LEDs
After switching on, the Bus Coupler immediately checks the connected configuration. Error-free start-up is signaled by the red LED I/O ERR being extinguished. If the I/O ERR LED blinks, an error in the area of the terminals is indicated. The frequency and number of flashes indicate the error code (see below).
The BK1120 / BK1150 Bus Coupler has a green LED Link/Act In / Link/Act Out at the RJ45 sockets, which indicates the fieldbus status.
The RUN and ERROR LEDs (for BK1120: center top, for BK1150: left row of the LED prism) indicate the state of the EtherCAT state machine.
On the upper right hand side of the BK1120 are two more green LEDs that indicate the supply voltage. The left hand LED indicates the presence of the 24 V supply for the Bus Coupler. The right hand LED indicates the presence of the supply to the power contacts. At the BK1150, the diagnostic LEDs are on the right side of the LED prism, as shown in Fig. BK1120, BK1150 - Diagnostic LEDs at Bus Coupler.
LEDs 1:
The diagnostic LEDs for the BK1250 are arranged as shown in Fig. BK1250 - Diagnostic LEDs at Bus Coupler.
LEDs 2:
Diagnostic LEDs at Bus Coupler BK1250
LEDs for power supply diagnostics
LED
Display
State
Us (POWER SUPPLY)
green
off
No operating voltage present at the Bus Coupler
on
24 VDC operating voltage present at the Bus Coupler
Up (POWER CONTACTS)
green
off
No power supply present at the power contacts
on
24 VDC power supply present at the power contacts
Diagnostic LEDs for the EtherCAT State Machine/PLC
LED
Display
State
RUN
green
off
Init
The Bus Coupler is in initialization state
flashing
Pre-Operational
The Bus Coupler is in pre-operational state
single flash
Safe-Operational
The Bus Coupler is in safe-operational state
on
Operational
The Bus Coupler is in operational state
flickers
Bootstrap
Firmware is being loaded.
ERROR
red
off
No error
flashing
Err-Operational
No Communication
PLC error / lost frames
LEDs for fieldbus diagnostics
BK1120, BK1150
LED
Display
State
LINK / ACT (X1 IN)
green
off
No connection on the incoming EtherCAT segment
on
linked
Preceding EtherCAT device connected
flashing
active
Communication with preceding EtherCAT device
LINK / ACT (X2 OUT)
green
off
No connection on the outgoing EtherCAT segment
on
linked
Following EtherCAT device connected
flashing
active
Communication with downstream EtherCAT device
BK1250
LED
Display
State
LINK/ACT
green
off
No connection/communication with the E-bus
flashing
linked
Connection/communication with the E-bus established
LEDs for K-bus diagnostics
LED
Display
State
I/O-RUN
green
off
K-bus inactive
on
K-bus active
LED red; I/O-Error
Error code argument
Remedy
Persistent, continuous flashing
EMC problems
  • Check power supply for undervoltage or overvoltage peaks
  • Implement EMC measures
  • If a K-bus error is present, it can be localized by a restart of the coupler (by switching it off and then on again)
1 pulse
0
EEPROM checksum error
  • Enter factory settings with the KS2000 configuration software
    (Menu "Online -> Coupler -> Services -> Factory Setting")
1
Code buffer overflow
  • Insert fewer Bus Terminals. Too many entries in the table for the programmed configuration
2
Unknown data type
  • Software update required for the Bus Coupler
2 pulses
0
Programmed configuration has an incorrect table entry
  • Check programmed configuration for correctness
n (n > 0)
Table comparison (Bus Terminal n)
  • Incorrect table entry
3 pulses
0
K-bus command error
  • No Bus Terminal inserted
  • One of the Bus Terminals is defective; halve the number of Bus Terminals attached and check whether the error is still present with the remaining Bus Terminals. Repeat until the defective Bus Terminal is located.
4 pulses
0
K-bus data error, break behind the Bus Coupler
  • Check whether the n+1 Bus Terminal is correctly connected; replace if necessary.
n
Break behind Bus Terminal n
  • Check whether the bus end terminal 9010 is connected.
5 pulses
n
K-bus error in register communication with Bus Terminal n
  • Exchange the nth bus terminal
14 pulses
n
nth Bus Terminal has the wrong format
  • Start the Bus Coupler again, and if the error occurs again then exchange the Bus Terminal
15 pulses
n
Number of Bus Terminals is no longer correct
  • Start the Bus Coupler again. If the error occurs again, restore the manufacturers setting using the KS2000 configuration software
16 pulses
n
Length of the K-bus data is no longer correct