Switch output voltages
For each EtherCAT P port the output voltages US and UP can be switched individually.
Protective functions can prevent the switching-on of the output voltages.
A switched-on output voltage is signaled in two ways:
  • Status LEDs
  • Status bits in the process data:
         „DPO Inputs Channel n“ > „Status“ > „Status Us“
         „DPO Inputs Channel n“ > „Status“ > „Status Up“
         (where: n = 0 for X52, n = 1 for X53, n = 2 for X54, n = 3 for X55)
The output variable "DPO Outputs Device" > "Enable Control Via Fieldbus" defines whether the output voltages are switched manually or automatically.
  • „0“: automatic (factory setting)
  • „1“: manual
Inadvertent switching of output voltages.
If you change the value of "Enable Control Via Fieldbus", it is possible that the output voltages may be switched on or off.
To prevent that, match the values of the CoE indices (automatic switching) and output variables (manual switching) mentioned below to each other before changing the value of "Enable Control Via Fieldbus".
Automatic switching
You can specify whether the output voltages are automatically switched on after application of the supply voltage US.
The following table shows the correlation of the output voltages and the CoE indices that control the automatic switch-on.
EtherCAT P port
Output voltage
CoE Index
X52
US
8000:02
„DPO Settings Ch. 1“ > „Default State Us“
UP
8000:03
„DPO Settings Ch. 1“ > „Default State Up“
X53
US
8010:02
„DPO Settings Ch. 2“ > „Default State Us“
UP
8010:03
„DPO Settings Ch. 2“ > „Default State Up“
X54
US
8020:02
„DPO Settings Ch. 3“ > „Default State Us“
UP
8020:03
„DPO Settings Ch. 3“ > „Default State Up“
X55
US
8030:02
„DPO Settings Ch. 4“ > „Default State Us“
UP
8030:03
„DPO Settings Ch. 4“ > „Default State Up“
Value range:
  • „1“: US/UP is switched on automatically when US is applied (factory setting).
  • „0“: US/UP remains switched off when US is applied.
The output voltages are switched on with a time offset. The time offset prevents the starting currents of the connected EtherCAT P devices adding together.
You can set the time offset in the CoE index F80E:11 "Startup Delay":
  • „0“: „Fast“
  • „1“: „Moderate“
  • „2“: „Slow“
Manual switching
Set "Enable Control Via Fieldbus" to "1" to switch output voltages manually via output variables.
EtherCAT P port
Output voltage
Output variable
X52
US
„DPO Outputs Channel 1“ > „Output Us“
UP
„DPO Outputs Channel 1“ > „Output Up“
X53
US
„DPO Outputs Channel 2“ > „Output Us“
UP
„DPO Outputs Channel 2“ > „Output Up“
X54
US
„DPO Outputs Channel 3“ > „Output Us“
UP
„DPO Outputs Channel 3“ > „Output Up“
X55
US
„DPO Outputs Channel 4“ > „Output Us“
UP
„DPO Outputs Channel 4“ > „Output Up“