Objects for commissioning
Index 0x1011 Restore default parameters
Index (hex)
Meaning
Data type
Flags
Default
1011:0
UINT8
RO
0x01 (1dec)
1011:01
SubIndex 0x001
If this object is set to “0x64616F6C” in the set value dialog, all backup objects are reset to their delivery state.
UINT32
RW
0x00000000 (0dec)
Objects for commissioning 1:
Use 0x8000 COM Settings for new implementations
For new implementations, it is recommended to use the settings listed below in 0x8000 COM Settings instead of the Settings objects 0x407_.
Index 0x4073 Baud rate
Index (hex)
Meaning
Data type
Flags
Default
4073:0
Baud rate
Detailed information can be found in chapter Communication features
UINT16
RW
0x0006 (6dec)
Index 0x4074 Data frame
Index (hex)
Meaning
Data type
Flags
Default
4074:0
Data frame
UINT16
RW
0x0003 (3dec)
Index 0x4075 Feature bits
Index (hex)
Meaning
Data type
Flags
Default
4075:0
Feature bits
Length of this object
UINT8
RO
0x06 (6dec)
4075:01
EL6001:
Enable RTS/CTS
0: RTS/CTS not enabled
1: RTS/CTS enabled
BOOLEAN
RW
0x00 (0dec)
EL6021:
Enable half duplex
0: Full-duplex mode
1: Half-duplex mode
4075:02
Enable XON/XOFF supported tx data
0: XON/XOFF is not supported for send data
1: XON/XOFF is supported for send data
BOOLEAN
RW
0x00 (0dec)
4075:03
Enable XON/XOFF supported rx data
0: XON/XOFF is not supported for receive data
1: XON/XOFF is supported for receive data
BOOLEAN
RW
0x00 (0dec)
4075:04
EL6001:
Enable send FIFO data continous
0: No continuous sending of data from the FIFO
1: The send buffer is filled (up to 128 bytes) by the controller. The buffer content is sent with rising edge of bit CW.3 in the control word. The terminal acknowledges the data transfer to the controller through setting of bit SW.2 in the status word. SW.2 is reset with CW.3.
BOOLEAN
RO
0x00 (0dec)
EL6021:
Enable point to point connection (RS422)
0: Point-to-point connection disabled
1: Point-to-point connection enabled
BOOLEAN
RO
0x00 (0dec)
4075:05
EL6001:
Enable transfer rate optimization
0: Transfer rate optimization switched off
1: Transfer rate optimization switched on:
The content of the input buffer is automatically transferred into the process image if
  • no further byte was received for approx. 16 bit times (i.e. the time it would have taken to receive 2 bytes) after data were received;
  • the input buffer is full
BOOLEAN
RO
0x01 (1dec)
 EL6021:
Enable send FIFO data continuous
BOOLEAN
RO
0x00 (0dec)
4075:06
EL6021 only:
  • the process image is filled
BOOLEAN
RW
0x01 (1dec)
Index 0x4076 Rx buffer full notification
Index (hex)
Meaning
Data type
Flags
Default
4076:0
The value determines the number of data in the receive FIFO from which bit SW.3 (BUF_F) is set in the status byte.
UINT16
RW
0x0000 (0dec)
Index 0x8000 COM settings [from hardware version 03]
Index (hex)
Meaning
Data type
Flags
Default
8000:0
COM Settings
Max. SubIndex (hex)
UINT8
RO
0x26 (38dec)
8000:01**
Enable RTS/CTS
FALSE
RTS/CTS not enabled
BOOLEAN
RW
0x01 (1dec)
TRUE
RTS/CTS enabled
8000:02
FALSE
BOOLEAN
RW
0x00 (0dec)
TRUE
8000:03
FALSE
BOOLEAN
RW
0x00 (0dec)
TRUE
8000:04
FALSE
BOOLEAN
RW
0x00 (0dec)
TRUE
Continuous sending of data from the FIFO enabled:
The filled buffer content is sent on rising edge of bit “SendContinious”.
The terminal acknowledges the data transfer to the controller through setting of bit "InitAccepted".
InitAccepted” is reset with “SendContinuous”.
8000:05
FALSE
BOOLEAN
RW
0x01 (1dec)
TRUE
8000:06***
Enable half duplex
FALSE
Full-duplex mode
BOOLEAN
RW
0x00 (0dec)
TRUE
Half-duplex mode
8000:07***
FALSE
BOOLEAN
RW
0x00 (0dec)
TRUE
8000:11
Baud rate
BIT4
RW
0x06 (6dec)
8000:15
Data frame
BIT4
RW
0x03 (3dec)
8000:1A
The value specifies the number of data in the receive FIFO, from which the bit “buffer full” is set.
UINT16
RW
0x0360 (864dec)
8000:1B**
Explicit baudrate
In this object the desired baud rate can be entered directly as a number.
Only the baud rates specified in Communication features are supported. Changes to this object are also adopted into the objects 0x8000:11 and 4073
UINT32
RW
0x00000384 (9600dec)
8000:1C**
Extended data frame
In this object special formats can also be selected in addition to the usual data frames (e.g. 9N1). Changes to this object are also adopted in the objects 0x8000:15 and 0x4074.
ENUM16
RW
0x0003 (3dec)
**) EL6001 from FW11, EL6021 from FW09
***) only EL6021