Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT
Connection
2 x M8 socket, 4-pin, green
Electrical isolation
500 V
Supply voltages
Connection
Input: M8 connector, 4-pin
Downstream connection: M8 socket, 4-pin, black
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current: IS,sum
max. 4 A
Current consumption from US
120 mA
UP nominal voltage
0 … 30 VDC
UP sum current: IP,sum
max. 4 A
Current consumption from UP
Current for actuator supply.
Analog outputs
Number
4
Connection
M12 sockets
Cable length
Max. 30 m from the box module to the actuator.
Signal type
Configurable:
  • 0 … +10 V
  • -10 … +10 V
  • 0 … 20 mA
  • 4 to 20 mA
Load resistance | load
> 5 kΩ | < 500 Ω
Resolution
16 bits (including sign)
Conversion time
< 4 ms
Output error
< 0.1% (ambient temperature 0°C … +55°C)
< 0.2% (ambient temperature < 0°C oder > 55°C)
based on the final value.
Greatest short-term deviation during a specified electrical interference test
0.5% based on the final value
Actuator supply
From the supply voltage UP, can be selected as desired up to 30 VDC.
Housing data
Dimensions W x H x D
30 mm x 126 mm x 26.5 mm (without connectors)
Weight
approx. 165 g
Installation position
variable
Material
PA6 (polyamide)
Environmental conditions
Ambient temperature during operation
-25 … +60 °C
-25 … +55 °C according to cURus
0 … +55 °C according to ATEX
Ambient temperature during storage
-40 … +85 °C
Vibration resistance, shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
Additional tests
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection rating
IP65, IP66, IP67 (according to EN 60529)
Approvals / markings
Approvals / markings *)
ATEX, CE, cURus
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms