:0 | COM TxPDO-Par Inputs Ch.2 | PDO parameter TxPDO 2 | UINT8 | RO | 0x06 (6dec) |
1801:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2 | OCTET-STRING[2] | RO | 05 1A |
Index 1804 COM TxPDO-Par Inputs Ch.1
1804:0 | COM TxPDO-Par Inputs Ch.1 | PDO parameter TxPDO 5 | UINT8 | RO | 0x06 (6dec) |
1804:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 5 | OCTET-STRING[2] | RO | 00 1A |
Index 1805 COM TxPDO-Par Inputs Ch.2
1805:0 | COM TxPDO-Par Inputs Ch.2 | PDO parameter TxPDO 6 | UINT8 | RO | 0x06 (6dec) |
1805:06 | Exclude TxPDOs | Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 6 | OCTET-STRING[2] | RO | 01 1A |
Index 1A00 COM TxPDO-Map Inputs Ch.1
1A00:0 | COM TxPDO-Map Inputs Ch.1 | PDO Mapping TxPDO 1 | UINT8 | RO | 0x1F (31dec) |
1A00:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x01 (Transmit accepted)) | UINT32 | RO | 0x6000:01, 1 |
1A00:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x02 (Receive request)) | UINT32 | RO | 0x6000:02, 1 |
1A00:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x03 (Init accepted)) | UINT32 | RO | 0x6000:03, 1 |
1A00:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x04 (Buffer full)) | UINT32 | RO | 0x6000:04, 1 |
1A00:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x05 (Parity error)) | UINT32 | RO | 0x6000:05, 1 |
1A00:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x06 (Framing error)) | UINT32 | RO | 0x6000:06, 1 |
1A00:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x07 (Overrun error)) | UINT32 | RO | 0x6000:07, 1 |
1A00:08 | SubIndex 008 | 8. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A00:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x09 (Input length)) | UINT32 | RO | 0x6000:09, 8 |
1A00:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x11 (Data In 0)) | UINT32 | RO | 0x6000:11, 8 |
1A00:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x12 (Data In 1)) | UINT32 | RO | 0x6000:12, 8 |
1A00:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x13 (Data In 2)) | UINT32 | RO | 0x6000:13, 8 |
1A00:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x14 (Data In 3)) | UINT32 | RO | 0x6000:14, 8 |
1A00:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x15 (Data In 4)) | UINT32 | RO | 0x6000:15, 8 |
1A00:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x16 (Data In 5)) | UINT32 | RO | 0x6000:16, 8 |
1A00:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x17 (Data In 6)) | UINT32 | RO | 0x6000:17, 8 |
1A00:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x18 (Data In 7)) | UINT32 | RO | 0x6000:18, 8 |
1A00:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x19 (Data In 8)) | UINT32 | RO | 0x6000:19, 8 |
1A00:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1A (Data In 9)) | UINT32 | RO | 0x6000:1A, 8 |
1A00:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1B (Data In 10)) | UINT32 | RO | 0x6000:1B, 8 |
1A00:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1C (Data In 11)) | UINT32 | RO | 0x6000:1C, 8 |
1A00:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1D (Data In 12)) | UINT32 | RO | 0x6000:1D, 8 |
1A00:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1E (Data In 13)) | UINT32 | RO | 0x6000:1E, 8 |
1A00:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1F (Data In 14)) | UINT32 | RO | 0x6000:1F, 8 |
1A00:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x20 (Data In 15)) | UINT32 | RO | 0x6000:20, 8 |
1A00:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x21 (Data In 16)) | UINT32 | RO | 0x6000:21, 8 |
1A00:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x22 (Data In 17)) | UINT32 | RO | 0x6000:22, 8 |
1A00:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x23 (Data In 18)) | UINT32 | RO | 0x6000:23, 8 |
1A00:1D | SubIndex 029 | 29. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x24 (Data In 19)) | UINT32 | RO | 0x6000:24, 8 |
1A00:1E | SubIndex 030 | 30. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x25 (Data In 20)) | UINT32 | RO | 0x6000:25, 8 |
1A00:1F | SubIndex 031 | 31. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x26 (Data In 21)) | UINT32 | RO | 0x6000:26, 8 |
Index 1A01 COM TxPDO-Map Inputs Ch.2
1A01:0 | COM TxPDO-Map Inputs Ch.2 | PDO Mapping TxPDO 2 | UINT8 | RO | 0x1F (31dec) |
1A01:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x01 (Transmit accepted)) | UINT32 | RO | 0x6010:01, 1 |
1A01:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x02 (Receive request)) | UINT32 | RO | 0x6010:02, 1 |
1A01:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x03 (Init accepted)) | UINT32 | RO | 0x6010:03, 1 |
1A01:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x04 (Buffer full)) | UINT32 | RO | 0x6010:04, 1 |
1A01:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x05 (Parity error)) | UINT32 | RO | 0x6010:05, 1 |
1A01:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x06 (Framing error)) | UINT32 | RO | 0x6010:06, 1 |
1A01:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x07 (Overrun error)) | UINT32 | RO | 0x6010:07, 1 |
1A01:08 | SubIndex 008 | 8. PDO Mapping entry (1 bits align) | UINT32 | RO | 0x0000:00, 1 |
1A01:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x09 (Input length)) | UINT32 | RO | 0x6010:09, 8 |
1A01:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x11 (Data In 0)) | UINT32 | RO | 0x6010:11, 8 |
1A01:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x12 (Data In 1)) | UINT32 | RO | 0x6010:12, 8 |
1A01:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x13 (Data In 2)) | UINT32 | RO | 0x6010:13, 8 |
1A01:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x14 (Data In 3)) | UINT32 | RO | 0x6010:14, 8 |
1A01:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x15 (Data In 4)) | UINT32 | RO | 0x6010:15, 8 |
1A01:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x16 (Data In 5)) | UINT32 | RO | 0x6010:16, 8 |
1A01:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x17 (Data In 6)) | UINT32 | RO | 0x6010:17, 8 |
1A01:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x18 (Data In 7)) | UINT32 | RO | 0x6010:18, 8 |
1A01:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x19 (Data In 8)) | UINT32 | RO | 0x6010:19, 8 |
1A01:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1A (Data In 9)) | UINT32 | RO | 0x6010:1A, 8 |
1A01:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1B (Data In 10)) | UINT32 | RO | 0x6010:1B, 8 |
1A01:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1C (Data In 11)) | UINT32 | RO | 0x6010:1C, 8 |
1A01:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1D (Data In 12)) | UINT32 | RO | 0x6010:1D, 8 |
1A01:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1E (Data In 13)) | UINT32 | RO | 0x6010:1E, 8 |
1A01:18 | SubIndex 024 | 24. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1F (Data In 14)) | UINT32 | RO | 0x6010:1F, 8 |
1A01:19 | SubIndex 025 | 25. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x20 (Data In 15)) | UINT32 | RO | 0x6010:20, 8 |
1A01:1A | SubIndex 026 | 26. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x21 (Data In 16)) | UINT32 | RO | 0x6010:21, 8 |
1A01:1B | SubIndex 027 | 27. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x22 (Data In 17)) | UINT32 | RO | 0x6010:22, 8 |
1A01:1C | SubIndex 028 | 28. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x23 (Data In 18)) | UINT32 | RO | 0x6010:23, 8 |
1A01:1D | SubIndex 029 | 29. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x24 (Data In 19)) | UINT32 | RO | 0x6010:24, 8 |
1A01:1E | SubIndex 030 | 30. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x25 (Data In 20)) | UINT32 | RO | 0x6010:25, 8 |
1A01:1F | SubIndex 031 | 31. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x26 (Data In 21)) | UINT32 | RO | 0x6010:26, 8 |
Index 1A04 COM TxPDO-Map Inputs Ch.1
1A04:0 | COM TxPDO-Map Inputs Ch.1 | PDO Mapping TxPDO 5 | UINT8 | RO | 0x17 (23dec) |
1A04:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6001 (Status Ch.1), entry 0x01 (Status)) | UINT32 | RO | 0x6001:01, 16 |
1A04:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x11 (Data In 0)) | UINT32 | RO | 0x6000:11, 8 |
1A04:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x12 (Data In 1)) | UINT32 | RO | 0x6000:12, 8 |
1A04:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x13 (Data In 2)) | UINT32 | RO | 0x6000:13, 8 |
1A04:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x14 (Data In 3)) | UINT32 | RO | 0x6000:14, 8 |
1A04:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x15 (Data In 4)) | UINT32 | RO | 0x6000:15, 8 |
1A04:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x16 (Data In 5)) | UINT32 | RO | 0x6000:16, 8 |
1A04:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x17 (Data In 6)) | UINT32 | RO | 0x6000:17, 8 |
1A04:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x18 (Data In 7)) | UINT32 | RO | 0x6000:18, 8 |
1A04:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x19 (Data In 8)) | UINT32 | RO | 0x6000:19, 8 |
1A04:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1A (Data In 9)) | UINT32 | RO | 0x6000:1A, 8 |
1A04:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1B (Data In 10)) | UINT32 | RO | 0x6000:1B, 8 |
1A04:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1C (Data In 11)) | UINT32 | RO | 0x6000:1C, 8 |
1A04:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1D (Data In 12)) | UINT32 | RO | 0x6000:1D, 8 |
1A04:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1E (Data In 13)) | UINT32 | RO | 0x6000:1E, 8 |
1A04:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x1F (Data In 14)) | UINT32 | RO | 0x6000:1F, 8 |
1A04:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x20 (Data In 15)) | UINT32 | RO | 0x6000:20, 8 |
1A04:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x21 (Data In 16)) | UINT32 | RO | 0x6000:21, 8 |
1A04:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x22 (Data In 17)) | UINT32 | RO | 0x6000:22, 8 |
1A04:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x23 (Data In 18)) | UINT32 | RO | 0x6000:23, 8 |
1A04:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x24 (Data In 19)) | UINT32 | RO | 0x6000:24, 8 |
1A04:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x25 (Data In 20)) | UINT32 | RO | 0x6000:25, 8 |
1A04:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x6000 (COM Inputs Ch.1), entry 0x26 (Data In 21)) | UINT32 | RO | 0x6000:26, 8 |
Index 1A05 COM TxPDO-Map Inputs Ch.2
1A05:0 | COM TxPDO-Map Inputs Ch.2 | PDO Mapping TxPDO 6 | UINT8 | RO | 0x17 (23dec) |
1A05:01 | SubIndex 001 | 1. PDO Mapping entry (object 0x6011 (Status Ch.2), entry 0x01 (Status)) | UINT32 | RO | 0x6011:01, 16 |
1A05:02 | SubIndex 002 | 2. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x11 (Data In 0)) | UINT32 | RO | 0x6010:11, 8 |
1A05:03 | SubIndex 003 | 3. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x12 (Data In 1)) | UINT32 | RO | 0x6010:12, 8 |
1A05:04 | SubIndex 004 | 4. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x13 (Data In 2)) | UINT32 | RO | 0x6010:13, 8 |
1A05:05 | SubIndex 005 | 5. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x14 (Data In 3)) | UINT32 | RO | 0x6010:14, 8 |
1A05:06 | SubIndex 006 | 6. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x15 (Data In 4)) | UINT32 | RO | 0x6010:15, 8 |
1A05:07 | SubIndex 007 | 7. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x16 (Data In 5)) | UINT32 | RO | 0x6010:16, 8 |
1A05:08 | SubIndex 008 | 8. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x17 (Data In 6)) | UINT32 | RO | 0x6010:17, 8 |
1A05:09 | SubIndex 009 | 9. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x18 (Data In 7)) | UINT32 | RO | 0x6010:18, 8 |
1A05:0A | SubIndex 010 | 10. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x19 (Data In 8)) | UINT32 | RO | 0x6010:19, 8 |
1A05:0B | SubIndex 011 | 11. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1A (Data In 9)) | UINT32 | RO | 0x6010:1A, 8 |
1A05:0C | SubIndex 012 | 12. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1B (Data In 10)) | UINT32 | RO | 0x6010:1B, 8 |
1A05:0D | SubIndex 013 | 13. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1C (Data In 11)) | UINT32 | RO | 0x6010:1C, 8 |
1A05:0E | SubIndex 014 | 14. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1D (Data In 12)) | UINT32 | RO | 0x6010:1D, 8 |
1A05:0F | SubIndex 015 | 15. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1E (Data In 13)) | UINT32 | RO | 0x6010:1E, 8 |
1A05:10 | SubIndex 016 | 16. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x1F (Data In 14)) | UINT32 | RO | 0x6010:1F, 8 |
1A05:11 | SubIndex 017 | 17. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x20 (Data In 15)) | UINT32 | RO | 0x6010:20, 8 |
1A05:12 | SubIndex 018 | 18. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x21 (Data In 16)) | UINT32 | RO | 0x6010:21, 8 |
1A05:13 | SubIndex 019 | 19. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x22 (Data In 17)) | UINT32 | RO | 0x6010:22, 8 |
1A05:14 | SubIndex 020 | 20. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x23 (Data In 18)) | UINT32 | RO | 0x6010:23, 8 |
1A05:15 | SubIndex 021 | 21. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x24 (Data In 19)) | UINT32 | RO | 0x6010:24, 8 |
1A05:16 | SubIndex 022 | 22. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x25 (Data In 20)) | UINT32 | RO | 0x6010:25, 8 |
1A05:17 | SubIndex 023 | 23. PDO Mapping entry (object 0x6010 (COM Inputs Ch.2), entry 0x26 (Data In 21)) | UINT32 | RO | 0x6010:26, 8 |
Index 1C00 Sync manager type
1C00:0 | Sync manager type | Using the Sync Managers | UINT8 | RO | 0x04 (4dec) |
1C00:01 | SubIndex 001 | Sync-Manager Type Channel 1: Mailbox Write | UINT8 | RO | 0x01 (1dec) |
1C00:02 | SubIndex 002 | Sync-Manager Type Channel 2: Mailbox Read | UINT8 | RO | 0x02 (2dec) |
1C00:03 | SubIndex 003 | Sync-Manager Type Channel 3: Process Data Write (Outputs) | UINT8 | RO | 0x03 (3dec) |
1C00:04 | SubIndex 004 | Sync-Manager Type Channel 4: Process Data Read (Inputs) | UINT8 | RO | 0x04 (4dec) |
Index 1C12 RxPDO assign
1C12:0 | RxPDO assign | PDO Assign Outputs | UINT8 | RW | 0x02 (2dec) |
1C12:01 | Subindex 001 | 1. allocated RxPDO (contains the index of the associated RxPDO mapping object) | UINT16 | RW | 0x1604 (5636dec) |
1C12:02 | Subindex 002 | 2. allocated RxPDO (contains the index of the associated RxPDO mapping object) | UINT16 | RW | 0x1605 (5637dec) |
Index 1C13 TxPDO assign
1C13:0 | TxPDO assign | PDO Assign Inputs | UINT8 | RW | 0x02 (2dec) |
1C13:01 | Subindex 001 | 1. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A04 (6660dec) |
1C13:02 | Subindex 002 | 2. allocated TxPDO (contains the index of the associated TxPDO mapping object) | UINT16 | RW | 0x1A05 (6661dec) |
1C32:0 | SM output parameter | Synchronization parameters for the outputs | UINT8 | RO | 0x20 (32dec) |
1C32:01 | Sync mode | Current synchronization mode:
| UINT16 | RW | 0x0000 (0dec) |
1C32:02 | Cycle time | Cycle time (in ns):
| UINT32 | RW | 0x000F4240 (1000000dec) |
1C32:03 | Shift time | Time between SYNC0 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000384 (900dec) |
1C32:04 | Sync modes supported | Supported synchronization modes:
| UINT16 | RO | 0xC007 (49159dec) |
1C32:05 | Minimum cycle time | Minimum cycle time (in ns) | UINT32 | RO | 0x00002710 (10000dec) |
1C32:06 | Calc and copy time | Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only) | UINT32 | RO | 0x00000000 (0dec) |
1C32:07 | Minimum delay time |
1C32:08 | Command |
The entries 1C32:03, 1C32:05, 1C32:06, 1C32:09, 1C33:03, 1C33:06, 1C33:09 are updated with the maximum measured values. | UINT16 | RW | 0x0000 (0dec) |
1C32:09 | Maximum Delay time | Time between SYNC1 event and output of the outputs (in ns, DC mode only) | UINT32 | RO | 0x00000384 (900dec) |
1C32:0B | SM event missed counter | Number of missed SM events in OPERATIONAL (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:0C | Cycle exceeded counter | Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early) | UINT16 | RO | 0x0000 (0dec) |
1C32:0D | Shift too short counter | Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only) | UINT16 | RO | 0x0000 (0dec) |
1C32:20 | Sync error | The synchronization was not correct in the last cycle (outputs were output too late; DC mode only) | BOOLEAN | RO | 0x00 (0dec) |
Index 1C33 SM input parameter
1C33:0 | SM input parameter | Synchronization parameters for the inputs | UINT8 | RO | 0x20 (32dec) |
1C33:01 | Sync mode | Current synchronization mode:
1C33:02 | Cycle time | as 1C32:02 | UINT32 | RW | 0x000F4240 (1000000dec) |
1C33:03 | Shift time | Time between SYNC0 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000384 (900dec) |
1C33:04 | Sync modes supported | Supported synchronization modes:
1C33:05 | Minimum cycle time | as 1C32:05 | UINT32 | RO | 0x00002710 (10000dec) |
1C33:06 | Calc and copy time | Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode) | UINT32 | RO | 0x00000000 (0dec) |
1C33:07 | Minimum delay time |
1C33:08 | Command | as 1C32:08 | UINT16 | RW | 0x0000 (0dec) |
1C33:09 | Maximum Delay time | Time between SYNC1 event and reading of the inputs (in ns, only DC mode) | UINT32 | RO | 0x00000384 (900dec) |
1C33:0B | SM event missed counter | as 1C32:11 | UINT16 | RO | 0x0000 (0dec) |
1C33:0C | Cycle exceeded counter | as 1C32:12 | UINT16 | RO | 0x0000 (0dec) |
1C33:0D | Shift too short counter | as 1C32:13 | UINT16 | RO | 0x0000 (0dec) |
1C33:20 | Sync error | as 1C32:32 | BOOLEAN | RO | 0x00 (0dec) |
Profile-specific objects (0x6000-0xFFFF)
The profile-specific objects have the same meaning for all EtherCAT slaves that support the profile 5001.
Index 6000 COM Inputs Ch.1
6000:0 | COM Inputs Ch.1 |
| UINT8 | RO | 0x26 (38dec) |
6000:01 | Transmit accepted | The module acknowledges receipt of data by changing the state of this bit | BOOLEAN | RO | 0x00 (0dec) |
6000:02 | Receive request | By changing the state of this bit, the module informs the controller that the DataIn bytes contain the number of bytes displayed in "Input length" | BOOLEAN | RO | 0x00 (0dec) |
6000:03 | Init Accepted | The initialization is carried out from the terminal | BOOLEAN | RO | 0x00 (0dec) |
6000:04 | Buffer full | The receive FIFO is full | BOOLEAN | RO | 0x00 (0dec) |
6000:05 | Parity error | A parity error has occurred | BOOLEAN | RO | 0x00 (0dec) |
6000:06 | Framing error | A framing error has occurred | BOOLEAN | RO | 0x00 (0dec) |
6000:07 | Overrun error | An overrun error has occurred | BOOLEAN | RO | 0x00 (0dec) |
6000:09 | Input length | Number of input bytes available for transfer from the terminal to the controller | UINT8 | RO | 0x00 (0dec) |
6000:11 | Data In 0 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:12 | Data In 1 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:13 | Data In 2 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:14 | Data In 3 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:15 | Data In 4 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:16 | Data In 5 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:17 | Data In 6 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:18 | Data In 7 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:19 | Data In 8 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:1A | Data In 9 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:1B | Data In 10 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:1C | Data In 11 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:1D | Data In 12 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:1E | Data In 13 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:1F | Data In 14 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:20 | Data In 15 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:21 | Data In 16 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:22 | Data In 17 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:23 | Data In 18 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:24 | Data In 19 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:25 | Data In 20 | Input data | UINT8 | RO | 0x00 (0dec) |
6000:26 | Data In 21 | Input data | UINT8 | RO | 0x00 (0dec) |
Index 6001 Status Ch.1
6001:0 | Status Ch.1 |
6001:01 | Status | Status word for compatible process image | UINT16 | RO | 0x0000 (0dec) |
Index 6010 COM Inputs Ch.2
6010:0 | COM Inputs Ch.2 |
6010:01 | Transmit accepted | The module acknowledges receipt of data by changing the state of this bit | BOOLEAN | RO | 0x00 (0dec) |
6010:02 | Receive request | By changing the state of this bit, the module informs the controller that the DataIn bytes contain the number of bytes displayed in "Input length" | BOOLEAN | RO | 0x00 (0dec) |
6010:03 | Init Accepted | The initialization is carried out from the terminal | BOOLEAN | RO | 0x00 (0dec) |
6010:04 | Buffer full | The receive FIFO is full | BOOLEAN | RO | 0x00 (0dec) |
6010:05 | Parity error | A parity error has occurred | BOOLEAN | RO | 0x00 (0dec) |
6010:06 | Framing error | A framing error has occurred | BOOLEAN | RO | 0x00 (0dec) |
6010:07 | Overrun error | An overrun error has occurred | BOOLEAN | RO | 0x00 (0dec) |
6010:09 | Input length | Number of input bytes available for transfer from the terminal to the controller | UINT8 | RO | 0x00 (0dec) |
6010:11 | Data In 0 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:12 | Data In 1 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:13 | Data In 2 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:14 | Data In 3 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:15 | Data In 4 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:16 | Data In 5 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:17 | Data In 6 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:18 | Data In 7 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:19 | Data In 8 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:1A | Data In 9 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:1B | Data In 10 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:1C | Data In 11 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:1D | Data In 12 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:1E | Data In 13 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:1F | Data In 14 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:20 | Data In 15 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:21 | Data In 16 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:22 | Data In 17 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:23 | Data In 18 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:24 | Data In 19 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:25 | Data In 20 | Input data | UINT8 | RO | 0x00 (0dec) |
6010:26 | Data In 21 | Input data | UINT8 | RO | 0x00 (0dec) |
Index 6011 Status Ch.2
6011:0 | Status Ch.2 |
6011:01 | Status | Status word for compatible process image | UINT16 | RO | 0x0000 (0dec) |
Index 7000 COM Outputs Ch.1
7000:0 | COM Outputs Ch.1 |
7000:01 | Transmit request | By changing the state of this bit, the controller informs the terminal that the DataOut bytes contain the number of bytes displayed in "Output length". | BOOLEAN | RO | 0x00 (0dec) |
7000:02 | Receive accepted | The controller acknowledges receipt of data by changing the state of this bit. | BOOLEAN | RO | 0x00 (0dec) |
7000:03 | Init request | The controller requests the module to initialize. | BOOLEAN | RO | 0x00 (0dec) |
7000:04 | Send continuous | Continuous sending of data from the FIFO. | BOOLEAN | RO | 0x00 (0dec) |
7000:09 | Output length | Number of output bytes available for transfer from the controller to the terminal. | UINT8 | RO | 0x00 (0dec) |
7000:11 | Data Out 0 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:12 | Data Out 1 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:13 | Data Out 2 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:14 | Data Out 3 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:15 | Data Out 4 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:16 | Data Out 5 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:17 | Data Out 6 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:18 | Data Out 7 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:19 | Data Out 8 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:1A | Data Out 9 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:1B | Data Out 10 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:1C | Data Out 11 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:1D | Data Out 12 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:1E | Data Out 13 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:1F | Data Out 14 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:20 | Data Out 15 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:21 | Data Out 16 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:22 | Data Out 17 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:23 | Data Out 18 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:24 | Data Out 19 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:25 | Data Out 20 | Output data | UINT8 | RO | 0x00 (0dec) |
7000:26 | Data Out 21 | Output data | UINT8 | RO | 0x00 (0dec) |
Index 7001 Ctrl Ch.1
7001:0 | Ctrl Ch.1 |
7001:01 | Ctrl | Control word for compatible process image | UINT16 | RO | 0x0000 (0dec) |
Index 7010 COM Outputs Ch.2
7010:0 | COM Outputs Ch.2 |
7010:01 | Transmit request | By changing the state of this bit, the controller informs the terminal that the DataOut bytes contain the number of bytes displayed in "Output length". | BOOLEAN | RO | 0x00 (0dec) |
7010:02 | Receive accepted | The controller acknowledges receipt of data by changing the state of this bit. | BOOLEAN | RO | 0x00 (0dec) |
7010:03 | Init request | The controller requests the module to initialize. | BOOLEAN | RO | 0x00 (0dec) |
7010:04 | Send continuous | Continuous sending of data from the FIFO. | BOOLEAN | RO | 0x00 (0dec) |
7010:09 | Output length | Number of output bytes available for transfer from the controller to the terminal. | UINT8 | RO | 0x00 (0dec) |
7010:11 | Data Out 0 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:12 | Data Out 1 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:13 | Data Out 2 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:14 | Data Out 3 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:15 | Data Out 4 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:16 | Data Out 5 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:17 | Data Out 6 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:18 | Data Out 7 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:19 | Data Out 8 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:1A | Data Out 9 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:1B | Data Out 10 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:1C | Data Out 11 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:1D | Data Out 12 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:1E | Data Out 13 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:1F | Data Out 14 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:20 | Data Out 15 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:21 | Data Out 16 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:22 | Data Out 17 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:23 | Data Out 18 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:24 | Data Out 19 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:25 | Data Out 20 | Output data | UINT8 | RO | 0x00 (0dec) |
7010:26 | Data Out 21 | Output data | UINT8 | RO | 0x00 (0dec) |
Index 7011 Ctrl Ch.2
7011:0 | Ctrl Ch.2 |
7011:01 | Ctrl | Control word for compatible process image | UINT16 | RO | 0x0000 (0dec) |
Index A000 COM Diag data Ch.1
A000:0 | COM Diag data Ch.1 |
| UINT8 | RO | 0x21 (33dec) |
A000:01 | Buffer overflow | A buffer overflow has occurred. | BOOLEAN | RO | 0x00 (0dec) |
A000:02 | Parity error | A parity error has occurred. | BOOLEAN | RO | 0x00 (0dec) |
A000:03 | Framing error | A framing error has occurred. | BOOLEAN | RO | 0x00 (0dec) |
A000:04 | Overrun error | An overrun error has occurred. | BOOLEAN | RO | 0x00 (0dec) |
A000:05 | Buffer full | The receive FIFO is full. | BOOLEAN | RO | 0x00 (0dec) |
A000:11 | Data bytes in send buffer | Number of data bytes in the send FIFO | UINT16 | RO | 0x0000 (0dec) |
A000:21 | Data bytes in receive buffer | Number of data bytes in the receive FIFO | UINT16 | RO | 0x0000 (0dec) |
Index A010 COM Diag data Ch.2
A010:0 | COM Diag data Ch.2 |
A010:01 | Buffer overflow | A buffer overflow has occurred. | BOOLEAN | RO | 0x00 (0dec) |
A010:02 | Parity error | A parity error has occurred. | BOOLEAN | RO | 0x00 (0dec) |
A010:03 | Framing error | A framing error has occurred. | BOOLEAN | RO | 0x00 (0dec) |
A010:04 | Overrun error | An overrun error has occurred. | BOOLEAN | RO | 0x00 (0dec) |
A010:05 | Buffer full | The receive FIFO is full. | BOOLEAN | RO | 0x00 (0dec) |
A010:11 | Data bytes in send buffer | Number of data bytes in the send FIFO | UINT16 | RO | 0x0000 (0dec) |
A010:21 | Data bytes in receive buffer | Number of data bytes in the receive FIFO | UINT16 | RO | 0x0000 (0dec) |
F000:0 | Modular device profile | General information for the modular device profile | UINT8 | RO | 0x02 (2dec) |
F000:01 | Module index distance | Index distance of the objects of the individual channels | UINT16 | RO | 0x0010 (16dec) |
F000:02 | Maximum number of modules | Number of channels | UINT16 | RO | 0x0002 (2dec) |
Index F008 Code word
F008:0 | Code word |
Index F010 Module list
F010:0 | Module list |
F010:01 | SubIndex 001 |
| UINT32 | RW | 0x00000258 (600dec) |
F010:02 | SubIndex 002 |