Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
Index (hex)
Meaning
Data type
Flags
Default
1000:0
Device type
Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile.
UINT32
RO
0x012C1389 (19665801dec)
Index 1008 Device name
Index (hex)
Meaning
Data type
Flags
Default
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EJ3255
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
00
Index 100A Software version
Index (hex)
Meaning
Data type
Flags
Default
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
01
Index 1018 Identity
Index (hex)
Meaning
Data type
Flags
Default
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID of the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0CB72852 (213330002dec)
1018:03
Revision
Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description
UINT32
RO
0x00000000 (0dec)
1018:04
Serial number
Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0
UINT32
RO
0x00000000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 1800 AI TxPDO-Par Standard Ch. 1
Index (hex)
Meaning
Data type
Flags
Default
1800:0
PDO parameter TxPDO 1
UINT8
RO
0x06 (6dec)
1800:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1.
OCTET-STRING[2]
RO
01 1A
Index 1801 AI TxPDO-Par Compact Ch. 1
Index (hex)
Meaning
Data type
Flags
Default
1801:0
AI TxPDO-Par Compact Ch.1
PDO parameter TxPDO 2
UINT8
RO
0x06 (6dec)
1801:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2.
OCTET-STRING[2]
RO
00 1A
Index 1802 AI TxPDO-Par Standard Ch. 2
Index (hex)
Meaning
Data type
Flags
Default
1802:0
AI TxPDO-Par Standard Ch.2
PDO parameter TxPDO 3
UINT8
RO
0x06 (6dec)
1802:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 3.
OCTET-STRING[2]
RO
03 1A
Index 1803 AI TxPDO-Par Compact Ch. 2
Index (hex)
Meaning
Data type
Flags
Default
1803:0
AI TxPDO-Par Compact Ch.2
PDO parameter TxPDO 4
UINT8
RO
0x06 (6dec)
1803:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 4.
OCTET-STRING[2]
RO
02 1A
Index 1804 AI TxPDO-Par Standard Ch. 3
Index (hex)
Meaning
Data type
Flags
Default
1804:0
AI TxPDO-Par Standard Ch.3
PDO parameter TxPDO 5
UINT8
RO
0x06 (6dec)
1804:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 5.
OCTET-STRING[2]
RO
05 1A
Index 1805 AI TxPDO-Par Compact Ch. 3
Index (hex)
Meaning
Data type
Flags
Default
1805:0
AI TxPDO-Par Compact Ch.3
PDO parameter TxPDO 6
UINT8
RO
0x06 (6dec)
1805:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 6.
OCTET-STRING[2]
RO
04 1A
Index 1806 AI TxPDO-Par Standard Ch. 4
Index (hex)
Meaning
Data type
Flags
Default
1806:0
PDO parameter TxPDO 7
UINT8
RO
0x06 (6dec)
1806:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 7.
OCTET-STRING[2]
RO
07 1A
Index 1807 AI TxPDO-Par Compact Ch. 4
Index (hex)
Meaning
Data type
Flags
Default
1807:0
AI TxPDO-Par Compact Ch.4
PDO parameter TxPDO 8
UINT8
RO
0x06 (6dec)
1807:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 8.
OCTET-STRING[2]
RO
06 1A
Index 1808 AI TxPDO-Par Standard Ch. 5
Index (hex)
Meaning
Data type
Flags
Default
1808:0
AI TxPDO-Par Standard Ch.5
PDO parameter TxPDO 9
UINT8
RO
0x06 (6dec)
1808:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 9.
OCTET-STRING[2]
RO
09 1A
Index 1809 AI TxPDO-Par Compact Ch. 5
Index (hex)
Meaning
Data type
Flags
Default
1809:0
AI TxPDO-Par Compact Ch.5
PDO parameter TxPDO 10
UINT8
RO
0x06 (6dec)
1809:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 10.
OCTET-STRING[2]
RO
08 1A
Index 1A00 AI TxPDO-Map Standard Ch. 1
Index (hex)
Meaning
Data type
Flags
Default
1A00:0
AI TxPDO-Map Standard Ch.1
PDO Mapping TxPDO 1
UINT8
RW
0x0B (11dec)
1A00:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x01 (Underrange))
UINT32
RW
0x6000:01, 1
1A00:02
SubIndex 002
2. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x02 (Overrange))
UINT32
RW
0x6000:02, 1
1A00:03
SubIndex 003
3. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x03 (Limit 1))
UINT32
RW
0x6000:03, 2
1A00:04
SubIndex 004
4. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x05 (Limit 2))
UINT32
RW
0x6000:05, 2
1A00:05
SubIndex 005
5. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x07 (Error))
UINT32
RW
0x6000:07, 1
1A00:06
SubIndex 006
6. PDO Mapping entry (1 bit align)
UINT32
RW
0x0000:00, 1
1A00:07
SubIndex 007
7. PDO Mapping entry (5 bits align)
UINT32
RW
0x0000:00, 5
1A00:08
SubIndex 008
8. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x0E (Sync error))
UINT32
RW
0x6000:0E, 1
1A00:09
SubIndex 009
9. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x0F (TxPDO-State))
UINT32
RW
0x6000:0F, 1
1A00:0A
SubIndex 010
10. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x10 (TxPDO-Toggle))
UINT32
RW
0x6000:10, 1
1A00:0B
SubIndex 011
11. PDO Mapping entry (object 0x6000 (AI Inputs Ch.1), entry 0x11 (Value))
UINT32
RW
0x6000:11, 16
Index 1A01 AI TxPDO-Map Compact Ch. 1
Index (hex)
Meaning
Data type
Flags
Default
1A01:0
AI TxPDO-Map Compact Ch.1
PDO Mapping TxPDO 2
UINT8
RW
0x01 (1dec)
1A01:01
SubIndex 001
UINT32
RW
0x6000:11, 1
Index 1A02 AI TxPDO-Map Standard Ch. 2
Index (hex)
Meaning
Data type
Flags
Default
1A02:0
AI TxPDO-Map Standard Ch.2
PDO Mapping TxPDO 3
UINT8
RW
0x0B (11dec)
1A02:01
SubIndex 001
1. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x01 (Underrange))
UINT32
RW
0x6010:01, 1
1A02:02
SubIndex 002
2. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x02 (Overrange))
UINT32
RW
0x6010:02, 1
1A02:03
SubIndex 003
3. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x03 (Limit 1))
UINT32
RW
0x6010:03, 2
1A02:04
SubIndex 004
4. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x05 (Limit 2))
UINT32
RW
0x6010:05, 2
1A02:05
SubIndex 005
5. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x07 (Error))
UINT32
RW
0x6010:07, 1
1A02:06
SubIndex 006
UINT32
RW
0x0000:00, 1
1A02:07
SubIndex 007
UINT32
RW
0x0000:00, 5
1A02:08
SubIndex 008
8. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x0E (Sync error))
UINT32
RW
0x6010:0E, 1
1A02:09
SubIndex 009
9. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x0F (TxPDO-State))
UINT32
RW
0x6010:0F, 1
1A02:0A
SubIndex 010
10. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x10 (TxPDO-Toggle))
UINT32
RW
0x6010:10, 1
1A02:0B
SubIndex 011
11. PDO Mapping entry (object 0x6010 (AI Inputs Ch.2), entry 0x11 (Value))
UINT32
RW
0x6010:11, 16
Index 1A03 AI TxPDO-Map Compact Ch. 2
Index (hex)
Meaning
Data type
Flags
Default
1A03:0
AI TxPDO-Map Compact Ch.2
PDO Mapping TxPDO 4
UINT8
RW
0x01 (1dec)
1A03:01
SubIndex 001
UINT32
RW
0x6010:11, 1
Index 1A04 AI TxPDO-Map Standard Ch. 3
Index (hex)
Meaning
Data type
Flags
Default
1A04:0
AI TxPDO-Map Standard Ch.3
PDO Mapping TxPDO 5
UINT8
RW
0x0B (11dec)
1A04:01
SubIndex 001
1. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x01 (Underrange))
UINT32
RW
0x6020:01, 1
1A04:02
SubIndex 002
2. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x02 (Overrange))
UINT32
RW
0x6020:02, 1
1A04:03
SubIndex 003
3. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x03 (Limit 1))
UINT32
RW
0x6020:03, 2
1A04:04
SubIndex 004
4. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x05 (Limit 2))
UINT32
RW
0x6020:05, 2
1A04:05
SubIndex 005
5. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x07 (Error))
UINT32
RW
0x6020:07, 1
1A04:06
SubIndex 006
UINT32
RW
0x0000:00, 1
1A04:07
SubIndex 007
UINT32
RW
0x0000:00, 5
1A04:08
SubIndex 008
8. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x0E (Sync error))
UINT32
RW
0x6020:0E, 1
1A04:09
SubIndex 009
9. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x0F (TxPDO-State))
UINT32
RW
0x6020:0F, 1
1A04:0A
SubIndex 010
10. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x10 (TxPDO-Toggle))
UINT32
RW
0x6020:10, 1
1A04:0B
SubIndex 011
11. PDO Mapping entry (object 0x6020 (AI Inputs Ch.3), entry 0x11 (Value))
UINT32
RW
0x6020:11, 16
Index 1A05 AI TxPDO-Map Compact Ch. 3
Index (hex)
Meaning
Data type
Flags
Default
1A05:0
AI TxPDO-Map Compact Ch.3
PDO Mapping TxPDO 6
UINT8
RW
0x01 (1dec)
1A05:01
SubIndex 001
UINT32
RW
0x6020:11, 1
Index 1A06 AI TxPDO-Map Standard Ch. 4
Index (hex)
Meaning
Data type
Flags
Default
1A06:0
AI TxPDO-Map Standard Ch.4
PDO Mapping TxPDO 7
UINT8
RW
0x0B (11dec)
1A06:01
SubIndex 001
1. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x01 (Underrange))
UINT32
RW
0x6030:01, 1
1A06:02
SubIndex 002
2. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x02 (Overrange))
UINT32
RW
0x6030:02, 1
1A06:03
SubIndex 003
3. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x03 (Limit 1))
UINT32
RW
0x6030:03, 2
1A06:04
SubIndex 004
4. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x05 (Limit 2))
UINT32
RW
0x6030:05, 2
1A06:05
SubIndex 005
5. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x07 (Error))
UINT32
RW
0x6030:07, 1
1A06:06
SubIndex 006
UINT32
RW
0x0000:00, 1
1A06:07
SubIndex 007
UINT32
RW
0x0000:00, 5
1A06:08
SubIndex 008
8. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x0E (Sync error))
UINT32
RW
0x6030:0E, 1
1A06:09
SubIndex 009
9. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x0F (TxPDO-State))
UINT32
RW
0x6030:0F, 1
1A06:0A
SubIndex 010
10. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x10 (TxPDO-Toggle))
UINT32
RW
0x6030:10, 1
1A06:0B
SubIndex 011
11. PDO Mapping entry (object 0x6030 (AI Inputs Ch.4), entry 0x11 (Value))
UINT32
RW
0x6030:11, 16
Index 1A07 AI TxPDO-Map Compact Ch. 4
Index (hex)
Meaning
Data type
Flags
Default
1A07:0
AI TxPDO-Map Compact Ch.4
PDO Mapping TxPDO 8
UINT8
RW
0x01 (1dec)
1A07:01
SubIndex 001
UINT32
RW
0x6030:11, 1
Index 1A08 AI TxPDO-Map Standard Ch. 5
Index (hex)
Meaning
Data type
Flags
Default
1A08:0
AI TxPDO-Map Standard Ch.5
PDO Mapping TxPDO 9
UINT8
RW
0x0B (11dec)
1A08:01
SubIndex 001
1. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x01 (Underrange))
UINT32
RW
0x6040:01, 1
1A08:02
SubIndex 002
2. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x02 (Overrange))
UINT32
RW
0x6040:02, 1
1A08:03
SubIndex 003
3. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x03 (Limit 1))
UINT32
RW
0x6040:03, 2
1A08:04
SubIndex 004
4. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x05 (Limit 2))
UINT32
RW
0x6040:05, 2
1A08:05
SubIndex 005
5. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x07 (Error))
UINT32
RW
0x6040:07, 1
1A08:06
SubIndex 006
UINT32
RW
0x0000:00, 1
1A08:07
SubIndex 007
UINT32
RW
0x0000:00, 5
1A08:08
SubIndex 008
8. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x0E (Sync error))
UINT32
RW
0x6040:0E, 1
1A08:09
SubIndex 009
9. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x0F (TxPDO-State))
UINT32
RW
0x6040:0F, 1
1A08:0A
SubIndex 010
10. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x10 (TxPDO Toggle))
UINT32
RW
0x6040:10, 1
1A08:0B
SubIndex 011
11. PDO Mapping entry (object 0x6040 (AI Inputs Ch.5), entry 0x11 (Value))
UINT32
RW
0x6040:11, 16
Index 1A09 AI TxPDO-Map Compact Ch. 5
Index (hex)
Meaning
Data type
Flags
Default
1A09:0
AI TxPDO-Map Compact Ch.5
PDO Mapping TxPDO 10
UINT8
RW
0x01 (1dec)
1A09:01
SubIndex 001
UINT32
RW
0x6040:11, 1
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default
1C00:0
Sync manager type
Using the Sync Managers
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync-Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync-Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync-Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync-Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 1C12 RxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RW
0x00 (0dec)
Index 1C13 TxPDO assign
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x05 (5dec)
1C13:01
Subindex 001
1. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A00 (6656dec)
1C13:02
Subindex 002
2. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A02 (6658dec)
1C13:03
Subindex 003
3. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A04 (6660dec)
1C13:04
Subindex 004
4. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A06 (6662dec)
1C13:05
Subindex 005
5. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A08 (6664dec)
Index 1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default
1C33:0
SM input parameter
Synchronization parameters for the inputs
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
Current synchronization mode:
  • 0: Free Run
  • 1: Synchron with SM 3 Event (no outputs available)
  • 2: DC - Synchron with SYNC0 Event
  • 3: DC - Synchron with SYNC1 Event
  • 34: Synchron with SM 2 Event (outputs available)
UINT16
RW
0x0001 (1dec)
1C33:02
Cycle time
Cycle time (in ns):
  • Free Run: Cycle time of the local timer
  • Synchron with SM 2 Event: Master cycle time
  • DC mode: SYNC0/SYNC1 Cycle Time
UINT32
RW
0x00030D40 (200000dec)
1C33:03
Shift time
Time between SYNC0 event and reading of the inputs (in ns, DC mode only)
UINT32
RW
0x0002E630 (19000dec)
1C33:04
Sync modes supported
Supported synchronization modes:
  • Bit 0: free run is supported
  • Bit 1: Synchron with SM 2 Event is supported (outputs available)
  • Bit 1: Synchron with SM 3 Event is supported (no outputs available)
  • Bit 2-3 = 01: DC mode is supported
  • Bit 4-5 = 01: Input Shift through local event (outputs available)
  • Bit 4-5 = 10: Input Shift with SYNC1 Event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C33:08)
UINT16
RO
0x400B (16359dec)
1C33:05
Minimum cycle time
Minimum cycle time (in ns)
UINT32
RO
1C33:06
Calc and copy time
Time between reading of the inputs and availability of the inputs for the master (in ns, DC mode only)
UINT32
RO
0x00002710 (10000dec)
1C33:07
Minimum delay time
Minimum time between Sync-1 Event and reading of the inputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:08
Command
  • 0: Measurement of the local cycle time is stopped
  • 1: Measurement of the local cycle time is started
The entries 0x1C33:03, 0x1C33:06, 0x1C33:09 are updated with the maximum measured values.
For a subsequent measurement the measured values are reset
UINT16
RW
0x0000 (0dec)
1C33:09
Maximum Delay time
Time between SYNC1 event and reading of the inputs (in ns, DC mode only)
UINT32
RO
0x00000000 (0dec)
1C33:0B
SM event missed counter
Number of missed SM events in OPERATIONAL (DC mode only)
UINT16
RO
0x0000 (0dec)
1C33:0C
Cycle exceeded counter
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early)
UINT16
RO
0x0000 (0dec)
1C33:0D
Shift too short counter
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only)
UINT16
RO
0x0000 (0dec)
1C33:20
Sync error
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only)
BOOLEAN
RO
0x00 (0dec)