EJ3318 - 8-channel thermocouple input with open-circuit recognition
EJ3318 - Technical data
Technical data
EJ3318
Number of inputs
8 x TC
2 x PT1000 for cold junction compensation
Power supply
via the E-bus
Thermocouple sensor types
types J, K, L, B, E, N, R, S, T, U (default setting type K), mV measurement
Distributed Clocks
Maximum cable length to the sensor
30 m (see note)
Input filter limit frequency
typ. 1 kHz; depending on sensor length, conversion time, sensor type
Connection technology
2-wire
Open-circuit recognition
yes
Conversion time
approx. 5 s up to 40 ms, depending on configuration and filter setting, preset approx. 500 ms
Temperature range
defined in the range for each sensor (preset: type K; -200..+1370 °C); voltage measurement ±30 mV..±75 mV
Resolution
0.1 °C/ digit
Measuring error
< ±0.3 % (relative to full scale value FSV)
yes
Electrical isolation
500 V (E-bus/signal voltage)
Current consumption load voltage (Up contacts)
Current consumption via E-bus
190 mA
Special features
Idle detection, error detection of external cold junction compensation (CJC)
Permissible ambient temperature range during operation
-25 °C .. + 60 °C (extended temperature range)
Permissible ambient temperature range during storage
-40°C .. +85°C
Permissible relative air humidity
95 %, no condensation
Operating altitude
max.2,000 m
Dimensions (W x H x D)
approx. 12 mm x 66 mm x 55 mm
Pollution degree
2
Weight
approx. 30 g
Mounting
on signal distribution board
Mounting position
Position of the coding pins
2 and 7
Color coding
green
Vibration / shock resistance
conforms to EN60068-2-6 / EN 60068-2-27 (with corresponding signal distribution board)
EMC immunity / emission
conforms to EN 61000-6-2 /EN 61000-6-4 (with corresponding signal distribution board)
Protection class
EJ module: IP20
EJ system: dependent on the signal distribution board and housing
Approval
CE, UL
CE approval
The CE Marking refers to the EtherCAT plug-in module mentioned above.
If the EtherCAT plug-in module is used in the production of a ready-to-use end product (PCB in conjunction with a housing), the manufacturer of the end product must check compliance of the overall system with relevant directives and CE certification.
To operate the EtherCAT plug-in modules, they must be installed in a housing.