Diagnostic LEDs
After switching on, the Bus Coupler immediately checks the connected configuration. Error-free start-up is indicated when the red I/O ERR LED goes out. If the I/O ERR LED blinks, an error in the area of the terminals is indicated. The error code can be determined from the frequency and number of blinks. This permits rapid rectification of the error.
The Bus Coupler has two groups of LEDs for the display of status. The upper group with four LEDs indicates the status of the respective fieldbus. The significance of the fieldbus status LEDs is explained in the appropriate sections of this manual. It corresponds to the usual fieldbus display.
On the upper right hand side of the Bus Couplers are two more green LEDs that indicate the supply voltage. The left hand LED indicates the presence of the 24 V supply for the Bus Coupler. The right hand LED indicates the presence of the supply to the power contacts.
Diagnostic LEDs 1:
LEDs of Bus Couplers BK9053 and BK9103
LEDs for power supply diagnostics
LED
Meaning
LED Us
off
the power supply voltage, Us, is not present
on
the power supply voltage, Us, is present
LED Up
off
Supply voltage Up (for power contacts) not available
on
Supply voltage Up (for power contacts) available
LEDs at RJ45
LED
Meaning
LED Link/Act
off
No physical connection present
on
Physical connection present
flashing
Communication available
LED 10/100 Mbaud
(only BK9103)
off
10 Mbaud (if LED Link/Act is lit or flashes)
on
100 Mbaud
LEDs for PROFINET diagnostics
PROFINET diagnosis
PN Err (red)
PN Run (green)
DIAG E (red)
DIAG R (green)
IP Address OK
off
0,5 s
x
x
No IP valid Address (Dip Switch 9,10 -> on)
0,1 sec
off
x
x
Online
off
on
x
x
Offline PLC Stop
off
0,1 s
x
x
TimeOut
0,5 s
off
x
x
IP address configuration fault
on
off
x
x
Alternate flashing (triggered by a Profinet tool)
0.5 sec
0.5 sec
x
x
Configuration Diagnose
PN Err (red)
PN Run (green)
DIAG E (red)
DIAG R (green)
OK
x
x
off
on
Wrong module
x
x
Slot number
1
Missing module (physical)
x
x
Slot number
2
Missing module (in the configuration)
x
x
Slot number
3
No PROFINET name assigned
x
x
0
4
Substitute
x
x
Slot number
5
x: The status of the LED is not relevant for this diagnosis.
Note:
Sample
You have configured a KL2xx4 for the fifth slot, but in fact only four modules are inserted.
Diagnostic LEDs 2:
Example for Error Code and Error Argument
LEDs for K-bus diagnostics
Error code
Error code argument
Remedy
Persistent, continuous flashing
EMC problems
  • Check power supply for undervoltage or overvoltage peaks
  • Implement EMC measures
  • If a K-bus error is present, it can be localized by a restart of the coupler (by switching it off and then on again)
1 pulse
0
EEPROM checksum error
Set manufacturer's settings with the KS2000 configuration software
1
Code buffer overflow
Insert fewer Bus Terminals. Too many entries in the table for the programmed configuration
2
Unknown data type
Software update required for the Bus Coupler
2 pulses
0
Programmed configuration has an incorrect table entry
Check programmed configuration for correctness
n (n > 0)
Table comparison (Bus Terminal n)
Incorrect table entry
3 pulses
0
K-bus command error
  • No Bus Terminal inserted
  • One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.
4 pulses
0
K-bus data error, break behind the Bus Coupler
Check whether the n+1 Bus Terminal is correctly connected; replace if necessary.
n
Break behind Bus Terminal n
Check whether the bus end terminal 9010 is connected.
5 pulses
n
K-bus error in register communication with Bus Terminal n
Exchange the nth bus terminal
6 pulses
0
Error at initialization
Exchange Bus Coupler
1
Internal data error
Perform a hardware reset on the Bus Coupler (switch off and on again)
4
DIP switch incorrect for BootP
Set 1-8 to on or off, see BootP
8
Internal data error
16
Error in IP socket
14 pulses
n
nth Bus Terminal has the wrong format
Start the Bus Coupler again, and if the error occurs again then exchange the Bus Terminal
15 pulses
n
Number of Bus Terminals is no longer correct
Start the Bus Coupler again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software
16 pulses
n
Length of the K-bus data is no longer correct