Power supply for the EtherCAT plug-in modules
WARNING
Power supply from SELV/PELV power supply unit!
SELV/PELV circuits (Safety Extra Low Voltage, Protective Extra Low Voltage) according to IEC 61010-2-201 must be used to supply this device.
Notes:
  • SELV/PELV circuits may give rise to further requirements from standards such as IEC 60204-1 et al, for example with regard to cable spacing and insulation.
  • A SELV (Safety Extra Low Voltage) supply provides safe electrical isolation and limitation of the voltage without a connection to the protective conductor,
    a PELV (Protective Extra Low Voltage) supply also requires a safe connection to the protective conductor.
The signal distribution board should have a power supply designed for the maximum possible current load of the module string. Information on the current required from the E-bus supply can be found for each module in the respective documentation in section “Technical data”, online and in the catalog. The power requirement of the module string is displayed in the TwinCAT System Manager.
E-bus power supply with EJ1100 or EJ1101-0022 and EJ940x
The EJ1100 Bus Coupler supplies the connected EJ modules with the E-bus system voltage of 3.3 V. The Coupler can accommodate a load up to 2.2 A. If a higher current is required, a combination of the coupler EJ1101-0022 and the power supply units EJ9400 (2.5 A) or EJ9404 (12 A) should be used. The EJ940x power supply units can be used as additional supply modules in the module string.
Depending on the application, the following combinations for the E-bus supply are available:
Power supply for the EtherCAT plug-in modules 1:
E-bus power supply with EJ1100 or EJ1101-0022 + EJ940x
In the EJ1101-0022 coupler, the RJ45 connectors and optional ID switches are external and can be positioned anywhere on the signal distribution board, as required. This facilitates feeding through a housing.
The EJ940x power supply plug-in modules provide an optional reset function (see chapter Connection of the documentation for EJ9400 and EJ9404)
E-bus power supply with CXxxxx and EK1110-004x
The Embedded PC supplies the attached EtherCAT Terminals and the EtherCAT EJ coupler
The EK1110-004x EtherCAT EJ couplers relay the following parameters to the signal distribution board via the rear connector:
Power supply for the EtherCAT plug-in modules 2:
PCB with Embedded PC, EK1110-0043 and EJxxxx, rear view EK1110-0043
