CoE parameters
CoE parameters 1:
Parameterization
You can parameterize the box via the "CoE - Online" tab in TwinCAT.
CoE parameters 2:
EtherCAT XML Device Description
The presentation matches that of the EtherCAT XML Device Description.
Recommendation: download the latest XML file from https://www.beckhoff.com/ and install it according to the installation instructions.
Index 1011 Restore default parameters
Index (hex)
Meaning
Data type
Flags
Default
1011:0
Restore the default settings in the EtherCAT slave
UINT8
RO
0x01 (1dec)
1011:01
SubIndex 001
If this object is set to "0x64616F6C" ("Set Value Dialog") all terminal/box-specific objects are reset to their delivery state.
UINT32
RW
0x00000000 (0dec)
Index 8000 RMB Settings
Index (hex)
Meaning
Data type
Flags
Default
8000:0
RMB Settings
Max. subindex
UINT8
RO
0x32 (50dec)
8000:01
Mode0 enable filter
0: No filters active. The box operates cycle-synchronously
1: The filter settings selected in subindex 0x8000:11 or 0x8000:12 are active.
BOOLEAN
RW
0x01 (1dec)
8000:02
Mode1 enable filter
BOOLEAN
RW
0x01 (1dec)
8000:03
Mode0 enable averager
Activate hardware mean value filter
BOOLEAN
RW
0x01 (1dec)
8000:04
Mode1 enable averager
BOOLEAN
RW
0x01 (1dec)
8000:05
Symmetric reference potential
Activate symmetric measurement
BOOLEAN
RW
0x01 (1dec)
8000:11
Mode0 filter settings
0: FIR 50 Hz
1: FIR 60 Hz
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
10: Dynamic IIR
11: PDO Filter frequency
see Filter
UINT16
RW
0x0000 (0dec)
8000:12
Mode1 filter settings
UINT16
RW
0x0000 (0dec)
8000:13
Dynamic filter change time
Sampling rate for dynamic filter switching.
Scaling in 0.01 ms (100 = 1 s)
(only if the filters are active and "dynamic IIR" is selected as filter)
UINT16
RW
0x000A (10dec)
8000:14
Dynamic filter delta
Limit value  for dynamic filter switching.
REAL32
RW
0x41A00000 (1101004800dec) = 20.0
8000:21
Gain
Scaling factor
REAL32
RW
0x3F800000 (1065353216dec)  = 1.0
8000:22
Tara
Process data value offset
REAL32
RW
0x00000000 (0dec) = 0.0
8000:23
Rated output
Nominal characteristic value of the sensor element in mV/V
REAL32
RW
0x40000000 (1073741824dec)  = 2.0
Index (hex)
Meaning
Data type
Flags
Default
8000:24
Nominal load
Nominal load of the force transducer/load cell/etc. (e.g. in kg or N or ..)
REAL32
RW
0x40A00000 (1084227584dec) = 5.0
8000:25
Zero balance
Zero point offset in mV/V
REAL32
RW
8000:26
Gravity of earth
Current acceleration of gravity (default 9.806650)
REAL32
RW
0x411CE80A (1092413450dec) = 9.806650
8000:27
Scale factor
This factor can be used to re-scale the process data. In order to change the display from kg to g, for example, the factor 1000 can be entered here.
REAL32
RW
0x447A0000 (1148846080dec) = 1000.0
8000:28
Reference load
Reference weight for manual calibration
REAL32
RW
8000:29
Steady state window
Time constant for the "Steady state" bit (used for idle recognition)
UINT16
RW
0x03E8 (1000dec)
8000:2A
Steady state tolerance
Tolerance window for the "Steady state" bit
UINT32
RW
0x00000005 (5dec)
8000:31
Calibration interval
Calibration interval for automatic calibration of the terminal/box.
The unit is 100 ms.
The smallest possible value is 5 (500 ms). A value of 0 deactivates automatic self-calibration. This is also possible via the process data bit "Disable calibration".
UINT16
RW
0x0708 (1800dec)
8000:32
Test interval
This register contains the test interval for the cyclic self-test of the terminal/box. This interval is always a multiple (default: 10dec) of the calibration interval (0x8000:31). The test interval when the equipment leaves the factory is therefore 10 x 180 s = 1800 s.
The process data bit "Disable calibration" can be used to deactivate the self-test.
UINT16
RW
0x000A (10dec)
Index 8010, 8020 AI Settings
Index (hex)
Meaning
Data type
Flags
Default
80n0:0
AI Settings
Max. subindex
UINT8
RO
0x18 (24dec)
80n0:01
Enable user scale
User scale is enabled, if bit is set
BOOLEAN
RW
0x00 (0dec)
80n0:06
Enable filter
Activates filter
BOOLEAN
RW
0x01 (1dec)
80n0:0A
Enable user calibration
User calibration is enabled, if bit is set
BOOLEAN
RW
0x00 (0dec)
80n0:0B
Enable vendor calibration
Vendor calibration is enabled, if bit is set
BOOLEAN
RW
0x01 (1dec)
80n0:11
User scale offset
User scale offset
INT32
RW
0x00000000 (0dec)
80n0:12
User scale gain
User scale gain
The gain is represented in fixed-point format, with the factor 2-16.
A value of 1 for the gain factor therefore corresponds to 65535dec (0x00010000hex) and is limited to 0x7FFFF.
INT32
RW
0x00010000 (65536dec)
80n0:15
Filter settings
This object defines the digital filter settings, if it is activated with index 0x80n0:06 .
The possible settings are numbered consecutively
0: 50 Hz FIR
1: 60 Hz FIR
2: IIR 1
3: IIR 2
4: IIR 3
5: IIR 4
6: IIR 5
7: IIR 6
8: IIR 7
9: IIR 8
UINT16
RW
0x0000 (0dec)
80n0:17
User calibration offset
INT32
RW
0x00000000 (0dec)
80n0:18
User calibration gain
INT16
RW
0x4000 (16384dec)
Command object, Index FB00 RMB Command
Index (hex)
Meaning
Data type
Flags
Default
FB00:0
RMB Command
Max. subindex
UINT8
RO
0x03 (3dec)
FB00:01
Request
Via the request object, commands can be sent to the terminal/box
 Command:
- 0x0101: Zero adjustment
- 0x0102: Calibration
- 0x0001 Tara setting
- 0x0002 Tara setting (Data are saved into the EEPROM)
see commands
OCTET-STRING[2]
RW
{0}
FB00:02
Status
State of the current executed command
0: Command executed without errors
255: Execution of command
UINT8
RO
0x00 (0dec)
FB00:03
Response
Optional return value of the command
OCTET-STRING[4]
RO
{0}
Input data, Index 6000 RMB Inputs
Index (hex)
Meaning
Data type
Flags
Default
6000:0
RMB Inputs
Max. subindex
UINT8
RO
0x13 (19dec)
6000:02
Overrange
The measuring value has reached its terminal/box value
BOOLEAN
RO
0x00 (0dec)
6000:04
Data invalid
The indicated process data are not valid, e.g. during calibration
BOOLEAN
RO
0x00 (0dec)
6000:07
Error
An error has occurred
BOOLEAN
RO
0x00 (0dec)
6000:08
Calibration in progress
Calibration in progress. The process data indicate the last valid measuring value
BOOLEAN
RO
0x00 (0dec)
6000:09
Steady state
BOOLEAN
RO
0x00 (0dec)
6000:0E
Sync error
TRUE: In the last cycle the synchronization was not correct (only in DC-Mode)
BOOLEAN
RO
0x00 (0dec)
6000:10
TxPDO Toggle
The TxPDO Toggle is toggled by the slave, if the data of the corresponding PDO was updated.
BOOLEAN
RO
0x00 (0dec)
6000:11
Value
Measuring value as 32 Bit SIGNED INTEGER
INT32
RO
0x61746144 (1635017028dec)
6000:12
Value (Real)
Measuring value as REAL
REAL32
RO
0x00000000 (0dec)
6000:13
Timestamp
Timestamp of current measuring value (only in DC-Mode)
UINT64
RO
Input data Index 6010, 6020 AI Inputs
Index (hex)
Meaning
Data type
Flags
Default
60n0:0
AI Inputs
Max. subindex
UINT8
RO
0x11 (17dec)
60n0:01
Underrange
Value falls below the measuring range
BOOLEAN
RO
0x00 (0dec)
60n0:02
Overrange
Measurement range is exceeded.
BOOLEAN
RO
0x00 (0dec)
60n0:07
Error
An error has occurred, e.g.:
- Over- / underrange Udif
- Over- / underrange Uref
- the external Uref is too low (between-1 V and +1 V)
- Data invalid
BOOLEAN
RO
0x00 (0dec)
60n0:10
TxPDO Toggle
BOOLEAN
RO
0x00 (0dec)
60n0:11
Value
32 Bit measuring value
INT32
RO
0x00000000 (0dec)
Output data, Index 7000 RMB Outputs
Index (hex)
Meaning
Data type
Flags
Default
7000:0
RMB Outputs
Max. subindex
UINT8
RO
0x05 (5dec)
7000:01
Start calibration
The calibration can be started manually with a rising edge.
Therefore, an automatic start of the calibration at an inappropriate point of time can be prevented.
BOOLEAN
RO
0x00 (0dec)
7000:02
Disable calibration
0: The automatic calibration is active
1: The automatic calibration is inactive
BOOLEAN
RO
0x00 (0dec)
7000:03
Input freeze
The process data and the digital filter will be frozen
BOOLEAN
RO
0x00 (0dec)
7000:04
Sample mode
Selection of the sampling mode:
0: 10.5 kHz High precision
1: 105 kHz Low latency
BOOLEAN
RO
0x00 (0dec)
7000:05
Tara
The process data can be set to zero with a rising edge.
The tara value is not stored in the EEPROM and is lost after a reset of the terminal/box
BOOLEAN
RO
0x00 (0dec)
7000:11
Filter frequency
Filter frequency of the variable PDO filter in 0.1 Hz, see filter
Wertebereich:
value range: 1 ... 2000 (equates to 0,1 ... 200 Hz)
From a value 0 or >2000, the filter behaves like a 50 Hz FIR filter
UINT16
RO
0x00 (0dec)
Information-/diagnostic data, Index 801E, 802E AI Internal data
Index (hex)
Meaning
Data type
Flags
Default
801E:0
AI Internal data
Max. subindex
UINT8
RO
0x01 (1dec)
801E:01
ADC raw value 1
ADC raw value
INT32
RO
0x00000000 (0dec)
Index 9000 RMB Info data
Index (hex)
Meaning
Data type
Flags
Default
9000:0
RMB Info data
Max. subindex
UINT8
RO
0x11 (17dec)
9000:11
mV/V
Current mV/V value
REAL32
RO
0x00000000 (0dec)
Index A000 RMB Diag data
Index (hex)
Meaning
Data type
Flags
Default
A000:0
RMB Diag data
Max. subindex
UINT8
RO
0x18 (24dec)
A000:11
No internal referecnce supply
No internal reference voltage at ADC input (URef channel)
BOOLEAN
RO
0x00 (0dec)
A000:12
No internal referecnce bridge
No internal reference voltage at ADC input  (UDif channel
BOOLEAN
RO
0x00 (0dec)
A000:13
No external reference supply
The external reference voltage is below ±1 V
BOOLEAN
RO
0x00 (0dec)
A000:15
Overrange bridge
Overranged measuring value in the bridge section
BOOLEAN
RO
0x00 (0dec)
A000:16
Underrange bridge
Underranged measuring value in the bridge section
BOOLEAN
RO
0x00 (0dec)
A000:17
Overrange supply
Overranged measuring value of the reference voltage
BOOLEAN
RO
0x00 (0dec)
A000:18
Underrange supply
Underranged measuring value of the reference voltage
BOOLEAN
RO
0x00 (0dec)
Vendor configuration data, Index 801F, 802F AI Vendor data
Index (hex)
Meaning
Data type
Flags
Default
801F:0
AI Vendor data
Max. subindex
UINT8
RO
0x02 (2dec)
801F:01
Calibration offset
Offset (vendor calibration))
INT32
RW
0x01E10000 (31522816dec)
801F:02
Calibration gain
Gain (vendor calibration))
INT16
RW
0x4000 (16384dec)
Standard objects, Index 1000 Device type
Index (hex)
Meaning
Data type
Flags
Default
1000:0
Device type
Device type of the EtherCAT slave: The low word contains the CoE profile used (5001). The high word contains the module profile according to the modular device profile.
UINT32
RO
0x01681389 (23597961dec)
Index 1008 Device name
Index (hex)
Meaning
Data type
Flags
Default
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EPP3356-0022
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
00
Index 100A Software version
Index (hex)
Meaning
Data type
Flags
Default
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
01
Index 1018 Identity
Index (hex)
Meaning
Data type
Flags
Default
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID of the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0x647697C9 (1685493705dec)
1018:03
Revision
Revision number of the EtherCAT slave; the low word (bit 0-15) indicates the special terminal/box number, the high word (bit 16-31) refers to the device description
UINT32
RO
0x00100000 (1048576dec)
1018:04
Serial number
Serial number of the EtherCAT slave; the low byte (bit 0-7) of the low word contains the year of production, the high byte (bit 8-15) of the low word contains the week of production, the high word (bit 16-31) is 0
UINT32
RO
0x00000000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 1600 RMB RxPDO-Map Control
Index (hex)
Meaning
Data type
Flags
Default
1600:0
PDO Mapping RxPDO-Map control
UINT8
RO
0x07 (7dec)
1600:01
Subindex 001
1. PDO Mapping entry (object 0x7000 (RMB outputs), entry 0x01 (Start calibration))
OCTET-STRING[10]
RO
0x7000:01, 1
1600:02
Subindex 002
2. PDO Mapping entry (object 0x7000 (RMB outputs), entry 0x02 (Disable calibration))
OCTET-STRING[10]
RO
0x7000:02, 1
1600:03
Subindex 003
3. PDO Mapping entry (object 0x7000 (RMB outputs), entry 0x03 (Input freeze))
OCTET-STRING[10]
RO
0x7000:03, 1
1600:04
Subindex 004
4. PDO Mapping entry (1 bits align)
OCTET-STRING[10]
RO
0x0000:00, 1
1600:05
Subindex 005
5. PDO Mapping entry (object 0x7000 (RMB outputs), entry 0x05 (Tara))
OCTET-STRING[10]
RO
0x7000:05, 1
1600:06
Subindex 006
6. PDO Mapping entry (3 bits align)
OCTET-STRING[10]
RO
0x0000:00, 3
1600:07
Subindex 007
7. PDO Mapping entry (8 bits align)
OCTET-STRING[10]
RO
0x0000:00, 8
Index 1601 RMB RxPDO-Map-Filter frequency
Index (hex)
Meaning
Data type
Flags
Default
1601:0
RMB RxPDO-Map Filter frequency
PDO Mapping RxPDO-Map Filter frequency
UINT8
RO
0x01 (1dec)
1601:01
Subindex 001
1. PDO Mapping entry (object 0x7000 (RMB ouputs), entry 0x11 (Start calibration))
OCTET-STRING[10]
RO
0x7000:11, 16
Index 1800 RMB TxPDO-Par Status
Index (hex)
Meaning
Data type
Flags
Default
1800:0
PDO Parameter TxPDO 1
UINT8
RO
0x06 (6dec)
1800:06
Exclude TxPDOs
This entry contains the TxPDOs (Index of the TxPDO Mapping objects) which shall not be transmitted with TxPDO 1
OCTET-STRING[10]
RO
04 1A 05 1A 06 1A 07 1A 00 00
Index 1801 RMB TxPDO-Par Value (INT 32)
Index (hex)
Meaning
Data type
Flags
Default
1801:0
RMB TxPDO-Par Value (INT32)
PDO Parameter TxPDO 2
UINT8
RO
0x06 (6dec)
1801:06
Exclude TxPDOs
This entry contains the TxPDOs (Index of the TxPDO Mapping objects) which shall not be transmitted with TxPDO 2
OCTET-STRING[10]
RO
02 1A 04 1A 05 1A 06 1A 07 1A
Index 1802 RMB TxPDO-Par Value (Real)
Index (hex)
Meaning
Data type
Flags
Default
1802:0
PDO Parameter TxPDO 3
UINT8
RO
0x06 (6dec)
1802:06
Exclude TxPDOs
This entry contains the TxPDOs (Index of the TxPDO Mapping objects) which shall not be transmitted with TxPDO 3
OCTET-STRING[10]
RO
01 1A 04 1A 05 1A 06 1A 07 1A
Index 1803 RMB TxPDO-Par Timestamp
Index (hex)
Meaning
Data type
Flags
Default
1803:0
PDO Parameter TxPDO 4
UINT8
RO
0x06 (6dec)
1803:06
Exclude TxPDOs
This entry contains the TxPDOs (Index of the TxPDO Mapping objects) which shall not be transmitted with TxPDO 4
OCTET-STRING[10]
RO
Index 1804 AI TxPDO-Par Standard Ch. 1
Index (hex)
Meaning
Data type
Flags
Default
1804:0
AI TxPDO-Par Standard Ch.1
PDO Parameter TxPDO 5
UINT8
RO
0x06 (6dec)
1804:06
Exclude TxPDOs
This entry contains the TxPDOs (Index of the TxPDO Mapping objects) which shall not be transmitted with TxPDO 5
OCTET-STRING[10]
RO
05 1A 00 1A 01 1A 02 1A 03 1A
Index 1805 AI TxPDO-Par Compact Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1805:0
PDO Parameter TxPDO 6
UINT8
RO
0x06 (6dec)
1805:06
Exclude TxPDOs
This entry contains the TxPDOs (Index of the TxPDO Mapping objects) which shall not be transmitted with TxPDO 6
OCTET-STRING[10]
RO
04 1A 00 1A 01 1A 02 1A 03 1A
Index 1806 AI TxPDO-Par Standard Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1806:0
PDO Parameter TxPDO 7
UINT8
RO
0x06 (6dec)
1806:06
Exclude TxPDOs
This entry contains the TxPDOs (Index of the TxPDO Mapping objects) which shall not be transmitted with TxPDO 7
OCTET-STRING[10]
RO
07 1A 00 1A 01 1A 02 1A 03 1A
Index 1807 AI TxPDO-Par Compact Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1807:0
PDO Parameter TxPDO 8
UINT8
RO
0x06 (6dec)
1807:06
Exclude TxPDOs
This entry contains the TxPDOs (Index of the TxPDO Mapping objects) which shall not be transmitted with TxPDO 8
OCTET-STRING[10]
RO
06 1A 00 1A 01 1A 02 1A 03 1A
Index 1A00 RMB TxPDO-Map Status
Index (hex)
Meaning
Data type
Flags
Default
1A00:0
PDO Mapping RxPDO-Map Status
UINT8
RO
0x0C (12dec)
1A00:01
Subindex 001
1. PDO Mapping entry (1 bits align)
OCTET-STRING[10]
RO
0x0000:00, 1
1A00:02
Subindex 002
2. PDO Mapping entry (object 0x6000 (RMB inputs), entry 0x02 (Overrange))
OCTET-STRING[10]
RO
0x6000:02, 1
1A00:03
Subindex 003
3. PDO Mapping entry (1 bits align)
OCTET-STRING[10]
RO
0x0000:00, 1
1A00:04
Subindex 004
4. PDO Mapping entry (object 0x6000 (RMB inputs), entry 0x04 (Data invalid))
OCTET-STRING[10]
RO
0x6000:04, 1
1A00:05
Subindex 005
5. PDO Mapping entry (2 bits align)
OCTET-STRING[10]
RO
0x0000:00, 2
1A00:06
Subindex 006
6. PDO Mapping entry (object 0x6000 (RMB inputs), entry 0x07 (Error))
OCTET-STRING[10]
RO
0x6000:07, 1
1A00:07
Subindex 007
7. PDO Mapping entry (object 0x6000 (RMB inputs), entry 0x08 (Calibration in progress))
OCTET-STRING[10]
RO
0x6000:08, 1
1A00:08
Subindex 008
8. PDO Mapping entry (object 0x6000 (RMB inputs), entry 0x09 (Steady state))
OCTET-STRING[10]
RO
0x6000:09, 1
1A00:09
Subindex 009
9. PDO Mapping entry (4 bits align)
OCTET-STRING[10]
RO
0x0000:00, 4
1A00:0A
Subindex 010
10. PDO Mapping entry (object 0x6000 (RMB inputs), entry 0x0E (Sync error))
OCTET-STRING[10]
RO
0x6000:0E, 1
1A00:0B
Subindex 011
11. PDO Mapping entry (1 bits align)
OCTET-STRING[10]
RO
0x0000:00, 1
1A00:0C
Subindex 012
12. PDO Mapping entry (object 0x6000 (RMB inputs), entry 0x10 (TxPDO Toggle))
OCTET-STRING[10]
RO
0x6000:10, 1
Index 1A01 RMB TxPDO-Map Value (INT32)
Index (hex)
Meaning
Data type
Flags
Default
1A01:0
PDO Mapping Value (INT32)
UINT8
RW
0x01 (1dec)
1A01:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (RMB inputs), entry 0x11 (Value))
UINT32
RW
0x6000:11, 32
Index 1A02 RMB TxPDO-Map Value (Real)
Index (hex)
Meaning
Data type
Flags
Default
1A02:0
RMB TxPDO-Map Value (real)
PDO Mapping Value (real)
UINT8
RW
0x01 (1dec)
1A02:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (RMB inputs), entry 0x12 (Value (real)))
UINT32
RW
0x6000:12, 32
Index 1A03 RMB TxPDO-Map Timestamp
Index (hex)
Meaning
Data type
Flags
Default
1A03:0
PDO Mapping Value Timestamp
UINT8
RW
0x01 (1dec)
1A03:01
SubIndex 001
1. PDO Mapping entry (object 0x0000, entry 0x00)
UINT64
RW
0x0000:00, 64
Index 1A04 AI TxPDO-Map Standard Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A04:0
AI supply TxPDO-Map Standard Ch. 1
PDO Mapping TxPDO  Standard Ch. 1
UINT8
RW
0x07 (7dec)
1A04:01
SubIndex 001
1. PDO Mapping entry (object 0x6010 (AI supply Inputs), entry 0x01 (Underrange))
UINT32
RW
0x6010:01, 1
1A04:02
SubIndex 002
2. PDO Mapping entry (object 0x6010 (AI supply Inputs), entry 0x02 (Overrange))
UINT32
RW
0x6010:02, 1
1A04:03
SubIndex 003
3. PDO Mapping entry (4 bits align)
UINT32
RW
0x0000:00, 4
1A04:04
SubIndex 004
4. PDO Mapping entry (object 0x6010 (AI supply Inputs), entry 0x04 (Error))
UINT32
RW
0x6010:07, 1
1A04:05
SubIndex 005
5. PDO Mapping entry (8 bits align)
UINT32
RW
0x0000:00, 8
1A04:06
SubIndex 006
6. PDO Mapping entry (object 0x6010, entry 0x10 (TxPDO Toggle))
UINT32
RW
0x6010:10, 1
1A04:07
SubIndex 007
7. PDO Mapping entry (object 0x6010, entry 0x11 (Value))
UINT32
RW
0x6010:11, 32
Index 1A05 AI TxPDO-Map Compact Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A05:0
AI supply TxPDO-Map Compact Ch. 1
PDO Mapping TxPDO  Compact Ch. 1
UINT8
RW
0x01 (1dec)
1A05:01
SubIndex 001
1. PDO Mapping entry (object 0x6010, entry 0x11 (Value))
UINT32
RW
0x6010:11, 32
Index 1A06 AI TxPDO-Map Standard Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A06:0
AI supply TxPDO-Map Standard Ch. 2
PDO Mapping TxPDO  Standard Ch. 2
UINT8
RW
0x07 (7dec)
1A06:01
SubIndex 001
1. PDO Mapping entry (object 0x6020 (AI supply Inputs), entry 0x01 (Underrange))
UINT32
RW
0x6020:01, 1
1A06:02
SubIndex 002
2. PDO Mapping entry (object 0x6020 (AI supply Inputs), entry 0x02 (Overrange))
UINT32
RW
0x6020:02, 1
1A06:03
SubIndex 003
UINT32
RW
0x0000:00, 4
1A06:04
SubIndex 004
4. PDO Mapping entry (object 0x6020 (AI supply Inputs), entry 0x04 (Error))
UINT32
RW
0x6020:07, 1
1A06:05
SubIndex 005
UINT32
RW
0x0000:00, 8
1A06:06
SubIndex 006
6. PDO Mapping entry (object 0x6020, entry 0x10 (TxPDO Toggle))
UINT32
RW
0x6020:10, 1
1A06:07
SubIndex 007
7. PDO Mapping entry (object 0x6020, entry 0x11 (Value))
UINT32
RW
0x6020:11, 32
Index 1A07 AI TxPDO-Map Compact Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A07:0
AI supply TxPDO-Map Compact Ch. 2
PDO Mapping TxPDO  Compact Ch. 2
UINT8
RW
0x01 (1dec)
1A07:01
SubIndex 001
1. PDO Mapping entry (object 0x6020, entry 0x11 (Value))
UINT32
RW
0x6020:11, 32
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default
1C00:0
Sync manager type
Usage of the Sync Manager channels
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync-Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync-Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync-Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync-Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 1C12 RxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Inputs
UINT8
RW
0x01 (1dec)
1C12:01
Subindex 001
1. assigned TxPDO (contains the index of the corresponding TxPDO Mapping object)
UINT16
RW
0x1600 (5632dec)
1C12:02
Subindex 002
2. assigned TxPDO (contains the index of the corresponding TxPDO Mapping object)
UINT16
RW
Index 1C13 TxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x01 (1dec)
1C13:01
Subindex 001
UINT16
RW
0x1A00 (6656dec)
1C13:02
Subindex 002
UINT16
RW
0x1A01 (6657dec)
1C13:03
Subindex 003
3. assigned TxPDO (contains the index of the corresponding TxPDO Mapping object)
UINT16
RW
Index (hex)
Meaning
Data type
Flags
Default
1C32:0
SM output parameter
Synchronization parameter of the outputs
UINT8
RO
0x20 (32dec)
1C32:01
Sync mode
Actual synchronization mode:
  • 0: Free Run
  • 1: Synchron with SM 3 Event (no Outputs available)
  • 2: DC - Synchron with SYNC0 Event
  • 3: DC - Synchron with SYNC1 Event
UINT16
RW
0x0001 (1dec)
1C32:02
Cycle time
Cycle time (in ns):
  • Free Run: cycle time of the local timer
  • Synchron with SM 2 Event: Cycle time of the master
  • DC-Mode: SYNC0/SYNC1 Cycle time
UINT32
RW
0x000C65D4 (812500dec)
1C32:03
Shift time
Time between SYNC0-Event and Input Latch (in ns, only in DC-Mode)
UINT32
RO
0x00000000 (0dec)
1C32:04
Sync modes supported
Supported synchronization modes:
  • Bit 0 = 1: Free Run is supported
  • Bit 1 = 1: Synchron with SM 2 Event is supported
  • Bit 2-3 = 01: DC-Mode is supported
  • Bit 4-5 = 01: Input Shift with local event (Outputs available)
  • Bit 4-5 = 10: Output Shift with SYNC1 Event (only DC mode)
  • Bit 14 = 1: dynamic times (could be measured  by writing 0x1C32:08)
UINT16
RO
0xC007 (49159dec)
1C32:05
Minimum cycle time
Minimum cycle time supported (in ns)
UINT32
RO
0x0000C350 (50000dec)
1C32:06
Calc and copy time
Minimum time between SYNC0 and SYNC1 event (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C32:07
Minimum delay time
UINT32
RO
0x00000000 (0dec)
1C32:08
Command
  • 0: Measurement of the times will be stopped
  • 1: Measurement of the times will be started
The Entries 0x1C32:03, 0x1C32:05, 0x1C32:06, 0x1C32:09, 0x1C33:03, 0x1C33:06, 0x1C33:09 will be updated with the maximum measured values.
The measured valued well be reset, if measured again
UINT16
RW
0x0000 (0dec)
1C32:09
Maximum Delay time
Time between SYNC1-Event and output latch (in ns, only in DC mode)
UINT32
RO
0x00000000 (0dec)
1C32:0B
SM event missed counter
Number of the missed SM-Events in state OPERATIONAL (only in DC Mode)
UINT16
RO
0x0000 (0dec)
1C32:0C
Cycle exceeded counter
Number of the exceeded cycles in state OPERATIONAL
UINT16
RO
0x0000 (0dec)
1C32:0D
Shift too short counter
Number of the too short distances between SYNC0 and SYNC1 Event (only in DC Mode)
UINT16
RO
0x0000 (0dec)
1C32:20
Sync error
BOOLEAN
RO
0x00 (0dec)
Index 1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default
1C33:0
SM input parameter
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
  • 0: Free Run
  • 34: synchronous with SM 2 event (outputs available)
UINT16
RW
0x0022 (34dec)
1C33:02
Cycle time
same as 0x1C32:02
UINT32
RW
1C33:03
Shift time
Time between SYNC0 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:04
  • Bit 0: free run is supported
  • Bit 1: synchronous with SM 2 event is supported (outputs available)
  • Bit 1: synchronous with SM 3 event is supported (no outputs available)
  • Bit 2-3 = 01: DC mode is supported
  • Bit 4-5 = 01: input shift through local event (outputs available)
  • Bit 4-5 = 10: input shift with SYNC1 event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C32:08 or 1C33:08)
UINT16
RO
0xC007 (49159dec)
1C33:05
Minimum cycle time
same as 0x1C32:05
UINT32
RO
1C33:06
Calc and copy time
Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:07
Minimum delay time
UINT32
RO
0x00000000 (0dec)
1C33:08
Command
same as 0x1C32:08
UINT16
RW
0x0000 (0dec)
1C33:09
Maximum Delay time
Time between SYNC1 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
0x00000000 (0dec)
1C33:0B
same as 0x1C32:11
UINT16
RO
0x0000 (0dec)
1C33:0C
same as 0x1C32:12
UINT16
RO
0x0000 (0dec)
1C33:0D
same as 0x1C32:13
UINT16
RO
0x0000 (0dec)
1C33:20
Sync error
same as 0x1C32:32
BOOLEAN
RO
0x00 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
F000:0
General information for the modular device profile
UINT8
RO
0x02 (2dec)
F000:01
Module index distance
Index spacing of the objects of the individual channels
UINT16
RO
0x0010 (16dec)
F000:02
Maximum number of modules
Number of channels
UINT16
RO
0x0001 (1dec)
Index F008 Code word
Index (hex)
Meaning
Data type
Flags
Default
F008:0
Code word
reserved
UINT32
RW
0x00000000 (0dec)
Index F010 Module list
Index (hex)
Meaning
Data type
Flags
Default
F010:0
Module list
Max. subindex
UINT8
RW
0x03 (3dec)
F010:01
SubIndex 001
RMB
UINT32
RW
0x00000172 (370dec)
F010:02
SubIndex 002
 AI
UINT32
RW
0x0000012C (300dec)
F010:03
SubIndex 003
 AI
UINT32
RW
0x0000012C (300dec)