Technical data
Technical data | EJ3318 |
Number of inputs | 8 x TC |
Power supply | via the E-bus |
Thermocouple sensor types | types J, K, L, B, E, N, R, S, T, U (default setting type K), mV measurement |
Distributed Clocks | - |
Maximum cable length to the sensor | 30 m (see note) |
Input filter limit frequency | typ. 1 kHz; depending on sensor length, conversion time, sensor type |
Connection technology | 2-wire |
Open-circuit recognition | yes |
Conversion time | approx. 5 s up to 40 ms, depending on configuration and filter setting, preset approx. 500 ms |
Temperature range | defined in the range for each sensor (preset: type K; -200..+1370 °C); voltage measurement ±30 mV..±75 mV |
Resolution | 0.1 °C/ digit |
Measuring error | < ±0.3 % (relative to full scale value FSV) |
Electrical isolation | 500 V (E-bus/signal voltage) |
Current consumption load voltage (Up contacts) | - |
Current consumption via E-bus | 190 mA |
Special features | Idle detection, error detection of external cold junction compensation (CJC) |
Permissible ambient temperature range during operation | -25 °C .. + 60 °C (extended temperature range) |
Permissible ambient temperature range during storage | -40°C .. +85°C |
Permissible relative air humidity | 95 %, no condensation |
Operating altitude | max.2,000 m |
Dimensions (W x H x D) | approx. 12 mm x 66 mm x 55 mm |
Pollution degree | 2 |
Weight | approx. 30 g |
Mounting | on signal distribution board |
Mounting position | |
2 and 7 | |
Color coding | green |
Vibration / shock resistance | conforms to EN60068-2-6 / EN 60068-2-27 (with corresponding signal distribution board) |
EMC immunity / emission | conforms to EN 61000-6-2 /EN 61000-6-4 (with corresponding signal distribution board) |
Protection class | EJ module: IP20 |
Approvals / markings | CE, EAC, UKCA, |
CE approval The CE Marking refers to the EtherCAT plug-in module mentioned above. |
Maximum cable length to the sensor Without additional protective measures, the maximum cable length from the EtherCAT Module to the sensor is 30 m. For longer cable lengths, suitable surge protection should be provided. |