Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT
Connection
2 x M8 socket, 4-pin, green
Electrical isolation
500 V
Distributed Clocks
yes
Minimum cycle time
700 µs
Supply voltages
Connection
Input: M8 connector, 4-pin
Downstream connection: M8 socket, 4-pin, black
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current: IS,sum
max. 4 A
Current consumption from US
120 mA
+ Current consumption of connected sensors
+ Loads at digital outputs
Rated voltage UP
UP sum current: IP,sum
max. 4 A
Current consumption from UP
None. UP is only forwarded.
Diagnostics
Undervoltage detection
  • US < 18 VDC
  • UP < 18 VDC
Pressure inputs
EP3744-0041
EP3744-1041
Number
4
+ 1 reference input for the differential pressure measurement
Connections
Fittings, d = 6 mm
Number of mating cycles
5
Type of pressure measurement
Adjustable:
  • Absolute pressure measurement
  • Differential pressure measurement (factory setting)
Absolute pressure measuring range
0 … 1 bar 1)
(0 … 15 psi)
0 … 7 bar 1)
(0 … 100 psi)
Differential pressure measuring range 3)
-1 … +1 bar
(-15 … +15 psi)
-7 … +7 bar
(-100 … +100 psi)
Resolution
1 mbar per LSB
Measuring error
3% of the full scale value
Conversion time
5 EtherCAT cycles
(Note the minimum EtherCAT cycle time, see above)
Permissible media
non-aggressive gases
Maximum overload of an input
3 bar absolute pressure 2)
21 bar absolute pressure 2)
1) 0 bar = vacuum
   1 bar = ambient pressure
2) Even in the case of differential pressure measurement, the absolute pressure measuring range must not be exceeded at any pressure input.
Digital inputs
Number
6
Connection
4 M8 sockets (sockets 0, 1, 2, 3)
Characteristics
EN 61131-2 type 3, compatible with type 1
Signal voltage "0"
-3 … +5 V
Signal voltage "1"
+11 … +30 V
Input current
3 mA at 24 V
Sensor power supply
24 VDC from the control voltage US
max. 0.5 A in total, short-circuit proof
Digital outputs
Number
2
Connection
2 M8 sockets (sockets 2 and 3)
Nominal voltage
24 V from the control voltage US
Output current
max. 0.5 A per output, individually short-circuit proof
Housing data
Dimensions W x H x D
30 mm x 126 mm x 26.5 mm
(without connectors and fittings)
Weight
approx. 175 g
Installation position
variable
Material
PA6 (polyamide)
Environmental conditions
Ambient temperature during operation
-25…+60 °C
-25...+55 °C according to cURus
Ambient temperature during storage
-40…+85 °C
Vibration resistance, shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
Additional checks
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Approvals / markings
Approvals / markings *)
CE, cURus, EAC, UKCA
Additional checks
The boxes have been subjected to the following checks:
Verification
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms