Process image
Process image 1:
In the default setting the EP8309 is configured for:
  • analog input channel 1
  • analog input channel 2
  • Tacho signal from two sensors on one axis (single-shaft mode)
  • 6 digital inputs
  • Status of PWM output
  • Acknowledge / Reset in the event of a PWM error.
  • 6 digital outputs
  • General EtherCAT process data
AI Inputs Channel 1 and 2
Process image 2:
The data for the first analog channel can be found under AI Inputs Channel 1.
Underrange: Value of the analog input is less than 0/4 mA or -10/0 V
Overrange: Value of the analog input is greater than 20 mA or +10 V
Limit 1: with activated Limit 1 (object 0x8000:07 = 1) means
1: value less than limit 1 (set in object 0x8000:13)
2: value greater than limit 1 (set in object 0x8000:13)
3: value equal to limit 1 (set in object 0x8000:13)
Limit 2: with activated Limit 2 (object 0x8000:08 = 1) means
1: value less than limit 2 (set in object 0x8000:14)
2: value greater than limit 2 (set in object 0x8000:14)
3: value equal to limit 2 (set in object 0x8000:14)
Error: This bit is set if over- or under-range was detected.
Tacho single-shaft mode (depending on the setting in the PDO assignment)
Process image 3:
The data for the tacho input can be found under TACHO Single Shaft Mode Input Channel 1.
see data under commissioning
Tacho dual-shaft mode (depending on the setting in the PDO assignment)
Process image 4:
The data for the tacho input can be found under TACHO Dual Shaft Mode Input Channel 1 or 2.
DIG Inputs
Process image 5:
The data for the digital inputs can be found under DIG Inputs.
X4 Pin4 -> socket 4, pin 4
PWM Status
Process image 6:
The data for the PWM output can be found under PWM Status
DEV  Inputs
Process image 7:
The diagnostic data for the two voltages Us and Up can be found under DEV Inputs.
TRUE = voltage <= approx. 18 VDC
TACHO Output Channel 1
Process image 8:
The control data for the tacho input can be found under TACHO Output Channel 1.
Reset Error - error reset
DO Outputs
Process image 9:
The data for the digital outputs can be found under DO Outputs.
X5 pin4 -> socket 5, pin 4
PWM control (activated through PDO assignment 0x1602, default PWM, alternatively AO)
Process image 10:
The control data for the PWM output can be found under PWM Control.
Enable Dithering -> activate dithering
Enable -> activate PWM output
Reset -> reset on error
PWM output -> load-independent current, depending on module rating (e.g. 1.2 A and setting in object 0x8050:10)
AO outputs (activated through PDO assignment 0x1603), not activated by default
Process image 11:
The values for the analog output can be found under AO Outputs.
Analog Output - output value