Technical data
Technical data
EJ7041-0052
Technology
compact Drive Technology
Number of outputs
1 stepper motor, 2 phases
Number of inputs
2 end position
Number of channels
1 stepper motor, 2 digital inputs
Connection method
direct motor connection
Load type
2-phase stepper motor (uni-/ bipolar)
Nominal voltage
24 VDC (-15%/+20%)
Supply voltage power
8 ... 48 VDC (via Distribution Board)
Output current max.
5.0 A (overload- and short-circuit-proof)
Maximum step frequency
1000, 2000, 4000, or 8000 full steps/s (configurable)
Step pattern
up to 64-fold micro stepping
Current controller frequency
approx. 16 kHz
Diagnostics LED
error phase A and B, loss of step/stagnation, power, enable
Resolution
approx. 5000 positions in typ. applications (per revolution)
Electrical isolation
500 V (E-bus/field voltage)
Current consumption Load voltage
(Up-contacts)
typ. 50 mA
Current consumption from the E-bus
typ. 140 mA
Distributed-Clocks (DC)
yes
Special features
travel distance control
Support NoCoEStorage
yes
Permissible ambient temperature range during operation
0°C ... +55°C
Permissible ambient temperature range during storage
-25°C ... + 85°C
Permissible relative humidity
95 %, no condensation
Operating altitude
max. 2.000 m
Dimensions (W x H x D)
approx. 24 mm x 66 mm x 55 mm
Weight
approx. 50 g
Mounting
on signal distribution board
Pollution degree
2
Installation position
Standard see note
Position of coding pins
1 and 8
Color coding
orange
Vibration/shock resistance
Conforms to EN 60068-2-6 / EN 60068-2-27 (with corresponding signal distribution board)
EMC immunity/emission
according to EN 61000-6-2 / EN 61000-6-4 (with corresponding signal distribution board)
according to IEC/EN 61800-3 (with corresponding signal distribution board)
EMC category
Category C3 - standard
Category C2, C1 - auxiliary filter required
Protection class
EJ module: IP20
EJ system: dependent on signal distribution board and housing
Approvals/markings*
CE, EAC, UKCA
Technical data 1:
CE approval
The CE Marking refers to the EtherCAT plug‑in module mentioned above.
If the EtherCAT plug-in module is used in the production of a ready-to-use end product (PCB in conjunction with a housing), the manufacturer of the end product must check compliance of the overall system with relevant directives and CE certification.
To operate the EtherCAT plug‑in modules, they must be installed in a housing.