Setting important motor parameters
Incorrect motor parameters can result in damage.
- Take care when setting the motor parameters.
The motor parameters are stored in CoE object 8010hex.
To ensure safe commissioning, it is sufficient to set the following parameters correctly. Further motor parameters are described under CoE object 8010hex: STM Motor Settings Ch.1.
8010:01 "Maximal current"
The maximum current that the current controller outputs per motor winding.
Unit: mA
Factory setting: 5000dec
The maximum value that should be entered here is the nominal motor current. The nominal current can usually be found in the data sheet of the motor.
8010:02 "Reduced current"
Winding current at motor standstill.
Unit: mA
Factory setting: 1000dec
Criteria for setting this parameter:
- A lower value results in a lower power loss when the motor is at standstill.
- A higher value leads to a higher breakdown torque when the motor is at standstill.
8010:03 "Nominal voltage"
The DC link voltage UP, which you connect to X60.
Risk of confusion: DC link voltage and nominal motor voltage
Unit: 10 mV