Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT
Connection
2 x M8 socket, 4-pin, A-coded, shielded
Electrical isolation
500 V
Distributed Clocks
yes
Minimum cycle time
100 µs
Supply voltages
Connection
Input: M8 connector, 4-pin, A-coded
Downstream connection: M8 socket, 4-pin, A-coded
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current: IS,sum
max. 4 A
Current consumption from US
120 mA
Rated voltage UP
UP sum current: IP,sum
max. 4 A
Current consumption from UP
The measuring bridge supply voltage Uref is generated internally from UP.
Measuring bridge connection
Signal interface
M12 socket, 5-pin, A-coded
Signal type
Resistor bridge, strain gauge (SG)
Number of analog inputs
2, for 1 bridge circuit in full bridge technology.
Cable length
max. 30 m between box and measuring bridge
Measured value resolution
24-bit, 32-bit representation
Conversion time
0.1 … 250 ms, configurable
Conversion rate
4 ... 10,000 samples/s (reciprocal of the conversion time)
Measuring error
< ±0.01 % 1) for the calculated load value based on the load end value with 10 V power supply and 20 mV bridge voltage (therefore nominal characteristic value for SG: 2 mV/V), self-calibration active, 50 Hz filter active.
Measuring range UD
max. -27 … +27 mV 2)
Recommended: -25 … +25 mV nominal voltage
Measuring range Uref
max. -13.8 … +13.8 V 2)
Supported nominal characteristic values
any, resolution of the parameter: 0.01 µV/V
Recommended: 0.5 … 2.5 mV/V
min. strain gauge resistance
Parallel use of strain gauges only recommended with suitable strain gauges
Input filter (hardware) cut-off frequency
10 kHz low-pass (-3 dB, see filter notes)
Filter (software)
Preset 50 Hz, configurable:
50/60 Hz FIR notch filter, IIR low-pass, 4-fold averager
Internal resistance
  • Uref-measurement input: > 200 kΩ
  • Ud-measurement input: > 1 MΩ
Measuring bridge supply voltage (sensor power supply)
Uref = 10 V (generated internally from UP)
max. 350 mA
1) External influences such as Temperature drift and RF interference can increase the measuring error.
2) See chapter Voltage measurement.
Housing data
Dimensions W x H x D
60 mm x 126 mm x 26.5 mm (without plug connectors)
Weight
approx. 250 g
Installation position
variable
Material
PA6 (polyamide)
Environmental conditions
Ambient temperature during operation
-25 … +60 °C
-25 … +55 °C according to cURus
Ambient temperature during storage
-40 … +85 °C
Vibration resistance, shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
Additional tests
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Approvals/markings
Approvals/markings *)
CE, cURus
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms