Technical data
Technical data
EP4374-0002
Fieldbus
     Fieldbus
EtherCAT
     Connection
2 x M8 socket, green
     Electrical isolation
500 V (fieldbus / IO)
     Process image
Inputs: 2 x 16 bit
Outputs: 2 x 16 bit
Supply
     Connection
Feed: 1 x M8 plug, 4-pin
Downstream connection: 1 x M8 socket, 4-pin
     Current carrying capacity of the connections
4 A per US and UP
     Control voltage US
24 VDC (-15 % / +20 %)
     Peripheral voltage UP
0…30 VDC
     Supply of the module electronics
from the control voltage US
     Current consumption of the module
     electronics
typically 120 mA
     Sensor supply
     (Analog input channels)
from the peripheral voltage UP,
not short-circuit protected
     Actuator supply
     (Analog output channels)
Analog inputs
     Number
2
     Connection
M12 sockets, 5-pin. Pin assignment
     Signal range
Adjustable:
  • -10…+10 V (default)
  • 0…10 V
  • 0…20 mA
  • 4…20 mA
     Electrical specifications
Analog outputs
     Number
2
     Connection
     Output signal range
Adjustable:
  • 0…10 V
  • 0…20 mA
  • 4…20 mA
Environmental conditions
     Ambient temperature during operation
-25…+60 °C
0…+55 °C according to cURus
0…+55 °C according to ATEX
     Ambient temperature during storage
-40…+85 °C
     Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27;
see also Additional checks.
     EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
     Protection class
IP65, IP66, IP67 conforms to EN 60529
Technical data
EP4374-0002
Mechanics
     Weight
approx. 165 g
     Mounting position
variable
Approvals and conformity
     Approvals
CE, cURus, ATEX
Analog inputs
The measuring range can be switched during operation. The following table shows the electrical specifications depending on the selected measuring range.
Technical data
Measuring range
-10…10 V
0…10 V
0…20 mA
4…20 mA
Input type
Differential
Input resistance
> 200 kΩ
> 200 kΩ
85 Ω typ. + diode voltage
Digital resolution
16-bit
15-bit
15-bit
15-bit
Measuring error
< 0.3 % relative to full scale value
Conversion time
approx. 100 µs
Input filter limit frequency
5 kHz
Value of the least significant bit
approx. 305 µV
approx. 305 µV
approx. 610 µA
approx. 488 µA
The analog inputs and outputs have a common analog ground potential. The analog ground potential is electrically isolated from all other ground potentials in the box.
Analog outputs
The output signal range can be switched during operation. The following table shows the electrical specifications depending on the selected output signal range.
Technical data
Output signal range
-10…10 V
0…10 V
0…20 mA
4…20 mA
Load resistor / load
> 5 kΩ
> 5 kΩ
< 500 Ω
< 500 Ω
Digital resolution
16-bit
15-bit
15-bit
15-bit
Output error
< 0.1 % (ambient temperature 0…+55 °C)
< 0.2 % (ambient temperature < 0 °C or > 55 °C)
related to the final value.
Conversion time
approx. 40 µs
approx. 305 µV
approx. 305 µV
approx. 610 µA
approx. 488 µA
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms