LED displays
LED displays 1:
Ethernet interface X001
Interface X001
Ethernet (CX8093)
Meaning
LED green
on
Link present
LED yellow
flashing
Activity
Ethernet interface X101/102
Interface X001/X002
Ethernet (CX8093)
Meaning
LED green
on
Link available/activity
LED yellow
is not used
LED coupler
Labelling
Meaning
Colour
Meaning
RUN
Indicates the status of the coupler
red
TwinCAT is in "stop" mode
Green
TwinCAT is in "run" mode
Blue
(If red DIP switch 1 is set to on when starting the coupler)
TwinCAT is in "config" mode
LED PN *
PROFINET Status
Meaning
green
red
Power On
off
200 ms flashing
Start-up phase
No name
200 ms flashing
off
no PROFINET name
No IP
1 sec off, 200 ms on
off
No IP address
Run
on
off
OK
LED DIAG *
PROFINET diagnosis
Meaning
green
red
Flashing, PN controller identification
500 ms
500 ms
The PN controller is transmitting an identification signal
No AR established
off
200 ms flashing
The establishment of a connection with the controller has not been completed
Device is in IO exchange
Error display of Outputs CR is set to module differences
1 s off 200, ms on
off
Problem with establishment of a connection or nominal and actual configuration differ
Device is in IO exchange but provider is in stop
200 ms
off
Coupler is in data exchange, but PLC is in stop
on
off
OK
* ) If a virtual PROFINET device has been projected, this is also signalled by the LEDs in the event of an error. The real device always has the higher priority; if it is OK the status of the virtual device is displayed.
LED power supply terminal
LED displays 2:
LED displays 3:
Operation with E-bus terminals
Operation with K-bus terminals
Display LED
Meaning
1 Us 24 V (top left, 1st row)
CX80xx supply voltage
connected to -24 V
2 Up 24 V (top right, 1st row)
Power contacts supply voltage
connected to -24 V
3 L/A (left centre,  2nd row)
EtherCAT LED
flashing green: EtherCAT communication active
connected to E-bus / no data traffic
not connected to E-bus
4 K-BUS RUN (right centre, 2nd row)
K-bus LED RUN
Lights up green: K-bus running, everything OK
6 K-BUS ERR (bottom right, 3rd row)
K-bus LED ERR
Lights up red: K-bus error - see K-bus error code
K-bus error code
Error code
Error code argument
Remedy
Persistent, continuous flashing
EMC problems
  • Check power supply for undervoltage or overvoltage peaks
  • Implement EMC measures
  • If a K-bus error is present, it can be localised by a restart of the coupler (by switching it off and then on again)
3 pulses
0
K-bus command error
  • No Bus Terminal inserted
  • One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.
4 pulses
0
K-Bus data error, break behind the Bus Coupler
Check whether the n+1 Bus Terminal is correctly connected; replace if necessary.
n
Break behind Bus Terminal n
Check whether the Bus End Terminal 9010 is connected.
5 pulses
n
K-Bus error in register communication with Bus Terminal n
Exchange the nth bus terminal
6 pulses
0
Error at initialisation
Exchange Bus Coupler
1
Internal data error
Perform a hardware reset on the Bus Coupler (switch off and on again)
8
Internal data error
7 pulses
0
Process data lengths do not correspond to the configuration
Check the Bus Terminals for the configured Bus Terminals
1..n
K-bus reset failed