Calculation of process data
The terminal/box constantly records measured values and saves the raw values from its A/D converter in the ADC raw value object 0x80nE:01. The calculation of the correction with the vendor calibration values takes place after each acquisition of the analog signal. This is followed (optionally) by user scaling:
YH= (XADC-BH) * AH measured value after vendor calibration (corresponds to XADC if index 0x80n0:0B inactive)
YA= (YH-BA) * AA measured value after user calibration (corresponds to YH if index 0x80n0:0A inactive)
YS= YA * AS * 22-16 + BS measured value after user scaling (corresponds to YA if index 0x80n0:01 is inactive)
Key
Index
XADC
Output value of the A/D converter
0x80nE:01
BH
Vendor calibration offset (can only be changed if the object Producer codeword 0xF008 is set)
0x80nF:01
AH
Vendor calibration gain (can only be changed if the object Producer codeword 0xF008 is set)
0x80nF:02
YH
Measured value after vendor calibration
BA
User calibration offset
0x80n0:11
AA
User calibration gain
0x80n0:12
YS
Measured value after user calibration
BS
User scaling offset (can be activated via index 0x80x0:0A)
0x80n0:17
AS
User scaling gain (can be activated via index 0x80x0:0A)
0x80n0:18
YS
Process data for control, measured value after user scaling