Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
Technical data
EPP4374-0002
Fieldbus
     Fieldbus
EtherCAT
     Connection
EtherCAT P: Combined connection for EtherCAT and supply voltages
Input: 1 x M8 socket, 4-pin, P-coded
Downstream connection: 1 x M8 socket, 4-pin, P-coded
Supply voltages
     Connection
See Fieldbus connection
     Control voltage US
          Nominal voltage
24 VDC (-15 % / +20 %)
          Sum current
max. 3 A 1)
          Consumers
Module electronics: 120 mA at 24 VDC
     Peripheral voltage UP
          Nominal voltage
          Sum current
max. 3 A 1)
          Consumers
• Sensors 2)
• Actuators 2)
Analog inputs
     Number
2
     Connection
M12 socket, 5-pin connection
     Signal range
Parameterizable:
  • -10 .. +10 V (default)
  • 0 .. 10 V
  • 0 .. 20 mA
  • 4 .. 20 mA
     Electrical specifications
     Sensor/actuator
     supply voltage 3)
from the peripheral voltage UP
max. 3 A in total, not short-circuit proof
Analog outputs
     Number
2
     Connection
     Output signal range
Parameterizable:
  • 0 .. 10 V
  • 0 .. 20 mA
  • 4 .. 20 mA
     Sensor/actuator
     supply voltage 3)
1) Sum current of consumers and power transmission.
2) "Actuators": Field devices that are intended to be connected to outputs.
   "Sensors": Field devices that are intended to be connected to inputs.
3) Supply voltage that is available on the plug connectors of the analog interfaces.
Technical data
EPP4374-0002
Environmental conditions
     Ambient temperature during operation
-25…+60 °C
-25…+55 °C according to cURus
0…+55 °C according to ATEX
     Ambient temperature during storage
-40…+85 °C
     Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27;
see also Additional checks.
     EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
     Protection class
IP65, IP66, IP67 conforms to EN 60529
Mechanics
     Weight
approx. 165 g
     Installation position
variable
Approvals and conformity
     Approvals
CE, cURus
Analog inputs
The measuring range can be switched during operation. The following table shows the electrical specifications depending on the selected measuring range.
Technical data
Measuring range
-10…10 V
0…10 V
0…20 mA
4…20 mA
Input type
Differential
Input resistance
> 200 kΩ
> 200 kΩ
85 Ω typ. + diode voltage
Digital resolution
16-bit
15-bit
15-bit
15-bit
Measuring error
< 0.3 % relative to full scale value
Conversion time
approx. 100 µs
Input filter limit frequency
5 kHz
Value of the least significant bit
approx. 305 µV
approx. 305 µV
approx. 610 µA
approx. 488 µA
The analog inputs and outputs have a common analog ground potential. The analog ground potential is electrically isolated from all other ground potentials in the box.
Analog outputs
The output signal range can be switched during operation. The following table shows the electrical specifications depending on the selected output signal range.
Technical data
Output signal range
-10…10 V
0…10 V
0…20 mA
4…20 mA
Load resistor / load
> 5 kΩ
> 5 kΩ
< 500 Ω
< 500 Ω
Digital resolution
16-bit
15-bit
15-bit
15-bit
Output error
< 0.1 % (ambient temperature 0…+55 °C)
< 0.2 % (ambient temperature < 0 °C or > 55 °C)
related to the final value.
Conversion time
approx. 40 µs
approx. 305 µV
approx. 305 µV
approx. 610 µA
approx. 488 µA
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms