EK9300 configuration
EK9300 configuration 1:
GSDML file
Only terminals that are present in the GSDML file are supported, but extensions are possible. The GSDML supports submodules, check with your PROFINET master/controller if it supports submodules. If this is not the case, some terminals cannot be used!
Alternatively the CX8093 can be used; this generally supports all EtherCAT slaves.
General
The EK9300 PROFINET coupler is always implemented with the help of a GSDML file in the controller (master). The GSDML file contains all parameterization data necessary for the operation of the coupler on the controller. The configuration tool reads this file and then provides the data to the user.
The respective terminals that are usable on the EK9300 are also specified in the GSDML file. Not all EtherCAT terminals are supported. Therefore, ascertain beforehand whether the terminals that you wish to use are also supported by the coupler.
Status and Ctrl. flags
PnIoBoxState and PnIoBoxDiag can be used to monitor and evaluate the current status of PROFINET communication.
EK9300 configuration 2:Fig.20: Evaluation via PnIoBoxState and PnIoBoxDiag
PnIoBoxState
Comment
Meaning
0
No Error
No error
1
PROFINET Device state machine is in boot mode
PROFINET DeviceStateMachine is in the start-up phase
2
Device not found
Device does not reply to the Identify Request
3
The station name is not unique
4
IP could not be set
IP address could not be set
5
IP conflict
An IP conflict has occurred in the network
6
DCP set was not successful
There was no reply or an erroneous reply to a DCP set
7
Watchdog error
The connection was broken off with a Watchdog error
8
Datahold error
The connection was broken off with a Datahold error
9
RTC3: Sync signal could not be started
Only the IRT: the Sync signal could not be started
10
PROFINET Controller has a link error
The PROFINET controller has no link
11
The alias name is not unique
12
The automatic name assignment is not possible - wrong device type
Automatic name assignment is not possible - wrong device type
13
IOC-AR is established but no application ready
The IOC-AR is established, the application is not ready
14
IOC-AR is established but module difference
The IOC-AR is established, but there is a module difference
15
At least one InputCR is invalid, provider in stop or problem indicator is set
16
At least one OutputCR is invalid, provider in stop or problem indicator is set
31
only for EtherCAT gateways: WC-State of cyclic EtherCAT frame is 1
Only for EL663x-00x0: EtherCAT WC State is set to 1
PnIoBoxDiag
Comment
Meaning
0x0000
No Diagnosis
No diagnosis
0x0001
IOC-AR is not established
The IOC-AR is not established
0x0002
The IOC-AR is built
0x0004
0x0008
0x0008 = IOC-AR is established but module difference
0x0010
At least one AlarmCR got a diagnosis alarm
At least one AlarmCR has received a diagnostic alarm
0x0100
0x0200
At least one InputCR provider is in stop
0x0400
At least one InputCR problem indicator is set
0x1000
0x2000
At least one OutputCR provider is in stop
0x4000
At least one OutputCR problem indicator is set
PnIoBoxCtrl
Comment
Meaning
0x0001
EBus reset
EBus reset at EK9300/EP9300
Data in the DAP (Device Access Point)
2 x 2 bytes of data are located in the DAP of the GSDML file.
This is once the ECCycleCounter (2 bytes). This is incremented on each EtherCAT cycle (1 ms), provided that the EC master is in the "OP" state.
The status (2 BYTE) is located at the DAP. This indicates individual status information bit by bit. These are currently occupied as follows:
Parameters in the DAP
Activate PN reset value Off -> EtherCAT data are written to zero. On -> there is a possibility to use another default value with outputs. With digital outputs, for example, the current output process value can be frozen or set to 0 or 1 in case of a PROFINET communication error.
Data presentationIntel Format data are represented in Intel format, Motorola Format data are represented in Motorola format. In Word variables, for example, the high and low bytes are exchanged.
EBus error behaviorSet IOs to 0 -> input and output data are set to zero in case of an EC error. Legacy -> input data retain their last state, but are no longer updated; output data can still be set (depending on the position of the terminal).
Mapping
Typically the coupler is used in a group with terminals that are connected to the coupler. The terminals are part of the GSDML; the terminals are parameterized from the PROFINET controller.
The mapping is card-slot-oriented, i.e. you must enter the terminals in the hardware configurator in exactly the same way as they are physically connected. It becomes a little more complicated if EtherCAT distribution boxes are used. In this case it is important to know the order in which the other EtherCAT terminals were entered into the process image (see EtherCAT Mapping).
EK9300 configuration 3:
Behavior when starting the bus coupler
All EtherCAT devices must always be present when starting (or resetting) the Bus Coupler. This means that all EtherCAT slaves must be supplied with voltage before or at the same time so that the coupler starts up properly on the PROFINET.
A solution can be constructed more flexibly with the CX8093.
Configuration of the EtherCAT devices
There are 4 types of EtherCAT devices:
All of these must be entered in the configuration.
Grouping digital inputs and outputs (pack terminals)
The digital input and output terminals can also be grouped according to their process data. This option can be used with 2 or 4-channel terminals. To do this a 2 or 4-channel pack terminal (without asterisk) must be appended to the GSDML file. In order to fill the byte, a 2 or 4-channel pack terminal (with asterisk) must be appended next. The terminals must be physically and systematically plugged in one behind the other or logically. The byte limit must not be exceeded.
Sample:
2-channel pack (without asterisk), after that 3 modules from 2-channel pack terminals (with asterisk) may be appended.
Not permitted:
2-channel pack (without asterisk), then 2 modules from 4-channel pack terminals (with asterisk). This exceeds the byte limit.
EtherCAT terminals with different mapping options
Some EtherCAT terminals offer the option to represent different process data. These are represented differently on the basis of the parameters. In the PROFINET controller such a terminal is represented by submodules. The standard mapping is always integrated. If you want to use a different mapping that deviates from the standard, then delete the standard submodule and insert the one that you wish to use. It may be the case that, contradictory to the documentation for the EtherCAT terminal or EtherCAT box, not all mappings can be used under the PROFINET coupler.
Example of an EL5101:
EK9300 configuration 4:Fig.21: Inserting a sub-module
EtherCAT gateway terminals
The gateway terminals support several submodules; the first or basic module is loaded immediately, the modules for the process data must be created. These must then also be parameterized on the master side of the corresponding gateway. Not all features of a gateway terminal can be used on the EK9300.
EL6631-0010
The PROFINET device terminal enables two different PROFINET networks to be connected; only one device interface is supported on the EK. A default station name can be assigned and IP settings made via parameterization data (GSDML). Note that the complete maximum data length of the EL6631-0010 cannot be used. The length is dependent on the other EtherCAT devices attached to the EK9300.
EL6731-0010
The PROFIBUS slave terminal enables communication with a PROFIBUS master. The PROFIBUS address is specified via the parameter settings (in the GSDML) in the terminal. Only pure process data can be exchanged.
EL6692
The EtherCAT slave terminal enables communication with a EtherCAT master. Only pure process data can be exchanged.
EL6652-0010
The EtherNet/IP slave terminal enables communication with an EtherNet/IP master; only one slave interface is supported on the EK. The IP address and subnet mask are specified via the parameter settings (in the GSDML) of the terminal. Only pure process data can be exchanged. The terminal on the EK supports only one slave interface.