Standard objects and PDO mapping
Standard objects and PDO mapping 1:
EtherCAT XML Device Description
The display matches that of the CoE objects from the EtherCAT XML Device Description. We recommend downloading the latest XML file from the download area of the Beckhoff website and installing it according to installation instructions.
Standard objects and PDO mapping 2:
Parameterization via the CoE list (CAN over EtherCAT)
The EtherCAT device is parameterized via the CoE-Online tab (double-click on the respective object) or via the Process Data tab (allocation of PDOs). Please note the following general CoE notes when using/manipulating the CoE parameters:
  • Keep a startup list if components have to be replaced
  • Differentiation between online/offline dictionary, existence of current XML description
  • use “CoE reload” for resetting changes
Index 1000 Device type
Index (hex)
Meaning
Data type
Flags
Default
1000:0
Device type
Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile.
UINT32
RO
0x012C1389 (19665801dec)
Index 1008 Device name
Index (hex)
Meaning
Data type
Flags
Default
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EPP3632-0001
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
Index 100A Software version
Index (hex)
Meaning
Data type
Flags
Default
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
05
Index 1018 Identity
Index (hex)
Meaning
Data type
Flags
Default
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID of the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0x6476A909 (1685498121dec)
1018:03
Revision
Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal number, the high word (bit 16-31) refers to the device description
UINT32
RO
0x00110000 (1114112dec)
1018:04
Serial number
Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0
UINT32
RO
0x00000000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 1A00 Analog Input TxPDO-Map Status Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A00:0
Analog Input TxPDO-MapStatus Ch.1
PDO Mapping TxPDO 1
UINT8
RO
0x09 (9dec)
1A00:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (Status), entry 0x01 (Underrange))
UINT32
RO
0x6000:01, 1
1A00:02
SubIndex 002
2. PDO Mapping entry (object 0x6000 (Status), entry 0x02 (Overrange))
UINT32
RO
0x6000:02, 1
1A00:03
SubIndex 003
3. PDO Mapping entry (object 0x6000 (Status), entry 0x03 (Limit 1))
UINT32
RO
0x6000:03, 2
1A00:04
SubIndex 004
4. PDO Mapping entry (object 0x6000 (Status), entry 0x05 (Limit 2))
UINT32
RO
0x6000:05, 2
1A00:05
SubIndex 005
5. PDO Mapping entry (object 0x6000 (Status), entry 0x07 (Error))
UINT32
RO
0x6000:07, 1
1A00:06
SubIndex 006
6. PDO Mapping entry (6 bits align)
UINT32
RO
0x0000:00, 6
1A00:07
SubIndex 007
7. PDO Mapping entry (object 0x6000 (Status), entry 0x0E (Sync error))
UINT32
RO
0x6000:0E, 1
1A00:08
SubIndex 008
8. PDO Mapping entry (object 0x6000 (Status), entry 0x0F (TxPDO State))
UINT32
RO
0x6000:0F, 1
1A00:09
SubIndex 009
9. PDO Mapping entry (object 0x6000 (Status), entry 0x10 (TxPDO Toggle))
UINT32
RO
0x6000:10, 1
Index 1A01 Analog Input TxPDO-MapSamples 1 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A01:0
PDO Mapping TxPDO 2
UINT8
RO
0x01 (1dec)
1A01:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x01)
UINT32
RO
0x6001:01, 16
Index 1A02 Analog Input TxPDO-MapSamples 2 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A02:0
PDO Mapping TxPDO 3
UINT8
RO
0x01 (1dec)
1A02:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x02 ())
UINT32
RO
0x6001:02, 16
Index 1A03 Analog Input TxPDO-MapSamples 3 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A03:0
PDO Mapping TxPDO 4
UINT8
RO
0x01 (1dec)
1A03:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x03 ())
UINT32
RO
0x6001:03, 16
Index 1A04 Analog Input TxPDO-MapSamples 4 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A04:0
PDO Mapping TxPDO 5
UINT8
RO
0x01 (1dec)
1A04:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x04 ())
UINT32
RO
0x6001:04, 16
Index 1A05 Analog Input TxPDO-MapSamples 5 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A05:0
PDO Mapping TxPDO 6
UINT8
RO
0x01 (1dec)
1A05:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x05 ())))
UINT32
RO
0x6001:05, 16
Index 1A06 Analog Input TxPDO-MapSamples 6 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A06:0
PDO Mapping TxPDO 7
UINT8
RO
0x01 (1dec)
1A06:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x06 ())
UINT32
RO
0x6001:06, 16
Index 1A07 Analog Input TxPDO-MapSamples 7 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A07:0
PDO Mapping TxPDO 8
UINT8
RO
0x01 (1dec)
1A07:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x07 ())
UINT32
RO
0x6001:07, 16
Index 1A08 Analog Input TxPDO-MapSamples 8 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A08:0
PDO Mapping TxPDO 9
UINT8
RO
0x01 (1dec)
1A08:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x08 ())
UINT32
RO
0x6001:08, 16
Index 1A09 Analog Input TxPDO-MapSamples 9 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A09:0
PDO Mapping TxPDO 10
UINT8
RO
0x01 (1dec)
1A09:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x09 ())
UINT32
RO
0x6001:09, 16
Index 1A0A Analog Input TxPDO-MapSamples 10 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A0A:0
PDO Mapping TxPDO 11
UINT8
RO
0x01 (1dec)
1A0A:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0A ())
UINT32
RO
0x6001:0A, 16
Index 1A0B Analog Input TxPDO-MapSamples 11 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A0B:0
PDO Mapping TxPDO 12
UINT8
RO
0x01 (1dec)
1A0B:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0B ())
UINT32
RO
0x6001:0B, 16
Index 1A0C Analog Input TxPDO-MapSamples 12 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A0C:0
PDO Mapping TxPDO 13
UINT8
RO
0x01 (1dec)
1A0C:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0C ())
UINT32
RO
0x6001:0C, 16
Index 1A0D Analog Input TxPDO-MapSamples 13 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A0D:0
PDO Mapping TxPDO 14
UINT8
RO
0x01 (1dec)
1A0D:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0D ())
UINT32
RO
0x6001:0D, 16
Index 1A0E Analog Input TxPDO-MapSamples 14 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A0E:0
PDO Mapping TxPDO 15
UINT8
RO
0x01 (1dec)
1A0E:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0E ())
UINT32
RO
0x6001:0E, 16
Index 1A0F Analog Input TxPDO-MapSamples 15 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A0F:0
PDO Mapping TxPDO 16
UINT8
RO
0x01 (1dec)
1A0F:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x0F ())
UINT32
RO
0x6001:0F, 16
Index 1A10 Analog Input TxPDO-MapSamples 16 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A10:0
PDO Mapping TxPDO 17
UINT8
RO
0x01 (1dec)
1A10:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x10 ())
UINT32
RO
0x6001:10, 16
Index 1A11 Analog Input TxPDO-MapSamples 17 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A11:0
PDO Mapping TxPDO 18
UINT8
RO
0x01 (1dec)
1A11:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x11 ())
UINT32
RO
0x6001:11, 16
Index 1A12 Analog Input TxPDO-MapSamples 18 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A12:0
PDO Mapping TxPDO 19
UINT8
RO
0x01 (1dec)
1A12:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x12 ())
UINT32
RO
0x6001:12, 16
Index 1A13 Analog Input TxPDO-MapSamples 19 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A13:0
PDO Mapping TxPDO 20
UINT8
RO
0x01 (1dec)
1A13:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x13 ())
UINT32
RO
0x6001:13, 16
Index 1A14 Analog Input TxPDO-MapSamples 20 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A14:0
PDO Mapping TxPDO 21
UINT8
RO
0x01 (1dec)
1A14:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x14 ())
UINT32
RO
0x6001:14, 16
Index 1A15 Analog Input TxPDO-MapSamples 21 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A15:0
PDO Mapping TxPDO 22
UINT8
RO
0x01 (1dec)
1A15:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x15 ())
UINT32
RO
0x6001:15, 16
Index 1A16 Analog Input TxPDO-MapSamples 22 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A16:0
PDO Mapping TxPDO 23
UINT8
RO
0x01 (1dec)
1A16:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x16 ())
UINT32
RO
0x6001:16, 16
Index 1A17 Analog Input TxPDO-MapSamples 23 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A17:0
PDO Mapping TxPDO 24
UINT8
RO
0x01 (1dec)
1A17:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x17 ())
UINT32
RO
0x6001:17, 16
Index 1A18 Analog Input TxPDO-MapSamples 24 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A18:0
PDO Mapping TxPDO 25
UINT8
RO
0x01 (1dec)
1A18:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x18 ())
UINT32
RO
0x6001:18, 16
Index 1A19 Analog Input TxPDO-MapSamples 25 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A19:0
PDO Mapping TxPDO 26
UINT8
RO
0x01 (1dec)
1A19:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x19 ())
UINT32
RO
0x6001:19, 16
Index 1A1A Analog Input TxPDO-MapSamples 26 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A1A:0
PDO Mapping TxPDO 27
UINT8
RO
0x01 (1dec)
1A1A:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1A ())
UINT32
RO
0x6001:1A, 16
Index 1A1B Analog Input TxPDO-MapSamples 27 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A1B:0
PDO Mapping TxPDO 28
UINT8
RO
0x01 (1dec)
1A1B:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1B ())
UINT32
RO
0x6001:1B, 16
Index 1A1C Analog Input TxPDO-MapSamples 28 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A1C:0
PDO Mapping TxPDO 29
UINT8
RO
0x01 (1dec)
1A1C:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1C ())
UINT32
RO
0x6001:1C, 16
Index 1A1D Analog Input TxPDO-MapSamples 29 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A1D:0
PDO Mapping TxPDO 30
UINT8
RO
0x01 (1dec)
1A1D:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1D ())
UINT32
RO
0x6001:1D, 16
Index 1A1E Analog Input TxPDO-MapSamples 30 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A1E:0
PDO Mapping TxPDO 31
UINT8
RO
0x01 (1dec)
1A1E:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1E ())
UINT32
RO
0x6001:1E, 16
Index 1A1F Analog Input TxPDO-MapSamples 31 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A1F:0
PDO Mapping TxPDO 32
UINT8
RO
0x01 (1dec)
1A1F:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x1F ())
UINT32
RO
0x6001:1F, 16
Index 1A20 Analog Input TxPDO-MapSamples 32 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A20:0
PDO Mapping TxPDO 33
UINT8
RO
0x01 (1dec)
1A20:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x20 ())
UINT32
RO
0x6001:20, 16
Index 1A21 Analog Input TxPDO-MapSamples 33 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A21:0
PDO Mapping TxPDO 34
UINT8
RO
0x01 (1dec)
1A21:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x21 ())
UINT32
RO
0x6001:21, 16
Index 1A22 Analog Input TxPDO-MapSamples 34 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A22:0
PDO Mapping TxPDO 35
UINT8
RO
0x01 (1dec)
1A22:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x22 ())
UINT32
RO
0x6001:22, 16
Index 1A23 Analog Input TxPDO-MapSamples 35 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A23:0
PDO Mapping TxPDO 36
UINT8
RO
0x01 (1dec)
1A23:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x23 ())
UINT32
RO
0x6001:23, 16
Index 1A24 Analog Input TxPDO-MapSamples 36 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A24:0
PDO Mapping TxPDO 37
UINT8
RO
0x01 (1dec)
1A24:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x24 ())
UINT32
RO
0x6001:24, 16
Index 1A25 Analog Input TxPDO-MapSamples 37 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A25:0
PDO Mapping TxPDO 38
UINT8
RO
0x01 (1dec)
1A25:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x25 ())
UINT32
RO
0x6001:25, 16
Index 1A26 Analog Input TxPDO-MapSamples 38 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A26:0
PDO Mapping TxPDO 39
UINT8
RO
0x01 (1dec)
1A26:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x26 ())
UINT32
RO
0x6001:26, 16
Index 1A27 Analog Input TxPDO-MapSamples 39 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A27:0
PDO Mapping TxPDO 40
UINT8
RO
0x01 (1dec)
1A27:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x27 ())
UINT32
RO
0x6001:27, 16
Index 1A28 Analog Input TxPDO-MapSamples 40 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A28:0
PDO Mapping TxPDO 41
UINT8
RO
0x01 (1dec)
1A28:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x28 ())
UINT32
RO
0x6001:28, 16
Index 1A29 Analog Input TxPDO-MapSamples 41 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A29:0
PDO Mapping TxPDO 42
UINT8
RO
0x01 (1dec)
1A29:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x29 ())
UINT32
RO
0x6001:29, 16
Index 1A2A Analog Input TxPDO-MapSamples 42 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A2A:0
PDO Mapping TxPDO 43
UINT8
RO
0x01 (1dec)
1A2A:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2A ())
UINT32
RO
0x6001:2A, 16
Index 1A2B Analog Input TxPDO-MapSamples 43 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A2B:0
PDO Mapping TxPDO 44
UINT8
RO
0x01 (1dec)
1A2B:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2B ())
UINT32
RO
0x6001:2B, 16
Index 1A2C Analog Input TxPDO-MapSamples 44 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A2C:0
PDO Mapping TxPDO 45
UINT8
RO
0x01 (1dec)
1A2C:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2C ())
UINT32
RO
0x6001:2C, 16
Index 1A2D Analog Input TxPDO-MapSamples 45 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A2D:0
PDO Mapping TxPDO 46
UINT8
RO
0x01 (1dec)
1A2D:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2D ())
UINT32
RO
0x6001:2D, 16
Index 1A2E Analog Input TxPDO-MapSamples 46 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A2E:0
PDO Mapping TxPDO 47
UINT8
RO
0x01 (1dec)
1A2E:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2E ())
UINT32
RO
0x6001:2E, 16
Index 1A2F Analog Input TxPDO-MapSamples 47 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A2F:0
PDO Mapping TxPDO 48
UINT8
RO
0x01 (1dec)
1A2F:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x2F ())
UINT32
RO
0x6001:2F, 16
Index 1A30 Analog Input TxPDO-MapSamples 48 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A30:0
PDO Mapping TxPDO 49
UINT8
RO
0x01 (1dec)
1A30:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x30 ())
UINT32
RO
0x6001:30, 16
Index 1A31 Analog Input TxPDO-MapSamples 49 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A31:0
PDO Mapping TxPDO 50
UINT8
RO
0x01 (1dec)
1A31:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x31 ())
UINT32
RO
0x6001:31, 16
Index 1A32 Analog Input TxPDO-MapSamples 50 Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A32:0
PDO Mapping TxPDO 51
UINT8
RO
0x01 (1dec)
1A32:01
SubIndex 001
1. PDO Mapping entry (object 0x6001 (Samples), entry 0x32 ())
UINT32
RO
0x6001:32, 16
Index 1A40 Analog Input TxPDO-MapStatus Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A40:0
PDO Mapping TxPDO 65
UINT8
RO
0x09 (9dec)
1A40:01
SubIndex 001
1. PDO Mapping entry (object 0x6010 (Status), entry 0x01 (Underrange))
UINT32
RO
0x6010:01, 1
1A40:02
SubIndex 002
2. PDO Mapping entry (object 0x6010 (Status), entry 0x02 (Overrange))
UINT32
RO
0x6010:02, 1
1A40:03
SubIndex 003
3. PDO Mapping entry (object 0x6010 (Status), entry 0x03 (Limit 1))
UINT32
RO
0x6010:03, 2
1A40:04
SubIndex 004
4. PDO Mapping entry (object 0x6010 (Status), entry 0x05 (Limit 2))
UINT32
RO
0x6010:05, 2
1A40:05
SubIndex 005
5. PDO Mapping entry (object 0x6010 (Status), entry 0x07 (Error))
UINT32
RO
0x6010:07, 1
1A40:06
SubIndex 006
UINT32
RO
0x0000:00, 6
1A40:07
SubIndex 007
7. PDO Mapping entry (object 0x6010 (Status), entry 0x0E (Sync error))
UINT32
RO
0x6010:0E, 1
1A40:08
SubIndex 008
8. PDO Mapping entry (object 0x6010 (Status), entry 0x0F (TxPDO State))
UINT32
RO
0x6010:0F, 1
1A40:09
SubIndex 009
9. PDO Mapping entry (object 0x6010 (Status), entry 0x10 (TxPDO Toggle))
UINT32
RO
0x6010:10, 1
Index 1A41 Analog Input TxPDO-MapSamples 1 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A41:0
PDO Mapping TxPDO 66
UINT8
RO
0x01 (1dec)
1A41:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x01 ())
UINT32
RO
0x6011:01, 16
Index 1A42 Analog Input TxPDO-MapSamples 2 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A42:0
PDO Mapping TxPDO 67
UINT8
RO
0x01 (1dec)
1A42:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x02 ())
UINT32
RO
0x6011:02, 16
Index 1A43 Analog Input TxPDO-MapSamples 3 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A43:0
PDO Mapping TxPDO 68
UINT8
RO
0x01 (1dec)
1A43:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x03 ())
UINT32
RO
0x6011:03, 16
Index 1A44 Analog Input TxPDO-MapSamples 4 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A44:0
PDO Mapping TxPDO 69
UINT8
RO
0x01 (1dec)
1A44:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x04 ())
UINT32
RO
0x6011:04, 16
Index 1A45 Analog Input TxPDO-MapSamples 5 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A45:0
PDO Mapping TxPDO 70
UINT8
RO
0x01 (1dec)
1A45:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x05 ())
UINT32
RO
0x6011:05, 16
Index 1A46 Analog Input TxPDO-MapSamples 6 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A46:0
PDO Mapping TxPDO 71
UINT8
RO
0x01 (1dec)
1A46:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x06 ())
UINT32
RO
0x6011:06, 16
Index 1A47 Analog Input TxPDO-MapSamples 7 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A47:0
PDO Mapping TxPDO 72
UINT8
RO
0x01 (1dec)
1A47:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x07 ())
UINT32
RO
0x6011:07, 16
Index 1A48 Analog Input TxPDO-MapSamples 8 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A48:0
PDO Mapping TxPDO 73
UINT8
RO
0x01 (1dec)
1A48:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples),), entry 0x08 ())
UINT32
RO
0x6011:08, 16
Index 1A49 Analog Input TxPDO-MapSamples 9 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A49:0
PDO Mapping TxPDO 74
UINT8
RO
0x01 (1dec)
1A49:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x09 ())
UINT32
RO
0x6011:09, 16
Index 1A4A Analog Input TxPDO-MapSamples 10 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A4A:0
PDO Mapping TxPDO 75
UINT8
RO
0x01 (1dec)
1A4A:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0A ())
UINT32
RO
0x6011:0A, 16
Index 1A4B Analog Input TxPDO-MapSamples 11 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A4B:0
PDO Mapping TxPDO 76
UINT8
RO
0x01 (1dec)
1A4B:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0B ())
UINT32
RO
0x6011:0B, 16
Index 1A4C Analog Input TxPDO-MapSamples 12 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A4C:0
PDO Mapping TxPDO 77
UINT8
RO
0x01 (1dec)
1A4C:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0C ())
UINT32
RO
0x6011:0C, 16
Index 1A4D Analog Input TxPDO-MapSamples 13 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A4D:0
PDO Mapping TxPDO 78
UINT8
RO
0x01 (1dec)
1A4D:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0D ())
UINT32
RO
0x6011:0D, 16
Index 1A4E Analog Input TxPDO-MapSamples 14 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A4E:0
PDO Mapping TxPDO 79
UINT8
RO
0x01 (1dec)
1A4E:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0E ())
UINT32
RO
0x6011:0E, 16
Index 1A4F Analog Input TxPDO-MapSamples 15 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A4F:0
PDO Mapping TxPDO 80
UINT8
RO
0x01 (1dec)
1A4F:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x0F ())
UINT32
RO
0x6011:0F, 16
Index 1A50 Analog Input TxPDO-MapSamples 16 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A50:0
PDO Mapping TxPDO 81
UINT8
RO
0x01 (1dec)
1A50:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x10 ())
UINT32
RO
0x6011:10, 16
Index 1A51 Analog Input TxPDO-MapSamples 17 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A51:0
PDO Mapping TxPDO 82
UINT8
RO
0x01 (1dec)
1A51:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x11 ())
UINT32
RO
0x6011:11, 16
Index 1A52 Analog Input TxPDO-MapSamples 18 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A52:0
PDO Mapping TxPDO 83
UINT8
RO
0x01 (1dec)
1A52:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x12 ())
UINT32
RO
0x6011:12, 16
Index 1A53 Analog Input TxPDO-MapSamples 19 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A53:0
PDO Mapping TxPDO 84
UINT8
RO
0x01 (1dec)
1A53:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x13 ())
UINT32
RO
0x6011:13, 16
Index 1A54 Analog Input TxPDO-MapSamples 20 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A54:0
PDO Mapping TxPDO 85
UINT8
RO
0x01 (1dec)
1A54:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x14 ())
UINT32
RO
0x6011:14, 16
Index 1A55 Analog Input TxPDO-MapSamples 21 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A55:0
PDO Mapping TxPDO 86
UINT8
RO
0x01 (1dec)
1A55:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x15 ())
UINT32
RO
0x6011:15, 16
Index 1A56 Analog Input TxPDO-MapSamples 22 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A56:0
PDO Mapping TxPDO 87
UINT8
RO
0x01 (1dec)
1A56:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x16 ())
UINT32
RO
0x6011:16, 16
Index 1A57 Analog Input TxPDO-MapSamples 23 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A57:0
PDO Mapping TxPDO 88
UINT8
RO
0x01 (1dec)
1A57:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x17 ())
UINT32
RO
0x6011:17, 16
Index 1A58 Analog Input TxPDO-MapSamples 24 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A58:0
PDO Mapping TxPDO 89
UINT8
RO
0x01 (1dec)
1A58:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x18 ())
UINT32
RO
0x6011:18, 16
Index 1A59 Analog Input TxPDO-MapSamples 25 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A59:0
PDO Mapping TxPDO 90
UINT8
RO
0x01 (1dec)
1A59:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x19 ())
UINT32
RO
0x6011:19, 16
Index 1A5A Analog Input TxPDO-MapSamples 26 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A5A:0
PDO Mapping TxPDO 91
UINT8
RO
0x01 (1dec)
1A5A:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1A ())
UINT32
RO
0x6011:1A, 16
Index 1A5B Analog Input TxPDO-MapSamples 27 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A5B:0
PDO Mapping TxPDO 92
UINT8
RO
0x01 (1dec)
1A5B:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1B ())
UINT32
RO
0x6011:1B, 16
Index 1A5C Analog Input TxPDO-MapSamples 28 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A5C:0
PDO Mapping TxPDO 93
UINT8
RO
0x01 (1dec)
1A5C:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1C ())
UINT32
RO
0x6011:1C, 16
Index 1A5D Analog Input TxPDO-MapSamples 29 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A5D:0
PDO Mapping TxPDO 94
UINT8
RO
0x01 (1dec)
1A5D:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1D ())
UINT32
RO
0x6011:1D, 16
Index 1A5E Analog Input TxPDO-MapSamples 30 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A5E:0
PDO Mapping TxPDO 95
UINT8
RO
0x01 (1dec)
1A5E:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1E ())
UINT32
RO
0x6011:1E, 16
Index 1A5F Analog Input TxPDO-MapSamples 31 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A5F:0
PDO Mapping TxPDO 96
UINT8
RO
0x01 (1dec)
1A5F:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x1F ())
UINT32
RO
0x6011:1F, 16
Index 1A60 Analog Input TxPDO-MapSamples 32 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A60:0
PDO Mapping TxPDO 97
UINT8
RO
0x01 (1dec)
1A60:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x20 ())
UINT32
RO
0x6011:20, 16
Index 1A61 Analog Input TxPDO-MapSamples 33 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A61:0
PDO Mapping TxPDO 98
UINT8
RO
0x01 (1dec)
1A61:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x21 ())
UINT32
RO
0x6011:21, 16
Index 1A62 Analog Input TxPDO-MapSamples 34 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A62:0
PDO Mapping TxPDO 99
UINT8
RO
0x01 (1dec)
1A62:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x22 ())
UINT32
RO
0x6011:22, 16
Index 1A63 Analog Input TxPDO-MapSamples 35 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A63:0
PDO Mapping TxPDO 100
UINT8
RO
0x01 (1dec)
1A63:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x23 ())
UINT32
RO
0x6011:23, 16
Index 1A64 Analog Input TxPDO-MapSamples 36 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A64:0
PDO Mapping TxPDO 101
UINT8
RO
0x01 (1dec)
1A64:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x24 ())
UINT32
RO
0x6011:24, 16
Index 1A65 Analog Input TxPDO-MapSamples 37 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A65:0
PDO Mapping TxPDO 102
UINT8
RO
0x01 (1dec)
1A65:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x25 ())
UINT32
RO
0x6011:25, 16
Index 1A66 Analog Input TxPDO-MapSamples 38 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A66:0
PDO Mapping TxPDO 103
UINT8
RO
0x01 (1dec)
1A66:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x26 ())
UINT32
RO
0x6011:26, 16
Index 1A67 Analog Input TxPDO-MapSamples 39 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A67:0
PDO Mapping TxPDO 104
UINT8
RO
0x01 (1dec)
1A67:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x27 ())
UINT32
RO
0x6011:27, 16
Index 1A68 Analog Input TxPDO-MapSamples 40 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A68:0
PDO Mapping TxPDO 105
UINT8
RO
0x01 (1dec)
1A68:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x28 ())
UINT32
RO
0x6011:28, 16
Index 1A69 Analog Input TxPDO-MapSamples 41 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A69:0
PDO Mapping TxPDO 106
UINT8
RO
0x01 (1dec)
1A69:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x29 ())
UINT32
RO
0x6011:29, 16
Index 1A6A Analog Input TxPDO-MapSamples 42 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A6A:0
PDO Mapping TxPDO 107
UINT8
RO
0x01 (1dec)
1A6A:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2A ())
UINT32
RO
0x6011:2A, 16
Index 1A6B Analog Input TxPDO-MapSamples 43 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A6B:0
PDO Mapping TxPDO 108
UINT8
RO
0x01 (1dec)
1A6B:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2B ())
UINT32
RO
0x6011:2B, 16
Index 1A6C Analog Input TxPDO-MapSamples 44 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A6C:0
PDO Mapping TxPDO 109
UINT8
RO
0x01 (1dec)
1A6C:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2C ())
UINT32
RO
0x6011:2C, 16
Index 1A6D Analog Input TxPDO-MapSamples 45 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A6D:0
PDO Mapping TxPDO 110
UINT8
RO
0x01 (1dec)
1A6D:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2D ())
UINT32
RO
0x6011:2D, 16
Index 1A6E Analog Input TxPDO-MapSamples 46 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A6E:0
PDO Mapping TxPDO 111
UINT8
RO
0x01 (1dec)
1A6E:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2E ())
UINT32
RO
0x6011:2E, 16
Index 1A6F Analog Input TxPDO-MapSamples 47 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A6F:0
PDO Mapping TxPDO 112
UINT8
RO
0x01 (1dec)
1A6F:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x2F ())
UINT32
RO
0x6011:2F, 16
Index 1A70 Analog Input TxPDO-MapSamples 48 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A70:0
PDO Mapping TxPDO 113
UINT8
RO
0x01 (1dec)
1A70:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x30 ())
UINT32
RO
0x6011:30, 16
Index 1A71 Analog Input TxPDO-MapSamples 49 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A71:0
PDO Mapping TxPDO 114
UINT8
RO
0x01 (1dec)
1A71:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x31 ())
UINT32
RO
0x6011:31, 16
Index 1A72 Analog Input TxPDO-MapSamples 50 Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A72:0
PDO Mapping TxPDO 115
UINT8
RO
0x01 (1dec)
1A72:01
SubIndex 001
1. PDO Mapping entry (object 0x6011 (Samples), entry 0x32 ())
UINT32
RO
0x6011:32, 16
Index 1A80 Analog Input Timestamp TxPDO-Map NextSync1Time
Index (hex)
Meaning
Data type
Flags
Default
1A80:0
PDO Mapping TxPDO 129
UINT8
RO
0x01 (1dec)
1A80:01
SubIndex 001
1. PDO Mapping entry (object 0x6020 (NextSync1Time), entry 0x01 ())
UINT32
RO
0x6020:01, 64
Index 1A81 Analog Input Timestamp TxPDO-Map Sample Count
Index (hex)
Meaning
Data type
Flags
Default
1A81:0
PDO Mapping TxPDO 130
UINT8
RO
0x01 (1dec)
1A81:01
SubIndex 001
1. PDO Mapping entry (object 0x6021 (SampleCount), entry 0x01 (Sample Count))
UINT32
RO
0x6021:01, 16
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default
1C00:0
Sync manager type
Using the sync managers
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync-Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync-Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync-Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync-Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 1C12 RxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RW
0x00 (0dec)
Index 1C13 TxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x06 (6dec)
1C13:01
Subindex 001
1. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A00 (6656dec)
1C13:02
Subindex 002
2. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A01 (6657dec)
1C13:03
Subindex 003
3. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A40 (6720dec)
1C13:04
Subindex 004
4. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A41 (6721dec)
1C13:05
Subindex 005
5. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A80 (6784dec)
1C13:06
Subindex 006
6. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A81 (6785dec)
1C13:07
Subindex 007
7. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x0000 (0dec)
1C13:69
Subindex 105
105. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x0000 (0dec)
Index 1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default
1C33:0
SM input parameter
Synchronization parameters for the inputs
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
Current synchronization mode:
  • 0: Free Run
  • 1: Synchron with SM 3 Event (no outputs available)
  • 2: DC - Synchron with SYNC0 Event
  • 3: DC - Synchron with SYNC1 Event
  • 34: Synchron with SM 2 Event (outputs available)
UINT16
RW
0x0022 (34dec)
1C33:02
Cycle time
as 0x1C32:02
UINT32
RW
0x000F4240 (1000000dec)
1C33:03
Shift time
Time between SYNC0 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:04
Sync modes supported
Supported synchronization modes:
  • Bit 0: free run is supported
  • Bit 1: Synchronous with SM 2 Event is supported (outputs available)
  • Bit 1: Synchronous with SM 3 Event is supported (no outputs available)
  • Bit 2-3 = 01: DC mode is supported
  • Bit 4-5 = 01: input shift through local event (outputs available)
  • Bit 4-5 = 10: input shift with SYNC1 event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C32:08 or 0x1C33:08)
UINT16
RO
0x0C06 (3078dec)
1C33:05
Minimum cycle time
as 0x1C32:05
UINT32
RO
0x00002710 (10000dec)
1C33:06
Calc and copy time
Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:07
Minimum delay time
UINT32
RO
0x00000000 (0dec)
1C33:08
Command
as 0x1C32:08
UINT16
RW
0x0000 (0dec)
1C33:09
Maximum delay time
Time between SYNC1 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:0B
SM event missed counter
as 0x1C32:11
UINT16
RO
0x0000 (0dec)
1C33:0C
Cycle exceeded counter
as 0x1C32:12
UINT16
RO
0x0000 (0dec)
1C33:0D
Shift too short counter
as 0x1C32:13
UINT16
RO
0x0000 (0dec)
1C33:20
Sync error
as 0x1C32:32
BOOLEAN
RO
0x00 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
F000:0
General information for the modular device profile
UINT8
RO
0x02 (2dec)
F000:01
Module index distance
Index distance of the objects of the individual channels
UINT16
RO
0x0010 (16dec)
F000:02
Maximum number of modules
Number of channels
UINT16
RO
0x0003 (3dec)
Index F008 Code word
Index (hex)
Meaning
Data type
Flags
Default
F008:0
Code word
reserved
UINT32
RW
0x00000000 (0dec)
Index F010 Module list
Index (hex)
Meaning
Data type
Flags
Default
F010:0
Module list
Maximum subindex
UINT8
RW
0x03 (3dec)
F010:01
SubIndex 001
Profile AI
UINT32
RW
0x0000012C (300dec)
F010:02
SubIndex 002
Profile AI
UINT32
RW
0x0000012C (300dec)
F010:03
SubIndex 003
Profile AI
UINT32
RW
0x0000012C (300dec)
