Input data
Index 6000 ENC Inputs
Index (hex)
Meaning
Data type
Flags
Default
6000:0
ENC Inputs
Maximum subindex
UINT8
RO
0x16 (22dec)
6000:01
Latch C valid
The counter value was latched with the  “C” input. The data with Latch Value (Index 0x6000:12) corresponds to the latched value if the bit is set.
To re-enable the latch input, Enable latch C (index 0x7000:01) must be canceled and then reset.
BOOLEAN
RO
0x00 (0dec)
6000:02
Latch extern valid
The counter value was locked via the external latch. The data with Latch Value (Index 0x6000:12) corresponds to the latched value if the bit is set.
To re-enable the latch input, Enable latch extern on positive edge (index 0x7000:02) or object Enable latch extern on negative edge (index 0x7000:04) must first be canceled and then reset.
BOOLEAN
RO
0x00 (0dec)
6000:03
Set counter done
The counter was set.
BOOLEAN
RO
0x00 (0dec)
6000:04
Counter underflow
The counter has passed the zero crossing backwards.
Overflow/underflow control is inactive in combination with a reset function (C/external).
BOOLEAN
RO
0x00 (0dec)
6000:05
Counter overflow
Counter overflow.
BOOLEAN
RO
0x00 (0dec)
6000:06
Status of input status
State of the status input (alarm “input 1”)
BOOLEAN
RO
0x00 (0dec)
6000:07
Open circuit
Indicates an open circuit.
Configuration via the objects:
Open circuit detection A Index Index0x8000:0B,
Open circuit detection B Index Index0x8000:0C,
Open circuit detection C Index Index0x8000:0D
BOOLEAN
RO
0x00 (0dec)
6000:08
Extrapolation stall
The extrapolated part of the counter is invalid.
BOOLEAN
RO
0x00 (0dec)
6000:09
Status of input A
Status of input A
BOOLEAN
RO
0x00 (0dec)
6000:0A
Status of input B
Status of input B
BOOLEAN
RO
0x00 (0dec)
6000:0B
Status of input C
Status of input C
BOOLEAN
RO
0x00 (0dec)
6000:0C
Status of input gate
The state of the gate input
BOOLEAN
RO
0x00 (0dec)
6000:0D
Status of external ledge
Status of the extern latch input
BOOLEAN
RO
0x00 (0dec)
6000:0E
Sync error
The Sync error bit is only required for DC mode. It indicates whether a synchronization error has occurred during the previous cycle. This means a SYNC signal was triggered in the Box, although no new process data were available (0=OK, 1=NOK).
BOOLEAN
RO
0x00 (0dec)
6000:0F
TxPDO State
Validity of the data of the associated TxPDO (0 = valid, 1 = invalid).
BOOLEAN
RO
0x00 (0dec)
6000:10
TxPDO Toggle
The TxPDO toggle is toggled by the slave when the data of the associated TxPDO is updated.
BOOLEAN
RO
0x00 (0dec)
6000:11
Counter value
Counter value
UINT32
RO
0x00000000 (0dec)
6000:12
Latch value
Latch value
UINT32
RO
0x00000000 (0dec)
6000:13
Frequency value
The frequency (setting of the scaling in index 0x8000:13 and resolution in index 0x8000:15)
UINT32
RO
0x00000000 (0dec)
6000:14
Period value
The period value (setting of the scaling in index 0x8000:14 and resolution in index 0x8000:16)
UINT32
RO
0x00000000 (0dec)
6000:16
Timestamp
Timestamp of the last counter change
UINT64
RO