EJ413x - Technical Data
Technical data | EJ4132 | EJ4134 |
Connection technology | 2-wire, single-ended | |
Number of outputs | 2 | 4 |
Signal voltage | -10 V to +10 V | |
Distributed Clocks | yes | |
Maximum cable length to the sensor |
| 30 m (see note) |
Accuracy Distributed Clocks | << 1 µs | |
Load | > 5 kΩ (short-circuit-proof) | |
Measuring error | < 0.1 % (at 0°C .. +55°C, relative to full scale value) | |
Resolution | 16 bit (including sign) | 16-bit |
Electrical isolation | 500 V (E-bus/field voltage) | |
Conversion time | ~ 40 µs | ~ 200 µs |
Current consumption load voltage (Up contacts) | - | typ. 40 mA |
Current consumption via E-bus | typ. 185 mA | typ. 90 mA |
Permissible ambient temperature range during operation | -25°C .. +60°C (extended temperature range) | |
Permissible ambient temperature range during storage | -40 °C .. +85 °C | |
Permissible relative air humidity | 95 %, no condensation | |
Operating altitude | max. 2,000 m | |
Dimensions (W x H x D) | approx. 12 mm x 66 mm x 55 mm | |
Pollution degree | 2 | |
Weight | approx. 30 g | |
Mounting | on signal distribution board | |
Mounting position | ||
1 and 7 | ||
Color coding | blue | |
Vibration / shock resistance | conforms to EN 60068-2-6 /EN 60068-2-27 (with corresponding signal distribution board) | |
EMC immunity / emission | conforms to EN 61000-6-2 /EN 61000-6-4 (with corresponding signal distribution board) | |
Protection class | EJ module: IP20 | |
Approvals / markings | CE, EAC, UKCA, |
CE approval The CE Marking refers to the EtherCAT plug-in module mentioned above. |
Maximum cable length to the sensor Without additional protective measures, the maximum cable length from the EtherCAT Module to the sensor is 30 m. For longer cable lengths, suitable surge protection should be provided. |