Diagnostic LEDs
A BX Controller has two groups of LEDs for status display:
Diagnostic LEDs 1:
Diagnostic LEDs for the fieldbus, the PLC, the K-bus and the power supply units
POWER LEDs for diagnostics of power supply
Power LEDs
Meaning
Left LED off
BX Controller has no power supply
Right LED off
Power contacts has no power supply
DIAG LEDs
The DIAG LEDs are sub-divided as follows:
- Bus: fieldbus diagnostics
- PLC: PLC diagnostics
- I/O: K-bus diagnostics
The LEDs can be off, green, orange or red.
Diagnostic LEDs 2:
Diagnostic LEDs for the fieldbus, the PLC and the K-bus
After switching on, the BX Controller immediately checks the connected configuration. The I/O LED goes out if the start-up was successful. A red I/O LED indicates a Bus Terminal error. The error type is shown in the display. This permits rapid rectification of the error.
LEDs for fieldbus diagnostics
LED Bus
Meaning
off
no fieldbus connected
red illuminated
no fieldbus connected, DeviceNet 24 V missing, DeviceNet communication error - wrong baud rate, incorrect termination
flashes red
communication error, IO timeout - communication to DeviceNet master interrupted
flashes orange
Baud rate search active, no baud rate found
flashing green
communication with master not yet established
green illuminated
DeviceNet communication active
LED for PLC diagnostics
LED PLC
Meaning
off
PLC in stop or no program available
flashes red
The set task time is sometimes exceeded (see also Chapter Deactivating the LED for cycle time exceeding).
red illuminated
The set task time is always exceeded.
orange illuminated
PLC runs without boot project (only lights up during the cycle),
when the boot project is generated, the LED flashes orange
green illuminated
Boot project - PLC is running (only lights up during cycle)
LED for K-bus diagnostics
LED I/O
Meaning
off
No data are exchanged via the K-bus
red illuminated
error flashing - error type - display
orange illuminated
Register or KS2000 online access
green illuminated
K-bus OK and running
Error code for K-bus diagnostics
Error code
Error code argument
Remedy
0
EMC problems
  • Check power supply for undervoltage or overvoltage peaks
  • Implement EMC measures
  • If a K-bus error is present, it can be localized by a restart of the coupler (by switching it off and then on again)
1
0
EEPROM checksum error
Enter factory settings with the KS2000 configuration software
1
Code buffer overflow
Insert fewer Bus Terminals. The programmed configuration has too many entries in the table
2
Unknown data type
Software update required for the BX Controller
2
reserved
3
0
K-bus command error
  • No Bus Terminal inserted
  • One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.
4
0
K-bus data error, break behind the BX Controller
Check whether the n+1 Bus Terminal is correctly connected; replace if necessary.
n
Break behind Bus Terminal n
Check whether the KL9010 Bus End Terminal is connected
5
n
K-bus error in register communication with Bus Terminal n
Exchange the nth Bus Terminal
6
0
Error at initialization
Replace BX Controller
1
Internal data error
Perform a hardware reset on the BX Controller (switch off and on again)
2
DIP switch changed after a software reset
7
0
Note: cycle time was exceeded
Warning: the set cycle time was exceeded. This indication (flashing LEDs) can only be cleared by booting the BX Controller again.
Remedy: increase the cycle time
9
0
Checksum error in Flash program
Transmit program to the BX again
1
Incorrect or faulty library implemented
Remove the faulty library
10
n
Bus Terminal n is not consistent with the configuration that existed when the boot project was created
Check the nth Bus Terminal. The boot project must be deleted if the insertion of an nth Bus Terminal is intentional.
14
n
nth Bus Terminal has the wrong format
Start the BX Controller again, and if the error occurs again then exchange the Bus Terminal.
15
n
Number of Bus Terminals is no longer correct
Start the BX Controller again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software
16
n
Length of the K-bus data is no longer correct