Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT | |
Connection | ENP B17 – connector |
Electrical isolation | 500 V |
Supply voltages | |
Connection | Supply (X70): Connector B17 5G 1.5 mm² ENP Downstream connection (X71): Socket B17 5G 1.5 mm² ENP |
US nominal voltage |
24 VDC (-15 % / +20 %) |
US sum current IS,sum | max. 15.5 A at 45 °C |
Current consumption from US | 110 mA + load: IS1, IS2, IS3, IS4 |
Rated voltage UP | 24 VDC (-15 % / +20 %) |
UP Sum current IP,sum | max. 15.5 A at 45 °C |
Current consumption from US | 40 mA + load: IP1, IP2, IP3, IP4 |
EtherCAT P ports | |
Number of ports | 4 |
Connections | M8 sockets, p-coded, shielded |
Nominal current | 3 A per US and UP on each EtherCAT P port |
Nominal current (sum) | 12 A per US and UP |
Capacitive load CLoad | max. 2200 µF per US and UP on each EtherCAT P port |
Switch-on time delay 1) |
1) The output voltages of the EtherCAT P ports are switched on one after the other at the start so that the input inrush currents do not add up. See chapter Switch output voltages.
Overcurrent protection | |
Nominal current In | 1…3 A per US and UP on each EtherCAT P port. |
Tripping characteristic | Adjustable. Default 100 ms at 3 x In. |
Current limitation ILim | 5 A per US and UP on each EtherCAT P port. |
Current limitation: | typically 75 ms |
Fuse (faile-safe element) | Rated current: 5 A |
Further protective functions and diagnosis | |
Overtemperature protection | Threshold values: Twarn = 75 °C → warning on exceeding |
Undervoltage protection | Threshold values: Uwarn = 21.6 V → warning on falling below |
Data logger: Sampling interval |
Data logger: Buffer size | 25 entries. |
Measured values | |
Resolution | Currents per port: 10 mA Sum currents US + UP: 10 mA Voltages: 100 mV Temperature: 1 K |
Representation | Currents per port: 1 mA / LSB Sum currents US + UP: 10 mA / LSB Voltages: 100 mV / LSB Temperature: 1 K / LSB (Celsius scale) |
Housing data | |
Dimensions W x H x D |
60 mm x 150 mm x 26,5 mm (without connectors) |
Weight | approx. 540 g |
Material |
PA6 (polyamide) |
Environmental conditions | |
Ambient temperature during operation |
-25…+60 °C |
Ambient temperature during storage |
-40…+85 °C |
Vibration / shock resistance |
conforms to EN 60068-2-6 / EN 60068-2-27 |
EMC immunity / emission |
conforms to EN 61000-6-2 / EN 61000-6-4 |
Protection class |
IP65, IP66, IP67 conforms to EN 60529 |
Approvals | |
Approvals | CE, EAC, UKCA, UL under preparation |
Additional checks
The boxes have been subjected to the following checks:
Verification | Explanation |
Vibration | 10 frequency sweeps in 3 axes |
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude | |
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude | |
Shocks | 1000 shocks in each direction, in 3 axes |
35 g, 11 ms |