Diagnostic LEDs
A BX Controller has two groups of LEDs for status display:
- On the top right of the BX controller there are two green power LEDs. These are provided for diagnostics of the power supply of the BX Controller and of the power contacts.
- The DIAG LEDs are located above the navigation switch on the left. They indicate the state of the fieldbus, the PLC and the K-bus.
POWER LEDs for diagnostics of power supply
Power LEDs |
Meaning |
Left LED off |
BX Controller has no power supply |
Right LED off |
Power contacts has no power supply |
DIAG LEDs
The DIAG LEDs are sub-divided as follows:
- Bus: fieldbus diagnostics
- PLC: PLC diagnostics
- I/O: K-bus diagnostics
The LEDs can be off, green, orange or red.
After switching on, the BX Controller immediately checks the connected configuration. The I/O LED goes out if the start-up was successful. A red I/O LED indicates a Bus Terminal error. The error type is shown in the display. This permits rapid rectification of the error.
LEDs for fieldbus diagnostics
LED Bus |
Meaning |
off |
no fieldbus connected |
red illuminated |
no fieldbus connected, DeviceNet 24 V missing, DeviceNet communication error - wrong baud rate, incorrect termination |
flashes red |
communication error, IO timeout - communication to DeviceNet master interrupted |
flashes orange |
Baud rate search active, no baud rate found |
flashing green |
communication with master not yet established |
green illuminated |
DeviceNet communication active |
LED for PLC diagnostics
LED PLC | Meaning |
off | PLC in stop or no program available |
flashes red | The set task time is sometimes exceeded (see also Chapter Deactivating the LED for cycle time exceeding). |
red illuminated | The set task time is always exceeded. |
orange illuminated | PLC runs without boot project (only lights up during the cycle), |
green illuminated | Boot project - PLC is running (only lights up during cycle) |
LED for K-bus diagnostics
LED I/O |
Meaning |
off |
No data are exchanged via the K-bus |
red illuminated |
error flashing - error type - display |
Register or KS2000 online access |
green illuminated |
K-bus OK and running |
Error code for K-bus diagnostics
Error code | Error code argument | Description | Remedy |
0 | - | EMC problems |
1 | 0 | EEPROM checksum error | Enter factory settings with the KS2000 configuration software |
1 | Code buffer overflow | Insert fewer Bus Terminals. The programmed configuration has too many entries in the table | |
2 | Unknown data type | Software update required for the BX Controller | |
2 | - | reserved | - |
3 | 0 | K-bus command error |
4 | 0 | K-bus data error, break behind the BX Controller | Check whether the n+1 Bus Terminal is correctly connected; replace if necessary. |
n | Break behind Bus Terminal n | Check whether the KL9010 Bus End Terminal is connected | |
5 | n | K-bus error in register communication with Bus Terminal n | Exchange the nth Bus Terminal |
6 | 0 | Error at initialization | Replace BX Controller |
1 | Internal data error | Perform a hardware reset on the BX Controller (switch off and on again) | |
2 | DIP switch changed after a software reset | Perform a hardware reset on the BX Controller (switch off and on again) | |
7 | 0 | Note: cycle time was exceeded | Warning: the set cycle time was exceeded. This indication (flashing LEDs) can only be cleared by booting the BX Controller again. |
9 | 0 | Checksum error in Flash program | Transmit program to the BX again |
1 | Incorrect or faulty library implemented | Remove the faulty library | |
10 | n | Bus Terminal n is not consistent with the configuration that existed when the boot project was created | Check the nth Bus Terminal. The boot project must be deleted if the insertion of an nth Bus Terminal is intentional. |
14 | n | nth Bus Terminal has the wrong format | Start the BX Controller again, and if the error occurs again then exchange the Bus Terminal. |
15 | n | Number of Bus Terminals is no longer correct | Start the BX Controller again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software |
16 | n | Length of the K-bus data is no longer correct | Start the BX Controller again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software |