EL6751 – Bus node diagnostics
The CANopen fieldbus card EL6751 has a comprehensive range of diagnostic options for connected network nodes.
EL6751 – Bus node diagnostics 1:Fig.139: Diagnosis of inputs in the TwinCAT tree
For each CANopen fieldbus node there is a node state input variable, which signals the status of the current slave during the runtime and can be linked, for example with the PLC.
Node State (Box-State)
EL6751 – Bus node diagnostics 2:Fig.140: "Variable" tab
Node State
Meaning
Explanation
0 = 0x00
No error
Bus node is operational, communication is running correctly
1 = 0x01
Node deactivated
The node is subject to one or more of the following errors:
  • guarding/heartbeat error (failure, toggle bit error, node has changed state)
  • expected TxPDO has not been received
  • TxPDO length shorter than expected
Node has been stopped, because "Manual restart" following a node failure has been selected.
2 = 0x02
Node not found
Node not found: no answer to SDO read access to object 0x1000 at the expected node address. Check the following at the node: what node address is set, and what baud rate. Check network (terminating resistors, connectors, bus length, crossed wiring etc.)
4 = 0x04
SDO syntax error at StartUp
Error during SDO write access: SDO abort by node. See the "Diag" tab for details.
or: the length of an object read by SDO does not agree with the expected length.
5 = 0x05
SDO data mismatch at StartUp
Expected data does not agree with that read via SDO (e.g. device profile and/or additional info do not agree with object 0x1000). Can also occur if the value to be written (e.g. PDO COB-ID) is read back due to refusal of write access, and does not agree. See the "Diag" tab for details.
8 = 0x08
Node StartUp in progress
Node was found and has been started.
11 = 0x0B
EL6751Bus-OFF
CAN chip has entered the "Bus-OFF" state: transmit error counter is running
12 = 0x0C
Pre-Operational
Node has gone pre-operational (on its own account).
13 = 0x0D
Severe bus fault
General firmware error
14 = 0x0E
Guarding: toggle error
Guarding error: Toggle bit has not changed
20 = 0x14
TxPDO too short
Received TxPDO shorter than expected
22 = 0x16
Expected TxPDO is missing
  • TxPDO has not been received within the expected time interval:
  • sync interval with synchronous TxPDOs,
  • event timer with event-driven PDOs)
23 = 0x17
Node is Operational but not all TxPDOs were received
Node has been started, but at least one TxPDO has not yet been received from the node. Possible causes (e.g.):
  • The node only sends event-driven PDOs after the first event (this is not the intention of the CANopen specification, but is quite usual)
  • Too many TxPDOs have been configured
  • A TxPDO is present at the node, but no process data has been mapped
  • The TxPDO has transmission type 1...120 (synchronous), but SYNC has not yet been sent because the associated task has not been started
DiagFlag
Shows whether the box diagnostic information has changed.
Reading the Diagnostic Data via ADS
CANopen emergencies and other diagnostic data can be read out via ADS read (new data present as soon as you see the DiagFlag). The ADS Net-ID of the EL6751 must be entered for this. Other ADS parameters:
Port: 200
IndexGroup: Lo-Word = 0xF180, Hi-Word = Node-Number.
IndexOffset: See below
Length: See below
If more than 26 bytes of diagnostic data have been read out the emergency memory is reset. The DiagFlag is reset as soon as at least 108 bytes have been read starting from offset 0. Alternatively, the flag is reset after each of read access, if IndexGroup 0xF181 (instead of 0xF180) is used for the read.
The diagnostic data have the following definitions:
Offset 0,1:
Bit 1:
Boot up message not received or incorrect
Bit 2:
Emergency-Overflow
Bit 0, Bit 3-15:
reserved
Offset 2,3:
Bit 0-14:
TX-PDO (i+1) received
Bit 15:
All TX PDOs 16-n received
Offset 4,5:
Bit 0-4:
1: Incorrect TX PDO length
2: Synchronous TX PDO absent
3: Node signaling PRE-OPERATIONAL
4: Event timer timed out for TX PDO
5: No response and guarding is activated
6: Toggling missed several times and guarding activated
Bit 5-15:
Associated COB ID
Offset 6:
Bit 0-7:
1: Incorrect value during SDO upload
2: Incorrect length during SDO upload
3: Abort during SDO up/download
4: Incorrect date during a boot-up message
5: Timeout while waiting for a boot-up message
Offset 7:
Bit 0-7:
2: Incorrect SDO command specifier
3: SDO toggle bit has not changed
4: SDO length too great
5: SDO-Abort
6: SDO-Timeout
Offset 8,9
Bit 0-7:
SDO up/download index
Offset 10:
Bit 0-7:
SDO up/download sub-index
Offset 11:
Bit 0-7:
reserved
Offset 12:
Bit 0-7:
Abort errorClass
Offset 13:
Bit 0-7:
Abort errorCode
Offset 14,15:
Bit 0-15:
Abort additionalCode
Offset 16-19:
Read value (if offset 6 = 1)
Offset 20-23:
Expected value (if offset 6 = 1)
Offset 24-25:
Number of consecutive emergencies
Offset 26 - n:
Emergencies (8 bytes each)
