Basic function principles of EtherCAT junctions
Some Beckhoff EtherCAT devices can be used for junctions in the EtherCAT segment. These include EK1122, EK1521, EP1122, CU1128 and EP9128. In the following examples only the EK1122 is used. The technical and system characteristics of the other devices are similar.
EtherCAT handling in the slaves
With EtherCAT as fieldbus protocol a wide range of bus topologies can be used: line, star and tree topology, with redundancy support even ring topology. The simplest topology is the line topology, in which each EtherCAT slave passes data only to the next slave.
Basic function principles of EtherCAT junctions 1:
EtherCAT line topology
When using EtherCAT Couplers, e.g. EK1100, it is possible to create a junction and therefore a kind of tree topology.
Basic function principles of EtherCAT junctions 2:
Line topology with extensions
The basic principle is that internally the Ethernet frame(s) with the EtherCAT protocol data continue to be transported in a logical ring:
At short cycle times in the order of 50 µs at 20,000 Ethernet frames are in transit in the EtherCAT system every second, plus acyclic organizational frames. The master awaits the return of the sent frames, which return the device input data to the master, for example. Telegram transfer between slaves is link-based: An EtherCAT slave will only forward a frame if a 'link' signal to the next device is present. Normally it can be assumed that the downstream device correctly processes each EtherCAT telegram and returns or process it at the end.
The crucial factor for forwarding EtherCAT telegrams is that a link signal is reported only from one slave to the next if both slaves are actually ready for real-time participation in data processing. Specifically, this means that an EtherCAT slave should not open the respective Ethernet port until it is ready to receive and forward an Ethernet frame immediately.
A switch or router is usually used for standard Ethernet traffic forwarding. Any collisions or frame losses are compensated through frame repetition in the higher-level protocol layers (e.g. TCP). This mode is generally not used for EtherCAT due to the short cycle times and the real-time requirement. Some Ethernet devices such as special switches, for example, report a link to the remote terminal even if they will only be ready for data processing in a few milliseconds. This behavior is particularly noticeable in media converters from 100Base-TX (copper) to 100Base-Fx (optical fiber), which may report a link to the preceding EtherCAT slave even if the optical fiber connection is interrupted, depending on the setting on the copper side.
Fast link detection is therefore a central component of each ESC (EtherCAT Slave Controller, hardware processing unit for the EtherCAT protocol). According to the EtherCAT specification an ESC can have and control 1 to 4 ports. Via an open port it can handle outgoing and incoming Ethernet traffic. Fig. 3 shows the direction of the data flow in a fully configured ESC. In the EtherCAT datagrams the data are only processed between ports 0 (A) and 3 (D) in the EtherCAT processing unit.
Basic function principles of EtherCAT junctions 3:
Direction of data flow in the ESC
Ideally link detection and therefore port handling in the ESC should be fast enough that lost frame events are avoided even at 100 µs cycle time. Nevertheless, at least one lost frame can never be ruled out if a connection is disconnected while an Ethernet frame is in transit on this line and in the bus segment downstream of the separation point.
Implementation: EL terminal
A standard EtherCAT slave  such as a Beckhoff EL terminal has 2 ports:
The other two ports are internally closed in the ESC. An EtherCAT telegram enters the processing unit via port 0 (A)/top and is forwarded to the next slave via port 3 (D)/left, if a link to this port exists - see green arrows. This is the case if a further EL terminal is connected to the right.
If no link exists, the frame is forwarded to port 1(B) via the purple route. This and port 2 (C) have no link and therefore return the frame to port 0 (A), where the frame leaves via the same Ethernet port through which it arrived at the slave. This is the case if the terminal acts as end terminal.
An EtherCAT device with a single port is therefore only of limited use, since it can only be used as end device.
Implementation: EK1100 EtherCAT Coupler
Three of the four available ports in the EK1100 EtherCAT Coupler are used, thus enabling a connection to the right to terminals and via an RJ45 socket to further couplers; cf. Fig. Line topology with extensions. In the EK1100 the processing unit is not used for process data exchange.
Implementation: EK1122 EtherCAT junction
In the EK1122 all four ESC ports can be connected. two via the internal E-Bus and two via the RJ45 sockets with Ethernet configuration. In the TwinCAT System Manager the link statuses of ports 0, 1, 2 and 3 are indicated via the online display as port A, B, C and D, see Fig. Topology display for interrupted line.
Implementation: EK1521/EK1521-0010/EK1561 EtherCAT junction
As in the EK1100, three ESC ports can be connected in these junctions. Two via E-bus within the terminal and one via the SC socket/versatile link and optical fiber cable/POF line.
Implementation: CU1128 and EP9128 EtherCAT junctions
The CU1128 integrates three ESCs, which means eight ports in total are available to users. The three ESCs are interconnected via E-bus.
Example configuration with EK1122
The following section describes the link characteristics under TwinCAT and its representation in the System Manager.
Basic function principles of EtherCAT junctions 4:
The wiring diagram is shown in the TwinCAT online topology, see Fig. Online topology. The EK1122 is selected, so that further information is shown. The green bars above the slaves indicate the correct RUN state in all slaves.
Basic function principles of EtherCAT junctions 5:
Online topology
An error is now generated by disconnecting the link between the upper RJ45 socket (X1) and the EL3102 device. Within a few µs the ESC in the EK1122 detects the lost link and automatically closes the affected port. This has the effect that the next incoming EtherCAT telegram is immediately forwarded to port D (port 3) and the EL4732. The link is missing here; the System Manager indicates this in the online display, see Fig. Example configuration with interrupted cable.
Basic function principles of EtherCAT junctions 6:
The System Manager messages can be interpreted as follows:
Basic function principles of EtherCAT junctions 7:
Logger output
The logger output can be displayed in the lower part of the System Manager (Display--> Show Logger Output). This may be helpful for diagnostic purposes (for link interruptions and other situations).
In the topology view this interruption is indicated by a red border around the affected slaves, see figure below.
Basic function principles of EtherCAT junctions 8:
Topology view with interrupted line
Note the display of the acyclic frames in Fig. Example configuration with EK1122 and Fig. Example configuration with interrupted line.
Basic function principles of EtherCAT junctions 9:
Comparison of the frame displays
The image on the left shows a small number (2) of acyclic frames sent by the master during the respective second - all slaves are operating properly. The image on the right shows a significant increase (currently 77 acyclic frames/sec): The EtherCAT master has quickly detected that not all slaves are properly taking part in the data exchange. Once the master has located the fault, it continuously tries to restore the connection.
Reconnection
Once the connection has been restored, the EK1122 reports to the master that a link is present again at port D (3). The EtherCAT master will then make its process data available again for this section. One the preparations are complete, it will instruct the EK1122 to re-open port D (3) for regular data exchange. Cyclic and acyclic data traffic with the other EtherCAT slaves continues normally.
Basic function principles of EtherCAT junctions 10:
External access to EtherCAT diagnostics
The system offers a wide range of options for accessing status and diagnostic information and EtherCAT master functions from the PLC. Almost all information displayed by the System Manager online can also be retrieved via ADS (see figures on this page). System Manager functions can also be triggered via PLC or ADS. Please refer to the relevant sections in the Beckhoff Information System and the notes on EtherCAT diagnostics.