Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
Technical data
EPP6001-0002
Fieldbus
     Fieldbus
EtherCAT
     Connection
EtherCAT P: Combined connection for EtherCAT and supply voltages
Input: 1 x M8 socket, 4-pin, P-coded
Downstream connection: 1 x M8 socket, 4-pin, P-coded
Supply voltages
     Connection
See Fieldbus connection
     Control voltage US
          Nominal voltage
24 VDC (-15 % / +20 %)
          Sum current
max. 3 A 1)
          Consumers
• Module electronics: 100 mA
• Remote communication station (e.g. barcode scanner)
• Loads at digital outputs
     Peripheral voltage UP
          Nominal voltage
          Sum current
max. 3 A 1)
          Current consumption from UP
None. UP is only forwarded.
Serial interface
     Number of channels
1
     Interface type
Parameterizable:
  • RS232
  • RS422
  • RS485
     Connection
RS232: 1x M12 socket
RS422: 2x M12 socket
RS485: 1x M12 socket
     End device supply voltage 2)
5 VDC from the control voltage US
max. 1 A, short-circuit proof
     Cable length
RS232: max. 15 m
RS422/RS485: max. 1,000 m
     Data transfer rate
Parameterizable:
300 .. 115,200 baud (bit/s)
     Data format
Parameterizable:
8N1, 7E1, 7O1, 8N1, 8E1, 8O1, 7E2, 7O2, 8N2, 8E2, 8O2
     Bit distortion
< 3 %
1) Sum current of consumers and power transmission.
2) Supply voltage available at the connections of the serial interface.
Technical data
EPP6001-0002
Digital inputs/outputs
     Number
2
     Connection
1x M12 socket
     I/O supply voltage 3)
24 VDC from the control voltage US
max. 0.5 A, short-circuit proof
     Input specification
          Characteristics
Type 3 according to EN 61131-2, compatible with type 1
          Input filter
10 µs
          Signal voltage “0”
-3 .. +5 VDC
          Signal voltage "1"
+11 .. +30 VDC
          Input current
3 mA at 24 VDC
     Output specification
          Load type
ohmic, inductive, lamp load
          Nominal voltage
24 VDC (-15%/+20%) from the control voltage US
          Output current
max. 0.5 A per channel, short-circuit proof
Environmental conditions
     Ambient temperature during operation
-25…+60 °C
-25…+55 °C according to cULus
     Ambient temperature during storage
-40…+85 °C
     Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
Additional checks
     EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
     Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Mechanics
     Weight
approx. 165 g
     Installation position
variable
Approvals and conformity
     Approvals
CE, cULus
3) Supply voltage available at the connection of the digital inputs/outputs.